Hi. Apologies for the long post...

I've had a Samsung heat pump fitted which has been running since September last year. Because the property was unoccupied, while I was renovating, I've had it almost permanently on 'outing' mode. Despite this and the cold weather it's always seemed warm in the house (especially compared to my draughty house with a gas boiler) which is great, in theory.

But, I have tenants moving in next weekend so I set it to run normally and every time I go there it feels, in my opinion, uncomfortably hot. For example last weekend it was 15° outside and according to the controller the indoor temperature was 24°. I think the indoor target temp is supposed to be 18°, but the radiators are still getting heat. If this was a gas system I would be assuming there was a problem with a diverter valve. 

I turned the radiator thermostats down, rhe bedroom ones off and turned the temperature adjustment on the pump down the maximum of -5.

But it still seems too warm in the house.

The property is (now) very well insulated and I don't think it's using too much electricity, but even efficiently gained heat is wasted if you have to open windows to get rid of it. 

My knowledge of how these systems work is very limited and I've found the user manual next to useless, so don't know if there's any way I can adjust anything. I tried to set schedules so it's at least not running in the day, but there only seems to be a daily opinion for hot water. I can't find an option for programming the heating and the weekly and yearly options are 'greyed' out anyway. 

I'd be grateful for any guidance. 

Thanks in advance. 

Neil

This topic was modified 1 day ago by Mars

   
Quote
bontwoody
(@bontwoody)
Noble Member Contributor
5330 kWhs
Joined: 3 years ago
Posts: 786
 

@pooneil Hi. It’s a nice problem to have 😁. Do you know if the system is running using weather compensation?  It’s called water law by Samsung

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote
(@pooneil)
Eminent Member Member
130 kWhs
Joined: 3 days ago
Posts: 14
Topic starter  

Posted by: @bontwoody

@pooneil Hi. It’s a nice problem to have 😁. Do you know if the system is running using weather compensation?  It’s called water law by Samsung

Hi. I did wonder if complaining it was working too well on 1st April might look like a joke 😃 

Yes, I believe it is using weather compensation... at least I recall seeing 'water law', but had no idea what that referred to. Again, user information seems deliberately vauge and confusing. 

While I was working there today I turned a couple of the downstairs rad stats right down -- I was in a t-shirt with all the windows open -- and got a E911 error. A flow issue apparently. This happened before, just after the system was first turned on, because the installer had forgotten to open all the check valves. 

This is my concern, with tenants moving in, that they will be fussing with it for comfort and worrying about bills and I'll be forever having to deal with resetting it.

 


   
ReplyQuote
(@pooneil)
Eminent Member Member
130 kWhs
Joined: 3 days ago
Posts: 14
Topic starter  

Generation and consumption for January, mainly on Outing Mode was:

Generation 790.5 kWh

Consumption 192.8 kWh

Does that sound about right for a 90 sqm 3 bed house?


   
ReplyQuote
(@jamespa)
Illustrious Member Moderator
11847 kWhs
contributor
Joined: 2 years ago
Posts: 2242
 

Posted by: @pooneil

Posted by: @bontwoody

@pooneil Hi. It’s a nice problem to have 😁. Do you know if the system is running using weather compensation?  It’s called water law by Samsung

Hi. I did wonder if complaining it was working too well on 1st April might look like a joke 😃 

Yes, I believe it is using weather compensation... at least I recall seeing 'water law', but had no idea what that referred to. Again, user information seems deliberately vauge and confusing. 

While I was working there today I turned a couple of the downstairs rad stats right down -- I was in a t-shirt with all the windows open -- and got a E911 error. A flow issue apparently. This happened before, just after the system was first turned on, because the installer had forgotten to open all the check valves. 

This is my concern, with tenants moving in, that they will be fussing with it for comfort and worrying about bills and I'll be forever having to deal with resetting it.

 

With tenants I'd be tempted to remove the trv heads, set it up to run on water law only, adjust the water law and leave.  (Otherwise you will likely get 911 errors when they turn down the trvs.). Which is anyway a good way to run a heat pump.

That said you seem to be getting a good cop (energy produced/energy consumed) with it running part time which is encouraging.

This post was modified 1 day ago 2 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
bontwoody
(@bontwoody)
Noble Member Contributor
5330 kWhs
Joined: 3 years ago
Posts: 786
 

OK, so the low flow error could well be because you are closing radiators stats down, I think. Its certainly not the way to control your heat pump.

If weather compensation is active then you need to reduce the two set point temperatures. this is in the installer menus.

Firstly though do some reading to understand how weather compensation works. Basically you set two flow temperatures for two outside air temperatures. For example when its minus 2C outside your flow temperature might be 45C and when its 15C outside your flow temperature might be 35C. Between these two outside temperatures the controller interpolates to find the correct flow temperature.

Once you get this right you really wont need to use radiator stats at all, but there is a bit of trial and error.

Ill have a look for some links to help you.

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote



bontwoody
(@bontwoody)
Noble Member Contributor
5330 kWhs
Joined: 3 years ago
Posts: 786
 

@pooneil This is how to alter the water law settings

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote
(@judith)
Prominent Member Member
2737 kWhs
Joined: 1 year ago
Posts: 320
 

@pooneil Hi and welcome.

I have to say you are thinking like a gas boiler and heat pumps don’t work well being treated that way. It’s best that you sort it before you have tenants and then you can guide them. There’s a document called ABC of heat pumps on this site and you should start by reading that.

The controls you write about are suitable for a gas system and possibly the pump settings may be too. You need to set the TRVs to fully open, the room thermostats to above what anyone might want, say 24C. Then the pump has always got water flowing and not show flow errors.

Then you need to balance the radiators using the lock-shield valves to give an even heat throughout the house. There’s a guide to that too in this forum.

The radiators should NEVER be hot, ours are barely warm so your plumber may have used set flow temperatures limits more appropriate for a gas boiler.

The away mode on our Vaillant uses about half the electricity than normal to keep the temperature about 3C less than normal.

Other Samsung users will best guide you on detailed settings but the principles are the same for all.

The pump may be too big for the house now that you have improved the insulation. 
Well done for insulating the house well and putting in a pump. At the present 15C it will barely need to run at all but you must keep the water flow up and all the radiators open.

Where has the control been mounted? Hopefully inside the house in a normally used room?

 

2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC


   
ReplyQuote
(@potatoman)
Estimable Member Member
592 kWhs
Joined: 12 months ago
Posts: 53
 

@pooneil   I too have a heat pump in a house which is rented out, this was a nightmare as every tenant wanted a different temperature regime to suit their needs, a constant cause of trouble. To overcome this I installed a Homely, which meant the tenants, or you could easily alter the temperature requirements remotely via an app which can be on everybody's phone, with an added advantage that the Homely is easy to use with time-of-use tariff.


   
ReplyQuote
(@pooneil)
Eminent Member Member
130 kWhs
Joined: 3 days ago
Posts: 14
Topic starter  

JamesPa
The flow error issue is almost certainly from shutting the TVRs off. I'll see if I can get it balanced and comfortable before thinking about taking them off.

bontwoody
Thanks for the video link. I've adjusted it to what he advised for a well insulated house. I'll check tomorrow to see if it makes any difference.

Judith
I'm definitely still in the gas boiler mindset, it's all I know. Living in a draughty house where we can't afford to have the heating over 18°, I'm not used to a constant 25° 😃
Opening all the bedroom TRVs reduced the downstair radiator temperatures, which makes sense as the heat is distributed over a larger area, but it didn't noticeably increase the bedrooms as I'd expect with gas. Again, the mindset of operating gas heating at 70°.

Potatoman
That's interesting to know. I'll investigate the Homely. The only controller is in the cupboard attached to the water tank. I asked the installer about a roomstat and he advised I didn't need one, especially with tenants, because they would more likely be turning it up, down, on and off which was not the best way to run a heat pump. He advised using the +5 and -5 and the Outing setting on the controller if needed. This made sense, assuming it's ticking over correctly 

Thanks again everyone. 


   
👍
1
ReplyQuote
(@jamespa)
Illustrious Member Moderator
11847 kWhs
contributor
Joined: 2 years ago
Posts: 2242
 

Posted by: @potatoman

@pooneil   I too have a heat pump in a house which is rented out, this was a nightmare as every tenant wanted a different temperature regime to suit their needs, a constant cause of trouble. To overcome this I installed a Homely, which meant the tenants, or you could easily alter the temperature requirements remotely via an app which can be on everybody's phone, with an added advantage that the Homely is easy to use with time-of-use tariff.

This is where the control philosophy adopted by Vaillant (and some others, mainly European) wins.  They give you a 'room temperature' adjustment, but behind the scenes it actually adjusts the flow temperature by moving the WC curve up or down.  This works even if you disable 'room influence' entirely so you are operating open loop on pure WC.

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@guthrie)
Estimable Member Member
772 kWhs
Joined: 1 year ago
Posts: 71
 

You have had good advice so far, but I am just wondering what your thermostat is?  What unit is telling the heat pump the desired temperature or when to come on? 

 

I ask because if the installers have a third party thermostat controlling when the pump comes on etc, then that might cause problems. 


   
ReplyQuote



Page 1 / 4
Share:

Join Us!

Trusted Installers

Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.

✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available

👉 Find your installer now!

Latest Posts

Most Active This Week

# Name kWhs
1 Mars 355
2 JamesPa 150
3 Pooneil 113
4 Majordennisbloodnok 112
5 Toodles 108
6 bontwoody 101
7 Heatgeek 98
8 Transparent 87
9 cathodeRay 81
10 Tim441 65
x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security