Ecodan consuming 100kwh per day in new build!!!

33 Posts
13 Users
6 Reactions
924 Views
(@anca1808)
Active Member Member
60 kWhs
Joined: 3 weeks ago
Posts: 7
Topic starter  

Hello, 

I am super desperate so please if anyone heat pump savvy could help!!!

I just bought my first home.

It has an Ecodan Mitsubishi heat pump.

In 4 days that we have been in ...using just the kettle and trying to get heating to around 22 degrees ( as we have a small baby) we have used 400kwh!

 my setup is 

downstairs underfloor heating with 4 termostats ( set at 21) ( zone 1)

4 double bedroom upstairs with radiators one termostat ( set at 20) ( zone 2) .

I am of medical background so barely understood anything about heat pumps. I have desperately read so much about heat pumps in last 48h  but still have no clue how to optimise efficiency. I have asked developer to help. they sent a plumber out and he just reset stuff but not much help as this did nothing to the energy consume...i am still down 60kwh from 1 pm til 10pm currently...

Downstairs ok temperature wise ( reaches 21, but i am scared to push it more due to consume), but upstairs nothing happens even if we put to 22 the termostat our desired temp. we stopped it because we are scared that something is not right as radiators barely get warm, temperature is actually 19.5 when i put it to 22 and i think heat pump is running non stop unefficiently. 

Anyway,  my COP is around 2 i think ( consumes 800kwh and produces 1600kwh....i hope that is how it is calculated).I  have no wifi yet as just moved in and cant connect to melcloud to download more data, but something is clearly wrong as house is cold and i am consuming 100kwh with nothing on inside .

Currently sleeping with baby on couch in livingroom as bedroom is far too cold at 18 degrees during night.

If anyone could help please with somesort of guide of what settings should i use or what could be wrong ....

Oh house is B ( 85) EPC rating .

Ps . I called mitsubishi and to send an engineer out takes a few weeks. by that time my bills will be the size of my mortgage so i am really panicked.....


   
Quote
Mars
 Mars
(@editor)
Illustrious Member Admin
26256 kWhs
Veteran
Joined: 4 years ago
Posts: 2979
 

First of all, congratulations on your new home and welcome to the forums. I’m sorry to hear you’re having such a stressful experience, especially with a little one to keep warm.

Can you please, if you have it, share your property heat loss with us as well as the size of the ASHP (in kWs). 100 kWh/day is a lot, even with the colder weather we’ve had of late. How big is the property in sqm, roughly? 

Your COP of around 2 suggests the system isn’t running as efficiently as it should, and there’s any number of things that could be contributing to this, and we’ll try to help. 

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Subscribe and follow our Homeowners’ Q&A heat pump podcast


   
ReplyQuote
(@guthrie)
Estimable Member Member
696 kWhs
Joined: 1 year ago
Posts: 67
 

That sounds really bad, our one uses a quarter of the energy when it is close to freezing. 

Do you have any documentation about the system?  If you do would you be able to type out what people request, information about the system and any settings?

Also is the heat pump heating a hot water tank?  The reason I ask is that for instance our one uses a lot of electricity for an hour in the morning to heat the water to 50C and sometimes if there is anything wrong with it, you end up using more electricity to keep heating the tank all day just because someone didn't set it up correctly.

Finally, we do sometimes find that photographs of an installation can help in diagnosis, would you be able to put some up later?  Something showing the pipes indoors to any tanks, any distribution manifolds that send the hot water out to the floors and radiators, the pumps that circulate the water, and of course the radiators themselves, I assume they have some kind of temperature control valve on them?


   
👍
1
ReplyQuote
(@anca1808)
Active Member Member
60 kWhs
Joined: 3 weeks ago
Posts: 7
Topic starter  

Thank you for your reply.!

The property is 150m2.

Unfortunately, i have no idea about heat loss ( did not have a surveryor calculate it.....would it be anywhere on a document?

IMG 20250218 WA0002

) ... It is a new build everything is double glazed , and i checked loft and it has thick insulation. there are mild draft here and there, but nothing to cause the upstairs not to heat up if radiators would turn hot. I know for sure that the pipes in garage and around the heat pump need lagging. will attach a picture of loft and model of pump (I do not know the size of it as it is not written anywhere or it might be written but I would not know) ....from 3 pm today until now at 10 pm i consumed 54kwh and had nothing on but my phone to charge . heating upstairs was on since 3 and it is still 19.5 , radiators ice cold. so just put stats to 19.5 to not consume more.

the temp of the flow pipe at the heat pump is 29 degrees....and the return one was 27. i don t know if that helps or what its suppose to be .....

The pump was comissioned in 2021 and there is no documentation if it was ever serviced ...

20250220 083235
20250220 221643

I hope some of the images atached as it is first ti

20250220 223526

me i use this .

i feel i read so much about heat pumps in last 48 h that i am ready to enrol in a full training .....

This post was modified 3 weeks ago by anca1808

   
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
26256 kWhs
Veteran
Joined: 4 years ago
Posts: 2979
 

@anca1808 deep breaths. It’s quite a steep learning curve, but you’ll get there. It just takes time unfortunately to get your head around things. What was your approximate outdoor temperature today?

You have a 8.5kW unit so hitting 100kWh per day is very, very high.

This post was modified 3 weeks ago by Mars

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Subscribe and follow our Homeowners’ Q&A heat pump podcast


   
ReplyQuote
(@guthrie)
Estimable Member Member
696 kWhs
Joined: 1 year ago
Posts: 67
 

Thanks for the photos that is useful.  A 2 degree drop between out and inflow, that's I think fairly normal, but where is the heat going?  You will lose some through the unlagged pipes by the tank, but then the garage will also feel warm. 

If is is nearly 4 years old and has not been serviced, I can guess there might be some issues, from blockages to wrong pump settings, but assuming the electricity measurement is correct then it should be putting heat somewhere. We can track it down, others will be on here at some point with more experience.


   
ReplyQuote



(@guthrie)
Estimable Member Member
696 kWhs
Joined: 1 year ago
Posts: 67
 

I see the checklist mentions Polypipe Smart Stat, which is apparently one of these:

https://www.plumb2u.com/polypipe-smart-programmable-room-thermostat-ufhsmartw-c2x32033111

do you have it somewhere?

 


   
ReplyQuote
(@anca1808)
Active Member Member
60 kWhs
Joined: 3 weeks ago
Posts: 7
Topic starter  

thank you all for the responses and the patience.

Luckly i am on maternity  leave and have a bit of time . although after working 70h/week as a neurosurgeon i did not fancy learning about heat curves 😂

the weather outside today was 14 degrees ....the garage is well insulated , but it is not very warm inside i would say warmer than outside anyway. 

I have those stats all around the house. 4 downstaies and 1 upstairs.

we are wondering the same, where is all this heat going. the meter readingz are accurate i have a smart2 meter . I switched yesterday to an octapus cosy apparently better for heat pumps......noynsure if better with mine as it seems a money pit.

 Should i ask my developer to pay my astronomical bill?


   
ReplyQuote
(@guthrie)
Estimable Member Member
696 kWhs
Joined: 1 year ago
Posts: 67
 

Well if you brought it brand new just now then you surely have a case to go back to them and threaten legal action, but 3 and a bit years latejudging by the commissioning date, you might need to set your solicitor on whoever sold you the house.  Here in Scotland anyway you can get money back from them if things in the house aren't quite right and you let them know within a specific time of moving in.  I suspect a malfunctioning heating system would count, but I am not a lawyer and you should consult one.


   
ReplyQuote
rob_cirrus_energy
(@rob_cirrus_energy)
Eminent Member Member
156 kWhs
Expert
Joined: 2 months ago
Posts: 11
 

Hi Anca1808, 

 

Welcome to the forum. 

 

First off, please try not to panic. We just need to do some problem solving. 

 

1. Where are you getting the kWh reading from, is this from the heat pump control centre, your smart meter?We need to know if that is the reading from the whole house or just the heat pump or just the plantroom area. 

2. Please check your immersion switch is not on. This is the light switch style near the cylinder that is hopefully labelled as immersion, which may have been set up as an on/off override. This will massively increase your total house electricity consumption if left on. Hot water should be heated only by the heat pump and the switch is only for if there's an issue with the heat pump. 

2. That whole plantroom need lagging. I am astounded it has been left like that. This needs to be rectified as a matter or urgency. You can ask the builder if the property was bought from new or if not you can either get some foam builders lagging and pop that on for now until you can get a professional out to do it or just get a plumber out to sort this. 

3. The low differential across the flow and return suggests to me that the heat pump is running against a low volume when the heating is off at the thermostat. Please confirm if you have actuators (white heads on the underfloor manifold) or TRVs on the radiators. The heat pump does not appear to have a volumiser to run against. Heat pumps should run for long periods and then stay off for long periods since steady operation is when they're at their most efficient. 

4. Please upload a picture of the pipework behind the heat pump outside so we can see if this is insulated. 

5. Is the plantroom in an unheated space eg garage or utility? If so this will only further negatively impact the efficiency on the unlagged system. 

6. The commissioning (setup) temps look fine to me and I would not advise that you adjust any settings for now. 

Best, 

Rob at Cirrus Energy

Heat pump consultant and designer at Cirrus Energy.
Thinking about installing a heat pump? Or already have one but it’s not performing as it should? Book a one-to-one session with Rob to discuss things here.


   
ReplyQuote
(@guthrie)
Estimable Member Member
696 kWhs
Joined: 1 year ago
Posts: 67
 

Also from what I have read it isn't impossible for a meter to be wrong but in your case for it to be wrong and the house not heating up is all too much at once. 

Random thought, is there really insulation below the underfloor heating coils?  You can't really tell though without investigation.


   
ReplyQuote
(@anca1808)
Active Member Member
60 kWhs
Joined: 3 weeks ago
Posts: 7
Topic starter  

To make it a bit clearer as we asked the same about the 2021 commisioning. the house is on a small estate and it is a corner plot build for the developer himself. he wanted to keep the house for him or his family.It has high specs and it is well build . fully brick copper pipes etc , but it was never finished until last year. long story short he did not want it in the end ( got another one bigger)  and it was put on market for sale last year.

Hence the shocking no insulation around pipes.As house was just left....until all the estate was sold and he decided to sell it as well.

I do not know if the unfloor has insulation aroind the coils . all the radiatoes upstairs have trv and there are actuators.

there is no immersion switch....we looked for one and nothing of some sort . unless we did not see it.

i left the settings as they are.

I am taling about the smart meter fornthe whole house. In the house we only have the oven dishwasher and kettel.  when we got the key friday 14 the meter reading was 19450. we moved in with a couch and the cot and aome bits and bobs on 16th night. on 17 i rang octapus to set up my account transfer and they asked for a neter reading again and it was 19680 . they said it is too high to double check and send it again in 24 to 48h. on 19 at 7 am i sent another meter reading and it was 19860 . They said something is very wrong with consuming 400kwh so fast hence why all the drama .Bare in mind i only used kettle 4 5 times,  once the dishwasher and once the oven and yes some lights at night....so i assumed that majority of  it is from the heatpump...


   
ReplyQuote



Page 1 / 3



Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security