Acond PRO-R Heat Pump
This review discusses the installation of an Acond heat pump in a neighbour's house, which is a two-story, semi-detached stone cottage covering around 100 square meters. The cottage, which recently underwent renovations, now features 50mm PIR foam insulation plasterboards on the walls and underfloor heating in the lounge. The owner chose Thermal Earth for the installation primarily because they had an available slot, which was crucial as she was in the midst of significant renovations and lacked heating and hot water.
Thermal Earth conducted an initial heat loss report, estimating the house's total heat loss at 5.8 kW with an exterior design temperature of -3C. Based on this, they recommended a heat pump from Acond, a Czech brand new to the UK market and, to my knowledge, exclusively used by Thermal Earth. The selected model was the Acond N, with an approximate output of 6kW. The Acond heat pump utilises the refrigerant R290, in contrast to the R32 used in most contemporary heat pumps.
Subsequent to agreeing on the installation, the homeowner informed Thermal Earth of potential future plans to convert a 30 square meter outhouse into living space. Thermal Earth then advised that this additional load, estimated between 600-1200 Watts, would exceed the capacity of the Acond N model. They recommended upgrading to the Acond PRO-R model, with a marked output of 16kW.
I became involved after the PRO-R unit was installed and operational, heating the home and its domestic hot water continuously. The homeowner expressed concerns over the resulting high energy bills, which ranged from £10-15 daily. A lack of handover instructions and the impression from installers that the heat pump could not be deactivated exacerbated her worries. Her attempts to communicate with the company were largely ignored, leading to significant frustration and highlighting a lack of customer focus on the company's part.
Upon inspecting the installation, I identified insulation deficiencies both inside the house, where it was missing, and outside, where it was substandard in certain areas. Additionally, I was troubled by the significant increase in heat pump capacity, jumping from a nominal 6kW to 16kW. This led to the placement of the larger model at the far end of the garden, necessitating a lengthy pipe run back to the house.

I addressed these concerns in an email to the company, mentioning my intention to write this review. In response, one of the owners clarified that at the design temperature of -3C, the output of the PRO-N model was "less than 5kW," while the PRO-R model was 9 kW. He also provided output graphs for both units, which, after verifying the design flow temperature was 45C, allowed me to correct the outputs to 6.5 kW for the PRO-N and 14 kW for the PRO-R at that specific flow temperature.

Subsequently, the company arranged for an engineer's visit and sent over a user manual by email. Although the manual was somewhat helpful, it was not comprehensive and referred to a different wall-mounted control unit.
During the visit, the engineer acknowledged the insulation issues and attempted to grant the homeowner access to the heat pump's control software. Due to poor internet connectivity, he was unable to complete this setup but managed to schedule the heat pump over a local network connection as per the homeowner's preferences. It's worth noting that while most of the heat pump's controls can be accessed via a wall-mounted control box, this method is cumbersome and lacks scheduling capabilities. The engineer committed to returning the following week to attempt setting up internet access again and to address any remaining minor issues.
The follow-up visit concluded with all minor issues being resolved satisfactorily, although internet access to the heat pump's controller was not established. I also sought to secure a guarantee from the company to replace the oversized heat pump with a smaller model if it cycled too frequently in mild weather, a request the company declined.
Due to the house's poor internet connection, I proposed that if the company could send me instructions on accessing the heat pump via the local network, I could set up access to the controller software myself. The engineer agreed to this plan. However, another week passed without the arrival of the instructions, and during this time, the house's heating system appeared to be malfunctioning.
At this juncture, the company's approach shifted, and they expressed reluctance to provide the instructions, arguing that a stronger internet signal was necessary for using the control app. The client countered, noting that one of the installers had previously mentioned an internet connection was preferable but not mandatory. In response, Thermal Earth referred to a detailed agreement the client had signed months earlier.
Following considerable debate and the client's decision to withhold the final payment, the company finally provided the instructions. Once connected to the heat pump's control software via a local network, we discovered that the system was set to heat domestic hot water to over 62C daily, despite the client not having any operational hot water taps and requesting this function be disabled.
Attempts to modify the heating and hot water schedules were unsuccessful; the heat pump would activate at the set times, yet no temperature increase was detected at the radiators. After additional discussions with Thermal Earth, they consented to dispatch another engineer to address the problems.
The new engineer quickly identified and resolved the issues within an hour of his arrival. The control software had both heating pumps deactivated, blocking heat delivery to the radiators and underfloor heating. Furthermore, the immersion heater for the hot water tank had been left on, causing continuous heating of the water to the thermostat's set temperature, likely since the initial handover more than a month prior.
Fortunately, the owner now has a fully operational heat pump system. Despite receiving written assurances from the company that the heat pump is appropriately sized and will not cycle excessively, they have firmly declined any offer to replace it with a smaller model if it fails to meet performance expectations. I plan to update this review in the future with further evaluation of the system's performance.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
What is R210? I haven't been able to find any details of it. e.g. it isn't in https://en.wikipedia.org/wiki/List_of_refrigerants
What is R210? I haven't been able to find any details of it. e.g. it isn't in https://en.wikipedia.org/wiki/List_of_refrigerants/p >
It is not using R210, but R290.
I asked Acond for a quote back at the start of my ashp journey… I nearly fell off my chair when the email came in…
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
@hughf that’s too intriguing. What was the proposed damage?
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody, all done.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor Thanks 🙂
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
@hughf wow. Pricey dicey.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Indeed.... And I wasn't too happy that I couldn't see the product before buying it, hence why I went with Cool Energy. I saw them at Installer show and saw them at the NHBC in Swindon. Any Chris couldn't have been more helpful with my technical queries.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Very interesting to read this and entirely matches my experience with Thermal Earth. They are interested in the cash, not customers experience or support.
the Acond HP is effective and quiet. The software is terrible, the manual doesn’t match the software or the controller and isn’t entirely in English. The App on the Apple Store has now stopped working completely…
-
Vaillant AroTherm Plus 7kW
1 month ago
-
Samsung 5kW R32 Monobloc Gen 6 ASHP
2 months ago
-
Ariston or Acond Heat Pumps?
1 year ago
- 22 Forums
- 2,039 Topics
- 44.4 K Posts
- 36 Online
- 3,259 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
Your understanding of having to wire those valves back ...
By GrahamL , 8 hours ago
-
RE: why solar diverters for HW instead of the heat pump?
I should probably add to my comments above that, whilst...
By JamesPa , 11 hours ago
-
RE: Commencing on an ASHP Installation Process
Lots of reading and questioning which the background ma...
By JamesPa , 16 hours ago
-
RE: The Great British Heat Pump Quiz
Not sure how that happened 🤣 I suspect that it ...
By Mars , 18 hours ago
-
RE: Help with understanding my Mitsubishi Ecodan air source heat pump
@patch I think @ashp-bobba gave you some great pointers...
By SUNandAIR , 2 days ago
-
RE: Installing your own ASHP - DIY
Hi @tomasmcguinness, how are you progressing with this?...
By Ashfp , 2 days ago
-
RE: Say hello and introduce yourself
Welcome to the forum. If you are new to ASHPs I sug...
By JamesPa , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@editor guess the reason im asking is cause ive looked ...
By AdamK , 2 days ago
-
RE: The Rise and Fall of Europe’s Most Generous Green Subsidy
This is where the cold water storage tank was situated;...
By Dwynwen , 3 days ago
-
RE: Air Source Heat Pump - Side Alley Suitability
Thats probably fair enough. The degree-days calculatio...
By JamesPa , 3 days ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
That’s interesting, but obviously concerning also…. Do ...
By SUNandAIR , 4 days ago
-
RE: In the middle of an ASHP installation - a few questions (and issues)
Thank you @robs - that very useful data. The issue wa...
By Transparent , 4 days ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
@trebor12345 The Auto function is supposed to adapt au...
By Heatgeek , 5 days ago
-
RE: help sizing rads based on room by room heat loss
If its 1988W at DT 50, which is how most radiators are ...
By JamesPa , 5 days ago
-
RE: Career change – entering the world of heating and heat pumps
@editor Mars, thank you. That's along the routes I was ...
By Lakey , 5 days ago
-
@editor thanks Mars, it's a rare occasion I'm looking f...
By big_si , 5 days ago
-
RE: Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
@ashp-bobba and @jamespa - thank you both for all your ...
By CBrenewable , 6 days ago
-
-
Win one of five "Heat Pumps 101" Courses
Heat pumps are gaining traction in the UK, but between ...
By Mars , 6 days ago