Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Different dT on each radiator?
All supplier surveys I've had, as well as tools like Heatpunk, assume the same dT (typically 5°C) across all radiators. In my house, with 8mm microbore radiator tails, that leads to very high flow velocity and pressure loss on the index circuit. Is there a reason not to run a higher dT (say 8°C) on some radiators to lower flow velocity and pressure loss? Other radiators could then run a lower dT so the heat pump still sees a combined dT of 5°C?
The way heating systems are designed will result in roughly equal dts across each radiator.
However design and reality may well differ so if it turns out that in practice radiators exhibit different DTs after balancing, that is not a problem so long as the house heating is satisfactory.
You can design for higher DT than the default 5 but there is an efficiency penalty of approximately 1.5% for each degree the system dt in increased above 5. This efficiency penalty may well be worth suffering to avoid major disruption.
If you want to design some rads for a DT of 8 and some for a DT of 5 you will need to do very detailed calculations of each circuit. This is probably not worthwhile and also requires details about your plumbing that cannot be readily obtained without taking up all the floorboards and calculations that few will be able to carry out.
Far simpler than trying to adjust for varying DT is to design the whole system for DT8 and adjust at commission time by balancing. This will result in marginally larger radiators than necessary but is the practical solution to the problem you describe.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa Thanks for getting back to me.
I know my pipework lengths and diameters (a combination of lifting floorboards, a borescope, and a thermal camera) so can have a good go at calculating pressure drops for each radiator.
On the subject of higher dT for the whole system rather than for a single radiator, I've often wondered what the efficiency penalty is so thanks for providing a number - can you point me towards a source with some more detail on that? Do you know if a Vaillant aroTHERM plus 5kW varies pump speed to maintain dT5, or runs a fixed pump speed so allows dT to vary?
Posted by: @medwardzOn the subject of higher dT for the whole system rather than for a single radiator, I've often wondered what the efficiency penalty is so thanks for providing a number - can you point me towards a source with some more detail on that?
I cant sorry. Its based on some calculations I did from Mitsubishi's R32 COP VS FT tables, which roughly gives a penalty of 3% for each degree increase in the DT at design OAT. Its a bit less, perhaps only 2.5%/C, for very low design FTs (eg <40) and a bit more for relative high design FTs (eg >50). So its rough and ready at best. Other commentators seem to say similar, but it maybe that I started it off!
I then assume that, if DT is changed, you need to raise/lower the FT by half the change in DT to keep the average surface temp (and thus rad output) the same. So if FT of 42.5 works at DT5, you will need FT of 45 at DT10.
Posted by: @medwardzDo you know if a Vaillant aroTHERM plus 5kW varies pump speed to maintain dT5, or runs a fixed pump speed so allows dT to vary?
I have the 7kW Arotherm and frankly I cant work out exactly what it does as I don't have a way to monitor pump speed aside from the Mk1 eyeball. It certainly does vary pump speed a bit, but there is no evidence from the little data I have collected that it maintains a fixed DT. The guys on the Vaillant thread on openenergymonitor may know.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,607 Topics
- 60.8 K Posts
- 279 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
@editor, I hear that too. I can confirm that out of ...
By ASHP-BOBBA , 5 hours ago
-
End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
As many of you know, our Global Energy Systems heat pum...
By Mars , 5 hours ago
-
@derbygraham fully agree with James, and it’d be good t...
By Mars , 6 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Finally got around to installing and setting up the Sol...
By Mars , 6 hours ago
-
Unfortunately its a function of the physics. Max heat ...
By JamesPa , 7 hours ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 7 hours ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 8 hours ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 10 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 10 hours ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 12 hours ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 15 hours ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 18 hours ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 1 day ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 2 days ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Many thanks for your, and the subsequent, answers tk qu...
By KevH , 2 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 3 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 3 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 3 days ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 4 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@optimistic-optimiser I have has a Daikin for a few yea...
By madsid , 4 days ago
-
RE: UK DIY Battery: SEPLOS 48V 200Ah x2 + Sunsynk 8K – Safe Installation for Garage Conversion
The rule of thumb is to ensure that you can isolate any...
By Transparent , 4 days ago