Posted by: @ashp-bobba@old_scientist 35 DegC outdoor air temperature?
Yes, that's the default value, but can be set between 10C to 35C.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
@old_scientist I see, thats good, so set for a couple Deg above design and you have an over heat stop point. I am sure most manufacturers have something like this somewhere in the vast control settings.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Mitsubishi Ecodan just runs the same flow temp when it reaches the limit of the set curve.
I am not aware of any way of telling the heat pump not to run above a certain outside temp.
Mitsubishi Ecodan just runs the same flow temp when it reaches the limit of the set curve.
I am not aware of any way of telling the heat pump not to run above a certain outside temp.
On a podcast a few months ago, one of the panelists mentioned that most heat pumps (and possibly boilers with outdoor sensors) are designed to stop running when the CIBSE outdoor temperature threshold is reached. I don’t remember the exact number offhand, but I think it was a very specific 15.5C.
I haven’t come across specific documentation confirming whether Mitsubishi Ecodan follows this principle, but it might be worth checking the service menu or installation manual to see if there’s a parameter for a high outdoor temperature cut-off.
In our case, I’ve not seen this setting anywhere, but I’ll check again today. That’s the reason we just turn ours off manually to prevent heating if, for example, the temp drops to 14.5C for a period of time.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @garyMitsubishi Ecodan just runs the same flow temp when it reaches the limit of the set curve.
I am not aware of any way of telling the heat pump not to run above a certain outside temp.
See my post https://renewableheatinghub.co.uk/forums/postid/44973 - it's called summer mode and is in the service menu.
Posted by: @editor
Mitsubishi Ecodan just runs the same flow temp when it reaches the limit of the set curve.
I am not aware of any way of telling the heat pump not to run above a certain outside temp.
On a podcast a few months ago, one of the panelists mentioned that most heat pumps (and possibly boilers with outdoor sensors) are designed to stop running when the CIBSE outdoor temperature threshold is reached. I don’t remember the exact number offhand, but I think it was a very specific 15.5C.
I haven’t come across specific documentation confirming whether Mitsubishi Ecodan follows this principle, but it might be worth checking the service menu or installation manual to see if there’s a parameter for a high outdoor temperature cut-off.
In our case, I’ve not seen this setting anywhere, but I’ll check again today. That’s the reason we just turn ours off manually to prevent heating if, for example, the temp drops to 14.5C for a period of time.
My Vaillant definitely has a 'Max outside temp for heating' parameter.
What it doesn't have, unfortunately, is a 'Max solar irradiance for heating' parameter. For much of this week its been quite chilly outside. Solar gain has dominated during the day, but then in the evening the house starts cooling. So really I need to turn off the heating during the daytime, and put it back on evening and night. I could set up a timed program to do this I suppose!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa use expanded mode! It’s ideal for that, and I’ve just moved back to it.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
@judith Thanks, Ill give it a go.
Given the tight hysteresis do you turn up the target temperature a bit to ensure it switches back on early enough in the evening?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Vailant arotherm+ has a setting to turn off heating when OT is above the set point. 16°c by default
-
Warm weather and heat pumps.
5 months ago
-
Savings - using Weather Compensation & Time of Use Tariffs
7 months ago
-
Daikin Octopus installation update - I saw my first defrost. 😍😂
8 months ago
-
LG Therma V. Software upgrades, AI (weather compensation), SCOP
2 years ago
-
LG Therma V R32 Monobloc. Setup advice inc flow temperature & weather compensation
2 years ago
Currently viewing this topic 1 guest.
- 26 Forums
- 2,177 Topics
- 47.9 K Posts
- 36 Online
- 5,748 Members
Podcast Picks
Latest Posts
-
Updated Data on Dimplex Edal 270L ASHP Hot water tank 1 year full data. Scottish Highlands
I replaced my oil burning boiler that did hot water and...
By Bob@Lochinver , 22 minutes ago
-
RE: Repiping and Reconfiguring our Heat Pump System Including Removing the Buffer Tank
@adamk &@editor I think these FRVs come into their ...
By Judith , 2 hours ago
-
RE: Which temperature sensor for a Steibel buffer and Ecodan?
@ashp-bobba many thanks for the information. I have f...
By downfield , 2 hours ago
-
@judith Applied for replacement from installer. If...
By cliffhanger , 3 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
The real answer is trial and error, because there are a...
By cathodeRay , 4 hours ago
-
@drei Id be wary of the reference in quote 1 to reattac...
By benson , 19 hours ago
-
RE: Renewable Heating Hub WhatsApp Channel
I clicked on the link and have WhatsApp on the computer...
By dgclimatecontrol , 19 hours ago
-
RE: Say hello and introduce yourself
Thanks for the warm welcome @editor and can't wait to b...
By Pirate Rich , 22 hours ago
-
RE: Powerwall 3 or Myenergi or something else?
Let's also bear in mind that Fogstar supply more than o...
By Majordennisbloodnok , 1 day ago
-
RE: How to choose Towel Rails for an ASHP
@judith Yes I agree. They are extremely expensive. ...
By GrahamF , 1 day ago
-
Riello NXHM Monobloc Air Source Heat Pump
Hi, does anyone have any feedback on Riello NXHM Monobl...
By dgarvey , 2 days ago
-
RE: How to Zone with a Single Room with UFH
We have exactly what you describe, one utility room wit...
By Judith , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
@agentgeorge Come the Ist of October, the Cosy cheapest...
By Toodles , 2 days ago
-
RE: Boxt Heat Pump Installation Experience
@ashfp Mine does have a buffer tank. That was my experi...
By Andrew J H , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
I'm sure you are right, I was just trying to understand...
By JamesPa , 3 days ago
-
RE: Preparing for 2nd winter in new build house.
Yuch! So that's basically just an on/off control. I...
By Transparent , 4 days ago
-
Good day everyone. I'm new here and have a few question...
By Edin67 , 4 days ago
-
RE: MCS certificate SCOP vs real-world performance
That may be contributing to lower than expected SCOP. ...
By JamesPa , 5 days ago
-