Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Ecodan Legionella cycle - immersion heater problem
I've had my 6kW Ecodan and (non-Mitsubishi) cylinder for 6 weeks.
I noticed that the Legionella cycle wasn't raising the tank temperature as high as it should have, so I fitted a Shelly EM clamp current monitor to the immersion supply cable from the consumer unit.
This is set up in Home Assistant, along with monitors for the ASHP supply and some Shelly temperature sensors, so that I can get graphs of what's actually happening.
The DHW is set to come on at midnight, target temp 49 degrees.
The Legionella cycle is set to every 15 days, starting at 01:00, max duration 2 hours, and 10 minutes holding at max temperature.
The Legionella cycle ran last night, and the temperature only got to 54 degrees
First graph is the heat pump power consumption, second is the tank temperature (from the Ecodan tank sensor), third is the immersion power consumption.
Everything looks right - heat pump heats the tank water as normal, then runs for the first part of the Legionella cycle, and goes to idle when the immersion takes over.
Immersion runs normally for about 20 minutes, then starts switching on and off.
Legionella heating cycle ends on schedule, and a few minutes later the heat pump comes back on for heating.
Tank never got above 54 degrees.
Dodgy immersion, or the Mitsubishi controller playing up?
I took the cover off the immersion 2 weeks ago, and it looks like the thermostat is set for 65 degrees.
Possibly a dodgy immersion heater thermostat? An immersion heater element would normally run (the 3 kW power level is right) until it reaches the set temperature then cutout; looks as though your thermostat needs attention (or replacement?). Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
I've had a closer look at the immersion heater. It seems that this model (Thermowatt RTS 3 ERP) is available in 3 different versions. I managed to find the proper instructions, and the different models gave different colour adjustment knobs, deniting different temperature ranges. Mine has a yellow knob, and is only adjustable between 52 and 60 degrees!
I've turned it up to full whack, and set the Legionella cycle to start at 11:00....
@clockworks Sounds like you may have your answer there then! Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Hi Clockworks. Have a look at this existing discussion about Ecodan - Legionella Operation Time and Target Temperature.
Not only is there heaps of technical detail, but that topic was the second occasion on which members here suggested that the Mitsubishi software is flawed in respect of the anti-legionella target temperature.
Posted by: @clockworksImmersion runs normally for about 20 minutes, then starts switching on and off.
Good observation. That doesn't sound right.
@editor -- can we move this discussion to the end of that other topic please?
Save energy... recycle electrons!
Reading the thread linked to, very similar setup to mine.
To me, it seems like the installers have made an error by fitting an immersion that will cut off at 60 degrees, and then setting the heatpump controller to run the legionella cycle for 2 hours with a target temp of 60 degrees (as measured by a pocket sensor in the cylinder).
Chances are, the sensor will never actually read 60 degrees, so the cycle will just run for 2+ hours with the immersion cycling every few minutes. During all this time, the heatpump will be in "standby" doing nothing, and the house will cool down.
They should really be fitting immersion thermostats that enable running at above the maximum legionella setting of the heatpump controller. That way, the controller would actually be in control, not waiting for an event that will never happen, and then timing out.
Assuming I'm correct, the answer in my case will be to set the Mitsubishi's Legionella temperature to 58 degrees for now. It should then actually reach 58 degrees, hold for 10 minutes, and revert to heating mode.
I'll raise my concerns with installer.
Seems like I can't force it to run a Legionella cycle, and setting it to run at 11:00 daily didn't work, presumably because it knew it had already run a cycle overnight?
I have set it back to the usual time of 01:00, but daily, so I'll see what happens tonight.
I've also realised that I can't set a temperature lower than 60 degrees!
I'll contact the installer, try and get them to fit an immersion heater that will operate at over 60 degrees.
Posted by: @clockworksAssuming I'm correct, the answer in my case will be to set the Mitsubishi's Legionella temperature to 58 degrees for now. It should then actually reach 58 degrees, hold for 10 minutes, and revert to heating mode.
Yes. You've got it.
And you should definitely throw the problem back at the installers.
You musn't have the thermostat in the immersion heater and the heat-pump control fighting each other around 60°C
As for your 'workaround':-
A. I doubt the Mitsubishi software is that accurate.
You may need to drop lower than 58°C before you see any difference.
B. Others have reported that the Mitsubishi code itself is flawed.
Be prepared for the system still not working.
C. I also understand the biology of bacterial growth.
If you drop the temperature then you need to elongate the time at which the peak is being held.
And, on another issue, would you mind moving your anti-legionella cycle start-time away from it coinciding with a half-hour interval?
That's when there are surge-demands on the electricity grid because tariffs get changed at half-hourly intervals in UK.
It's 'grid-friendly' if you choose a more random time, such as 01:17
Save energy... recycle electrons!
The Mitsubishi controller only allows for setting the Legionella cycle start time in hourly increments.
All the other timers/schedules are adjustable in shorter increments.
The immersion thermostat is available as a "blue knob" version, which is adjustable between 63 and 71 degrees. That's the one they should have fitted.
@clockworks It rather sounds as though the heat pump manufacturers (or rather their software programmers) are not taking on board the need to lessen surges on the grid yet😒 Toodles
Toodles, heats his home with cold draughts and cooks food with magnets.
Posted by: @toodlesPosted by: @clockworksThe Mitsubishi controller only allows for setting the Legionella cycle start time in hourly increments.
It rather sounds as though the heat pump manufacturers [...] are not taking on board the need to lessen surges on the grid yet
I'll raise that with the DESNZ committee who are creating the 'Standard' for Demand Side Response de-coupling of heat-pumps from the grid.
There are representatives of the ENA who are members,
and they have an interest in the avoidance of demand surges.
Save energy... recycle electrons!
To be fair, the total demand for the period was a maximum of 3kW - the ASHP goes idle while the immersion is running.
In contrast, my electric car's demand was 7.4 kW, but the charger is controlled by the energy supplier (Octopus). They tell the charger when to run, and can also knock the max current back if needed.
I was given a charging slot of 05:00 to 07:30, so I got an extra 2 hours at 7p for the whole house.
I think I read somewhere that Octopus will be able to do similar demand matching with their "Cosy" range of heatpumps?
It might be a good idea if some "randomisation" of schedules and timers was standard on electric heating systems though - just 5 minutes either side could make a difference in surges, and be transparent to the consumer.
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 330 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@agentgeorge I'll give it a go with my Apple Watch late...
By HarrisonC , 56 minutes ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 4 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 16 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 18 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 18 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 21 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 1 day ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 1 day ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 3 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 3 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago