Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Getting ready for export using 8kw solis and 16kwh seplos battery
So my plans when installing the 8kw solis and 16kwh seplos battery were not for export, just a protection for blackouts. And a first step to lower electricity expenses as they will only grow when we get an ASHP. Eventually we may add some PV.
The install is almost ready. 🙂
Now as ukpowernetworks stated will approve us to do 5kw export, taking the next step while it is all fresh seems simpler.
Octopus seems to accept export without MCS (as I had no plan to export now, I never got it from the electricians, not sure if they have it or not).
What are people's thoughts in terms of advantage to get the MCS paperwork vs setting up export to the utility operators that do not require it, is there much to gain?
And the simplest way to do it. As I have no questions about safety etc, the paper is the value.. 😉
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Maybe due to mine being a countercyclical application (when few folks think about PV), UK Powernetworks turned this around in less than a week.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Is your installer MCS certified? If so, they should register the install and provide the paperwork for you.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
Posted by: @old_scientistIs your installer MCS certified? If so, they should register the install and provide the paperwork for you.
Agree, that is the route I also advise most to take.
In my case, I contacted an installer recommended by Fogstar. After a few calls, £3200 was estimated over the phone. Fair for a simple no PV system with an inverter with a type-tested certificate? By the way, the installers are still recommended...
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
It seems that the electrically capable can go further on the G99 process. The G99 A3-1 and A3-2 form includes a checklist of safety aspects for the "site" and the grid.
Safety is key, always consult an electrician.
Credit to @transparent and other pioneers that made this journey a lot more accessible, like with last year's post.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Posted by: @batpredSafety is key, always consult an electrician.
With respect, since your home is connected to the grid, it’s not just sensible to consult an electrician; it’s a building regulations requirement for a qualified electrician to sign off the work. It doesn’t stop someone doing the work themselves (“overseen” by a qualified sparky) but it must be signed off as safe before it’s connected. If you don’t do it that way, you don’t get an installation certificate and that may cause significant problems when it comes time for you to sell the house.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
Thank you for raising it, major! The context of "no solar" is very relevant.
A few things, KISS applies:
- consulting an electrician early on is about making sure all the work is completed so the G99 process is a tick-box exercise (in case an MCS installer is not managing it)
- my DNO did not even ask to be notified about the inverter (it is only the intention to export that triggered it)
- using electricians when carrying out something as significant as this is common sense
When stating anything is part of building regulations, a source and image would help.
As for gaps in electrical certificates causing "significant problems" when a house is being sold, my experience is that unfortunately that is not always the case.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
You are very mistaken, @batpred. KISS does not apply; legislation does. That’s irrespective of the “no solar” context you talk about. That also means the use of a qualified electrician to eithe carry out or oversee the work is mandatory, common sense or no.
The building regulations are so well known that I’m surprised you feel it necessary to ask for a link but you can find all the relevant information on the gov.uk web site.
https://www.gov.uk/government/publications/electrical-safety-approved-document-p
I would suggest you familiarise yourself with the key points in the Part P document before going too much further.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
Posted by: @majordennisbloodnokIf you don’t do it that way, you don’t get an installation certificate and that may cause significant problems when it comes time for you to sell the house.
... or when you attempt make a claim on insurance !
Save energy... recycle electrons!
Indeed, @transparent
I understand it goes further, too. If someone unqualified carried out some notifiable work, that could render them liable for any damage or injury it caused. I’m not an expert, though, so don’t know how far that liability extends.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
In most cases I'd expect such liability would be tested under civil law.
But the boundaries of criminal liability aren't particularly clear when it comes to DIY stuff we do around the home.
Very few householders realise, for example, that Health and Safety rules apply equally at home as the workplace.
A neighbour could report a homeowner to HSE for attempting to undertake work from a ladder when scaffolding should be used.
I'm less clear on where matters stand when its the regulations themselves which are deficient.
Elsewhere on this forum we discussed PAS63100, which is a (non-mandatory) standard applying to domestic storage batteries.
It states that batteries should not be installed in the attic, but gives no such guidance on where their matching inverter should be sited.
Considering the two devices, I'd suggest that it's a faulty inverter which is more likely to cause a fire due to excess current.
A battery would be quite happy delivering 10,000 Amps because that's what its chemistry is designed to do!
Save energy... recycle electrons!
Posted by: @transparentPosted by: @majordennisbloodnokIf you don’t do it that way, you don’t get an installation certificate and that may cause significant problems when it comes time for you to sell the house.
... or when you attempt make a claim on insurance !
"KISS" applies. As the principle of "when in Rome, do it like the Romans do it". 😀
I had an EV charger put in by a qualified electrician. Did he register it with DNO? Of course not, apart from time spent, this could have attracted oversight: he applied the KISS principle for himself.
Did I register the EV charger when I got onto the ukpowernetworks portal and saw it missing? Of course I did, as I applied KISS for a homeowner. I want oversight, I want any future sale to not be delayed by such things.
Principles need to be used in context.
Note: I have nothing to gain for myself my sharing these insights.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 878 Online
- 6,993 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks @editor , @indevolt-uk Subject to any comments ...
By JamesPa , 4 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 5 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 8 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 9 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 10 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 10 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 13 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 13 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 19 hours ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 20 hours ago
-
RE: The Grid Says Yes.. Until It Doesn’t: Why Britain's Net Zero Push is Stalling at the Plug Socket
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 3 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 3 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago
-
That’s the solar up and running, I don’t think it’s the...
By David999 , 4 days ago
-
RE: Seeking ideas / information / commiseration - Pure Drive
I agree with @colinc that you can reuse some of it. A s...
By Batpred , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Im trying me best to ignore orangeman, I figur...
By Papahuhu , 4 days ago
-
@toodles That’s way better per kWp performance than our...
By Papahuhu , 5 days ago