Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
PV and battery long payback - sense check query
Posted by: @majordennisbloodnokNonetheless, assuming you were to get a fairly chunky compliant inverter - let's say a 12 kW inverter - my understanding is that it would be acceptable for the DNO to issue a G98 certificate on the understanding the inverter was limited to a maximum of 3.6 kW export to the grid.
My understanding is that will require a G99 and a G100. It's common to refuse a large G99 in many areas. It's unfortunately becoming increasingly common to refuse or tightly limit even G100 on fragile rural networks.
I think there are 4 paths
- 3.6kW inverter, G98, no extra plug in stuff. DNO can be unhappy but it's their problem and they'll have to spend some of the shareholders yacht money fixing problems (as slowly as possible).
- G99 to try and get a bit more - but may be refused, may also be ludicrously small like going from 3.6kW to 4kW. That said 5kW for many people is a lot better than 3.6.
- Big inverter, G100 - may get refused but this is the nice grid tie option and gets you capacity, big batteries and options to balance it sensibly with loads of solar easily if you pick the right products.
- Big inverter, don't grid tie, use the grid as input only
The last option you get a big grid forming ("off grid") inverter, wire the grid as generator input, and run the house off it. There's no feeding back into the grid so there are no problems with you overloading anything beyond blowing your house fuse. You need a transfer switch so you can reconnect the house directly to the grid (in case the inverter dies), ground rod and some oddments, and you need an offgrid inverter which can field your house load, and also pass through your house load (so 60-80A). The kit for this is widely available - as you can imagine large rural farms hit this quite often and may well want to go well beyond 16kW with 50kW+ 3 phase options being widely used.
You are essentially then operating an off grid house, whose generator happens to be a wire to the national grid. The downsides of that are that a) your inverter needs to be big enough to field your largest demand so costs more, and b) you won't get any SEG payments, which I imagine isn't going to happen much anyway.
It is possible to build hybrid setups with a mix of on and off grid inverters sometimes sharing the batteries. However that tends to turn into an infeasibly large amount of electrician hours and lots of very expensive blue boxes.
Currently viewing this topic 1 user ( Majordennisbloodnok ) and 2 guests.
Recently viewed by users: EtchedPixels 1 hour ago.
- 27 Forums
- 2,741 Topics
- 64.3 K Posts
- 1,293 Online
- 7,145 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: PV and battery long payback - sense check query
My understanding is that will require a G99 and a G100....
By EtchedPixels , 1 hour ago
-
RE: Indevolt Batteries UK Support & Info Thread
@transparent Thanks for adding this level of accuracy t...
By Indevolt Tech , 4 hours ago
-
RE: Do I need to change the control unit when replacing my Ecodan Air Source Heat Pump
Kind of you, @calumm, but it was @f1p who did the heavy...
By Majordennisbloodnok , 7 hours ago
-
The "thermal comfort" we feel is a mix of air temperatu...
By bobflux , 7 hours ago
-
RE: Electricity price predictions
2. As EV ownershp increases it'll certainly increase de...
By EtchedPixels , 18 hours ago
-
I meant to say I cannot register my kit at Energyplus… ...
By Batpred , 18 hours ago
-
RE: HomeTherma Is Live: A New Home-Energy Platform Built Around the Homeowner
Signed up!
By bobflux , 2 days ago
-
RE: Has anyone seen this problem before? Huge anticycling times
Oh dear. Glad it was replaced. I have been mighty imp...
By JamesPa , 3 days ago
-
RE: Can I start an argument about buffer tanks please? 🙂
Dont, just adjust the LSVs to get different temperature...
By JamesPa , 4 days ago
-
RE: Heat pump running costs – what has actually worked for you?
I installed the air source heat pump in January 2026, i...
By bobflux , 4 days ago
-
RE: Grant Aerona Air to Water R290 6.5 kW - Quiet Mark and Silent Running
Thats all interesting. DHW on my Vailant seems to respe...
By JamesPa , 4 days ago