Different dT on each radiator?
All supplier surveys I've had, as well as tools like Heatpunk, assume the same dT (typically 5°C) across all radiators. In my house, with 8mm microbore radiator tails, that leads to very high flow velocity and pressure loss on the index circuit. Is there a reason not to run a higher dT (say 8°C) on some radiators to lower flow velocity and pressure loss? Other radiators could then run a lower dT so the heat pump still sees a combined dT of 5°C?
The way heating systems are designed will result in roughly equal dts across each radiator.
However design and reality may well differ so if it turns out that in practice radiators exhibit different DTs after balancing, that is not a problem so long as the house heating is satisfactory.
You can design for higher DT than the default 5 but there is an efficiency penalty of approximately 1.5% for each degree the system dt in increased above 5. This efficiency penalty may well be worth suffering to avoid major disruption.
If you want to design some rads for a DT of 8 and some for a DT of 5 you will need to do very detailed calculations of each circuit. This is probably not worthwhile and also requires details about your plumbing that cannot be readily obtained without taking up all the floorboards and calculations that few will be able to carry out.
Far simpler than trying to adjust for varying DT is to design the whole system for DT8 and adjust at commission time by balancing. This will result in marginally larger radiators than necessary but is the practical solution to the problem you describe.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa Thanks for getting back to me.
I know my pipework lengths and diameters (a combination of lifting floorboards, a borescope, and a thermal camera) so can have a good go at calculating pressure drops for each radiator.
On the subject of higher dT for the whole system rather than for a single radiator, I've often wondered what the efficiency penalty is so thanks for providing a number - can you point me towards a source with some more detail on that? Do you know if a Vaillant aroTHERM plus 5kW varies pump speed to maintain dT5, or runs a fixed pump speed so allows dT to vary?
Posted by: @medwardzOn the subject of higher dT for the whole system rather than for a single radiator, I've often wondered what the efficiency penalty is so thanks for providing a number - can you point me towards a source with some more detail on that?
I cant sorry. Its based on some calculations I did from Mitsubishi's R32 COP VS FT tables, which roughly gives a penalty of 3% for each degree increase in the DT at design OAT. Its a bit less, perhaps only 2.5%/C, for very low design FTs (eg <40) and a bit more for relative high design FTs (eg >50). So its rough and ready at best. Other commentators seem to say similar, but it maybe that I started it off!
I then assume that, if DT is changed, you need to raise/lower the FT by half the change in DT to keep the average surface temp (and thus rad output) the same. So if FT of 42.5 works at DT5, you will need FT of 45 at DT10.
Posted by: @medwardzDo you know if a Vaillant aroTHERM plus 5kW varies pump speed to maintain dT5, or runs a fixed pump speed so allows dT to vary?
I have the 7kW Arotherm and frankly I cant work out exactly what it does as I don't have a way to monitor pump speed aside from the Mk1 eyeball. It certainly does vary pump speed a bit, but there is no evidence from the little data I have collected that it maintains a fixed DT. The guys on the Vaillant thread on openenergymonitor may know.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,372 Topics
- 53.8 K Posts
- 288 Online
- 6,053 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Solar Power Output – Let’s Compare Generation Figures
2025 energy total: 7.4mW produced, 5.4mWh exported, 3.0...
By jamespetts , 7 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
If I had to make a guess, I’d say that there are one or...
By Majordennisbloodnok , 7 hours ago
-
RE: Connecting Growatt SPH5000 over wired ethernet rather than wireless
Thanks folks. I had tried googling an ethernet lab adap...
By z8lccda , 8 hours ago
-
RE: Data Accuracy Problem: Daikin 8kW Heat Pump's Onecta App vs MMI Power Consumption
@toodles Good evening. Thankyou for the response I...
By Nursethescreens , 8 hours ago
-
RE: Changing from 4-port buffer to volumizer
@toodles I'm not concerned that the behaviour is not no...
By Andy1618 , 8 hours ago
-
-
RE: Forum updates, announcements & issues
As we head into 2026, I just wanted to take a moment to...
By Mars , 12 hours ago
-
RE: Setback savings - fact or fiction?
I agree, and I think there are two things in play here....
By cathodeRay , 13 hours ago
-
RE: Water Hammer After Heat Pump Install
That's really helpful. Yor last sentence confirms it'...
By JamesPa , 18 hours ago
-
RE: Help needed with Grant Aerona 3 issues
First time posting so bear with me. Some bits that have...
By Adamp , 1 day ago
-
RE: Mitsu PUHZ-SW120YHA + EHSC-VM20Uk - Performance
All understood. Obviously its a bit house de...
By JamesPa , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
@majordennisbloodnok This may be a better thread to ...
By Batpred , 2 days ago
-
RE: Best Heat Pump Brand in the UK
Last Call to Vote & Win! Haven't voted for your Hea...
By Mars , 3 days ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
Interesting question. To be frank, since I have no inte...
By Majordennisbloodnok , 3 days ago
-
RE: New Fogstar 15.5kWh upright solution
The video shows the JK balancer, but the connection of ...
By Batpred , 3 days ago
-
RE: Ecodan unable to hit legionella target temp - what's the consensus?
@9jwr9 Hi, yes this is the issue with every (stand alon...
By ASHP-BOBBA , 3 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk FWIW I managed unintentionally to 'coax' mine in...
By JamesPa , 3 days ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
You are in essence right. Adia only works with selecte...
By JamesPa , 3 days ago
-
No, you haven’t missed out, @batpred. This thread’ll st...
By Majordennisbloodnok , 3 days ago