Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Different dT on each radiator?
All supplier surveys I've had, as well as tools like Heatpunk, assume the same dT (typically 5°C) across all radiators. In my house, with 8mm microbore radiator tails, that leads to very high flow velocity and pressure loss on the index circuit. Is there a reason not to run a higher dT (say 8°C) on some radiators to lower flow velocity and pressure loss? Other radiators could then run a lower dT so the heat pump still sees a combined dT of 5°C?
The way heating systems are designed will result in roughly equal dts across each radiator.
However design and reality may well differ so if it turns out that in practice radiators exhibit different DTs after balancing, that is not a problem so long as the house heating is satisfactory.
You can design for higher DT than the default 5 but there is an efficiency penalty of approximately 1.5% for each degree the system dt in increased above 5. This efficiency penalty may well be worth suffering to avoid major disruption.
If you want to design some rads for a DT of 8 and some for a DT of 5 you will need to do very detailed calculations of each circuit. This is probably not worthwhile and also requires details about your plumbing that cannot be readily obtained without taking up all the floorboards and calculations that few will be able to carry out.
Far simpler than trying to adjust for varying DT is to design the whole system for DT8 and adjust at commission time by balancing. This will result in marginally larger radiators than necessary but is the practical solution to the problem you describe.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa Thanks for getting back to me.
I know my pipework lengths and diameters (a combination of lifting floorboards, a borescope, and a thermal camera) so can have a good go at calculating pressure drops for each radiator.
On the subject of higher dT for the whole system rather than for a single radiator, I've often wondered what the efficiency penalty is so thanks for providing a number - can you point me towards a source with some more detail on that? Do you know if a Vaillant aroTHERM plus 5kW varies pump speed to maintain dT5, or runs a fixed pump speed so allows dT to vary?
Posted by: @medwardzOn the subject of higher dT for the whole system rather than for a single radiator, I've often wondered what the efficiency penalty is so thanks for providing a number - can you point me towards a source with some more detail on that?
I cant sorry. Its based on some calculations I did from Mitsubishi's R32 COP VS FT tables, which roughly gives a penalty of 3% for each degree increase in the DT at design OAT. Its a bit less, perhaps only 2.5%/C, for very low design FTs (eg <40) and a bit more for relative high design FTs (eg >50). So its rough and ready at best. Other commentators seem to say similar, but it maybe that I started it off!
I then assume that, if DT is changed, you need to raise/lower the FT by half the change in DT to keep the average surface temp (and thus rad output) the same. So if FT of 42.5 works at DT5, you will need FT of 45 at DT10.
Posted by: @medwardzDo you know if a Vaillant aroTHERM plus 5kW varies pump speed to maintain dT5, or runs a fixed pump speed so allows dT to vary?
I have the 7kW Arotherm and frankly I cant work out exactly what it does as I don't have a way to monitor pump speed aside from the Mk1 eyeball. It certainly does vary pump speed a bit, but there is no evidence from the little data I have collected that it maintains a fixed DT. The guys on the Vaillant thread on openenergymonitor may know.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 27 Forums
- 2,753 Topics
- 64.7 K Posts
- 804 Online
- 7,158 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Glass lined Cylinder for private water supply
This has turned into a fascinating little rabbit hole. ...
By Mars , 7 hours ago
-
RE: Adventures in heat loss calculations
yes and no. apparently HG’s AI was automatically assumi...
By Batpred , 7 hours ago
-
RE: Switch suitable to change between two inverter CT's
Last winter my battery ,32KWh, could run the house com...
By Jancold , 8 hours ago
-
RE: How Accurate Is My DIY Heat Loss Calculation?
@rob-of-york Thank you for that, whilst familiar with t...
By kilgorexv , 8 hours ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
Agree with Major. And even if I was very happy with ...
By Batpred , 8 hours ago
-
RE: Is the "divide by 2900" rule still valid?
There is another estimator that you could use, a formul...
By Rob of York , 12 hours ago
-
RE: To re-pipe or not to re-pipe? Moving from oil boiler to air source heat pump.
@penval, really useful update. After all the discussion...
By Mars , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
@papahuhu I prefer to look at it simplistically. We d...
By Old_Scientist , 4 days ago
-
RE: Questions about A2A for heating as well as cooling
@rob-of-york I would concur with the underfloor insulat...
By Toodles , 4 days ago
-
RE: New Vaillant Arotherm controls link to existing thermostats ; wired vs wireless
Nothing attached! I have rads but UFH makes the case ...
By JamesPa , 4 days ago
-
RE: Cooling with air to water heat pumps
Passive cooling should always be the first call. Keep ...
By JamesPa , 4 days ago
-
RE: Do I add Air Con or MVHR to existing A2W ASHP?
@rob-of-york Thank you, I’m thinking along these same l...
By Toodles , 5 days ago
-
@Mars Good questions! The downstairs unit did the maj...
By Rob of York , 5 days ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@dave, I think @jamespa has probably identified the mos...
By Mars , 5 days ago