Ecodan - Legionella Operation Time and Target Temperature
Hi. What's a realistic operation time for a legionaire cycle?
New system: Ecodan 11.2kw and Telford Tempest HP 250L tank.
Mine is set for two hours with a 60 degree target.
1st half hour the heat pump flow temp gradually ramps up and Tank temp goes from 20 > 49
2nd half hour the flow temp starts to drop and tank temp goes up by 1 to 50
3rd half hour the flow temp continues to drop and the tank temp goes from 50 > 56 (Immersion on)
4th half hour the flow temp continues to drop and the tank temp goes from 56 to eventually just reaches 59 on the 2 hour mark.
I guess if I extend the run to over 3 hours it might get to 60 but that seems an awfully long time to be without any heating next winter.
Any thoughts?
Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Octopus Fixed Rate
It appears that your current Legionella cycle is quite lengthy. Typically, achieving and maintaining a water temperature of at least 60°C for about 30 minutes is enough for Legionella prevention. Given that your system is struggling to reach this temperature within a reasonable time frame, some adjustments might be necessary.
Typically, in low temperature units (like ours) the heat pump gets us 50C, the immersion takes over and gets us to 60C relatively quickly. I’m not sure why your immersion is “struggling”.
There are a lot Ecodan users in the forums that can provide their insights.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Ecodan user here and I have disabled the Legionella cycle..it is just not necessary. Heating water to 50C is more than adequate to mitigate Legionella bacteria growth, and as nearly all domestic settings do not have dead legs and do not have aerosol producing equipment and will turn over the water capacity in the pipework regularly so the risk is negligible.
I also have Solar Thermal which raises the stored DHW temperature to 60C in any case and as the DHW is heated via the Ecodan's AlfaLaval heat exchanger there is no stagnant usable water in the 40C-45C state.
The 60C hype is an abundance of caution. Your mileage may vary!
@abernyte Thank you for your reply and I agree that it's debatable as to whether a legionaires cycle is necessary. However, we are classed as vulnerable so maybe better safe than sorry.
Regardless, this is a new system so, at this time, what I am doing is simply proving that the system can do it if required. Based on what I have seen so far, it would appear something is not quite right so I was seeking information on what timings are to be expected.
The decision as to whether I continue with a legionaires cycle or not will come later.
Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Octopus Fixed Rate
Understood. My 14kW Ecodan does the DHW cycle from cold 25Cish to 52C in about 30 minutes. I am not sure what yours is dawdling around doing! Just checked this mornings report: it started heating DHW at 1006hrs with flow temp of 28C and tank temp of 28C and completed it at 1035hrs with flow temp of 62C and tank temp of 52C. No solar gain due to 100% cloud cover.
@richard24738 I think the issue with your system, which requires investigation, is why it's taking so long and not ultimately getting to 60C. Like @abernyte, our heat pump (18kW) takes about 30 minutes to get the hot water over 50C, and then the immersion takes over. Since your system is new, I'd call your installers and also speak to Mitsubishi as everything is still under warranty.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor Thanks.
I, of course, thought something was wrong with the timings but wanted to be sure what is normal before contacting my installer or Mitsubishi.
Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Octopus Fixed Rate
Hi. Unfortunately on-going.
Mitsubishi agreed that the immersion was taking too long and also pointed out that my software was out of date.
Installer adjusted the immersion thermostat but I couldn't see a difference.
Last Test:
The heat pump gets DHW to 50 degrees within 30 minutes, switches off and then the immersion switches on.
It then took 1 hour 48 mins to go from 50 to 59.5.
Stayed at 59.5 for 42 minutes with the immersion sign on until the cycle timed out at 3 hours. It never reached my desired 60 degrees.
No errors recorded.
Agreed with the installer that we would wait for the software update and see if it fixed the problem.
Further Action:
Mitsubishi updated the software last week and I have a scheduled legionella cycle for tomorrow so will report back afterwards.
Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Octopus Fixed Rate
UPDATE
Mitsubishi changes made no difference and they want an engineer to visit.
Waiting for an appointment.
Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Octopus Fixed Rate
Can you read the model number of your immersion heater @richard24738 ?
We are used to all immersion heaters being rated at 3kW and supplied via a 2.5mm² cable.
But that may not be what your installer has fitted.
Is it possibly a 1kW unit?
Posted by: @abernyteI have disabled the Legionella cycle..it is just not necessary. Heating water to 50C is more than adequate to mitigate Legionella bacteria growth, and as nearly all domestic settings do not have dead legs and do not have aerosol producing equipment and will turn over the water capacity in the pipework regularly so the risk is negligible.
That is generally true.
But it also depends whether your aim is prevent Legionella pneumophila bacteria growing within the water in the first place, or to quench a colony which is already established.
The latter situation might occur if your heat-pump system has been left idle whilst occupants are on vacation, for example.
If your mains water supply meets the required standards, then the purification processes are adequate to eradicate Legionella pneumophila bacteria and the protozoa they use for replication.
However, public trust in water authorities isn't particularly high at the moment.
Even when staff pick up breaches in regulations, these are often being recategorised internally to avoid notifying relevant authorities.
Residents in the Brixham area of Devon became seriously ill in May/June'24 due to the presence of cryptosporidium in the water supply.
This entered through a broken air-release valve after the water had been through the treatment works.
It took South West Water three months to flush through the pipework and eradicate the contamination.
I suggest that a householder in Brixham would be responding here very differently to @abernyte
Some of them are so traumatised that it's unlikely they will ever drink tap water again.
[aside] It's interesting to me that heat pump manufacturers seem to have universally chosen heating via an immersion as their method of deactivating pathogens.
The water authorities use UVc radiation (200nm - 280nm) which is extremely effective.
Since it is now possible to buy LEDs emitting 265nm, I wonder why these aren't being used for DHW tanks?
The running costs would be much less, even after factoring in the need to replace them at regular maintenance intervals.
What does @editor think?
Save energy... recycle electrons!
@transparent Hi. Thanks for the comments.
Just had a look at the immersion and it's a "THERMOWATT 3KW".
In fact my 14 day cycle for Legionnaires was yesterday so I have up to date results.
Ecodan > 50c = 29 minutes
Immersion 50 > 54.5 = 1 hour
Immersion 54.5 > 58.5 = 31 minutes
Cycle timed out at the 2 hours set by Mitsubishi. It never reached the target 60c for 5 minutes.
So it would seem that the start up of the immersion is where time is excessive.
I am aware of the discusions as to whether a legionnaire cycle is necessary in a domestic setting and I think it really depends on your circumstances and usage.
If I was a fit 30 year old then I probably wouldn't run it. I am however older and considered vulnerable so, to play safe, will run it.
Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Octopus Fixed Rate
- 22 Forums
- 2,074 Topics
- 45.5 K Posts
- 111 Online
- 3,350 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: 5 Star Service from Havenwise
@sheriff-fatman Good post. I am also considering Hav...
By Morgan , 1 hour ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@editor Cobbler’s Mantra that!
By Toodles , 2 hours ago
-
RE: What’s the modern take on advised types of insulation?
Grant was my local MP before he lost his seat. He was ...
By Jeff , 17 hours ago
-
RE: Radiators downstairs are cooler at the bottom after ASHP install
@melonbuffet This is great assuming now the down stairs...
By ASHP-BOBBA , 20 hours ago
-
RE: Commencing on an ASHP Installation Process
@jamespa Thanks for your input into this thread so far....
By Sheriff Fatman , 20 hours ago
-
Pacific Blue reveals ageing Codrington Wind Farm decommissioning plans.
Australia Blue, the first wind farm in Western Victoria...
By Morgan , 21 hours ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
The challenge is who pays, who holds the debt and the i...
By Jeff , 1 day ago
-
RE: Flow rate discrepancy between ASHP and manifold
That's useful thanks, I hadn't seen that table before. ...
By AshRolls , 2 days ago
-
In principle I agree, @johnmo, but with provisos. The...
By Majordennisbloodnok , 2 days ago
-
RE: Heat pump installation and BUS Grant timings
@jamespa Thats how I understood it too. 🙂
By ASHP-BOBBA , 2 days ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
@sallyl That sounds about right if they are re-filling ...
By Brendon Uys , 2 days ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
I would switch it off and see if anyone noticed. We use...
By Anonymous 5011 , 3 days ago
-
I wouldn't be so sure about that. Heat pump designers ...
By JamesPa , 3 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@toodles they're a rowdy bunch!
By Mars , 3 days ago
-
RE: Home energy storage & battery register
@jamespa To a certain extent, by exporting to the grid ...
By Toodles , 4 days ago
-
RE: Forum updates, announcements & issues
@editor Fairy Nuff Mars, I doubt that my ramblings woul...
By Toodles , 5 days ago
-
RE: Confusion about heat pump sizing
We’ve published a deep dive into heat pump sizing, and ...
By Mars , 5 days ago
-
We’ve published a deep dive into heat pump sizing, and ...
By Mars , 5 days ago
-
RE: Kensa GSHP finally installed - now to start the optimisation process
Just had a quick scan of the manual and should be weath...
By Anonymous 5011 , 6 days ago