Massive Electricity Cost for Running My Air Source Heat Pump
I don't think the insulation around those four external pipe runs is adequate.
Although I can't see how they arrange themselves to pass through a 100-125mm outer sleeve, the pipe clips have already compromised the wall thickness before the flow even gets there.
I also wonder if the installer has used Split-Insulation.
If so, then the split will be gaping open on the side which faces into the wall.
The approved method is to use adhesive to join the splits,
and for all bevel-cut ends around pipe elbows.
This then gets an outer layer of 'tape' to further cover the joins.
Armaflex and Kaiflex both manufacture UV-resistant external insulation.
It's usually sold as "solar insulation" because it gets used on roof-mounted solar-thermal collectors.
Save energy... recycle electrons!
As for the steel shed, I would expect to see around 100mm thick insulation sheet for the roof,
and around 75mm for the walls and door.
It must be draft-proof,
which may require neoprene rubber gaskets to be cut and glued around the pipe-exit holes.
I can provide further construction details if required.
The adhesive will be a 'contact' type such as this from Screwfix
Pipe insulation is usually best undertaken as a DIY task...
... preferably by someone with OCD!
Save energy... recycle electrons!
@transparent Hi, I spend most of my time on international travel through work.
However, I have taken some time to check what you guys are saying and you're entirely correct.
See pics!
My first avenue was simply to get it all corrected, however I see now I will have to find the time to do most of it myself if I want it done well.
If I posted pictures of the horrific work they did in my house I think you guys would turn up with pitch forks outside their office!
If you're going to take a DIY route to fixing the pipe insulation, then you should be asking for a rebate from the installer.
To calculate this, first ask them how long it will take them to remove what's there and do it again properly.
Then use £45/hour per person and add in the cost of buying the insulation yourself.
That should provide you with a good starting point.
They'll be super busy and wanting to get on with their next job rather than fix yours.
So the option of repaying you in cash will be tempting for them.
One possibility for you to consider is to make a rectangular box around those external pipes and seal them in...
... at least for the main vertical run.
There are PVC parts used by window-fitters and firms who clad facia boards, which could be fashioned into suitable boxing.
Save energy... recycle electrons!
@transparent I couldn't agree more, my first idea when looking at it was to box it in.
There isn't enough clearance between the pipes and wall to insulate it much better.
My sons arm was recently injured quite badly, but as soon as he is fit I will lob him up in the loft to check the pipe insulation in there. I wouldn't be at all surprised if it is just the rockwool!
Absolutely!
Child labour is well suited to the task of pipe insulation in confined spaces.
To seal where pipes enter the steel shed, I'd be using offcuts of EPDM rubber roofing material.
It's excellent for shaping around joins, and easy to cut.
You can glue it directly onto existing vertical surfaces.
So it's also a good choice to seal the top of your boxing.
Save energy... recycle electrons!
I know I'm late to this but I thought it would be worth pointing out that insulation of pipe runs outside the thermal envelope of the house is a building control matter. The installers should be responsible for complying with those regulations.
The relevant sections are 4.24 to 4.26 of approved document L:
It's worth noting that the insulation thicknesses described in that document are for very high quality insulation (i.e. very low thermal conductivity and low emissivity). The building regs defer to BS 5422 for lower performance insulation, and that can have a huge influence. See the attached two tables for low and high emissivity insulation, cribbed from a verv old copy of BS 5422.
If we take 22mm pipe as a reference. The really high quality insulation would require only 8mm thickness, but if it was high emissivity then that would increase to 11mm and if it then had high thermal conductivity typical of the sort of neoprene like insulation (~0.04 W/mK) then you'd need 23mm insulation to meet the regulations. That's a big jump from 8mm!
As an aside, the building regs are a great source in some areas like this. IMHO they're easy to read and a model of clarity.
I agree @mark-h The Building Regs are now very readable...
... although I do miss the sections of 'advisories' and illustrations of acceptable practices which used to be present.
There's an additional problem when selecting external pipe insulation because it has to be UV resistant of course.
The range of sizes available for installers to choose from is therefore reduced,
and especially so if they wish to use larger bore insulation around valve bodies.
Pipe Lagging offer a selection of 'solar' pipe insulation online, but it's expensive once you opt for sizes outside the common pipe diameters.
Another option is to swathe UV-resistant tape around the odd-sized sections and bends.
But my own experience with this approach is that the adhesive on the tape isn't good enough to hold firm around tight corners.
It needs supplementing with contact-adhesive at the edges.
There are also anti-UV paints which can be applied on top of existing insulation...
... provided it hasn't already been degraded of course!
Save energy... recycle electrons!
Currently viewing this topic 1 guest.
- 27 Forums
- 2,484 Topics
- 57.3 K Posts
- 520 Online
- 6,196 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Warranty Repairs- An Un Eddi fying experience!
@editor Did you have one of the really old ones with th...
By swwils , 2 hours ago
-
RE: Brine pump error message on Thermia 8kW ground source heat pump system
@schanna I’ve just DM’d you a potential company that’s ...
By Mars , 2 hours ago
-
RE: Tell us about your Solar (PV) setup
Actually not that far, however, the cost of my...
By upnorthandpersonal , 2 hours ago
-
RE: Passiv Smart Thermostat - Help & Forum Support
@petch I’ve not come across anyone yet that’s used thes...
By Mars , 2 hours ago
-
RE: Hoped for improvements not being realised on my Mitsubishi heat pump
Steady green means that the pump is running full speed....
By smsm1 , 3 hours ago
-
RE: Help…my NIBE heat pump has faulted again!
@jamespa I meant to say I attached the report from the ...
By Fiona , 4 hours ago
-
RE: Rate the quality of your heat pump design and installation
I don’t have the strength to post this tonight, but I’v...
By Mars , 4 hours ago
-
Vaillant app under reporting flow temperature
Our Vailllant 5kW heat pump is working well and the hou...
By Bengeo , 4 hours ago
-
@boycey, in your scenario if you use Melpump to change ...
By Majordennisbloodnok , 8 hours ago
-
RE: A Smarter Smart Controller from Homely?
Yep- already done that....nothing novel as such but som...
By benson , 8 hours ago
-
RE: Help needed to adjust weather compensation on Vaillant air source heat pump
I am in the fortunate position of having independent mo...
By MartinRobinson , 9 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@swwils Similar here, though it has been very mild. I...
By KevH , 11 hours ago
-
RE: Home energy storage & battery register
@toodles thankfully we have a range of tariffs to meet ...
By TechnoGeek , 13 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@editor thanks Mars! I'll contact them.
By kevinmc1970 , 14 hours ago
-
RE: Noisy Grant Aerona 3 13kW ASHP question
@heymikey thanks for the update and sorry to hear that ...
By Mars , 1 day ago
-
RE: Heat loss calculations and how they work in conjunction with heat pump sizing
@jamiejones85mespa your comments are spot on with my th...
By AgentGeorge , 1 day ago
-
RE: The good, the bad and the not that great – my heat pump installation
Must of knocked a load of crud through when they added ...
By Burtis , 1 day ago
-
@mkz, yes I have other installers... can you please sen...
By Mars , 2 days ago
-
I should add that our survey came up with a heat loss o...
By MartinRobinson , 2 days ago
-
RE: Optimising LG Therma V R32 using AI
@bontwoody oh dear! ... but as you say.. I suppose th...
By Tim441 , 2 days ago
-
RE: Volumiser required on Grant R290 air source heat pump?
@judith Indeed it's similar to the UK. It has to be an ...
By Patrick , 2 days ago
-
RE: Say hello and introduce yourself
Underfloor hydronic, powered by both the heat pump and ...
By upnorthandpersonal , 2 days ago
-
RE: PV export revenue and HMRC
That makes sense. They are companies that are on market...
By Batpred , 2 days ago
-
RE: R290 Heat Pump and Foundation Air Bricks
I have been having fun and games whilst getting surveys...
By petch , 2 days ago
-
RE: Ideal HP290 14kW ASHP - how to optimise
@ashp-bobba brill thanks again!
By cmartinbwmba , 3 days ago