Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Vaillant flow rates, Delta T, buffer sizing - trying to get ASHP running well but hit a brick wall.
Posted by: @iancalderbank@squonk run the system in DHW mode and with your thermometers, see if the water going through the diverter valve, on what should be the Hot input to the DHW tank, is actually the hot ?
that tells you more about where the crossed pipe is.
That’s a good thought, I’ll need to work out how it should be, will try that when I’m next off work.
Posted by: @squonk@iancalderbank I assume it does have glycol … but I also assumed the guy knew what he was doing, and look where that got me! There are numerous other problems with the install, so I have asked a proper company to quote for a complete re-install, I think that’s the only way I’ll know it’s done right.
yes. hanging on till the summer for a reinstall sounds like the right option. Although make sure you understand exactly what company #2 are going to do as well, you don't want to be in the same boat twice! heacol on this forum and his company seem to be acknowledged masters of fixing other peoples badly done ASHP installs so you could try them.
couple of things you mentioned much earlier in the thread - lower flow rate than ideal. components like the diverter valve and magnetic filters can have a very significant negative effect on the flow rate if they are the wrong spec. The size of the input pipe doesn' mean anything. what matters is the pressure loss. Worth you checking out exactly what those parts are in your current setup, and make sure they are replaced with properly specced ones if needed.
also if you're going for re-installing would suggest you give serious thought to going for a single loop with volumiser rather than two loops with buffer. There's an article by heacol that explains this way better than I can. On the articles section of this forum, here
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank Thanks, that's an interesting article. My installation matches Option 1 (the least efficient one) so there is clearly scope for improvement. When I spoke to Vaillant they stated that the buffer tank is in fact a volumiser. I must admit I'm a little sketchy on the difference, might have to read the article again! The reason they gave for having it was that the heat pump needs a minimum circulating volume of 150l to work efficiently, and for the defrost cycle to work. I did some rough calculations and I reckon we've got about 85l in the floor and 45l in the buffer, so still a bit low by that measure. The Vaillant design documents also specify that weather compensation should be off for the system layout which I have, although I've never found a satisfactory explanation for that one.
Posted by: @squonk@iancalderbank Thanks, that's an interesting article. My installation matches Option 1 (the least efficient one) so there is clearly scope for improvement. When I spoke to Vaillant they stated that the buffer tank is in fact a volumiser. I must admit I'm a little sketchy on the difference, might have to read the article again! The reason they gave for having it was that the heat pump needs a minimum circulating volume of 150l to work efficiently, and for the defrost cycle to work. I did some rough calculations and I reckon we've got about 85l in the floor and 45l in the buffer, so still a bit low by that measure. The Vaillant design documents also specify that weather compensation should be off for the system layout which I have, although I've never found a satisfactory explanation for that one.
The volumiser, as the name implies adds volume to the system, and if my understanding is correct would normally be placed in the return pipework to the heat pump. It has one input, normally at the top, and one output at the bottom, so it contains warm water at the same temperature as the return water to the heat pump. This store of heat energy can therefore be used during any defrost cycle.
A buffer tank has at least four connections, a flow in near the top from the heat pump, a flow out near the top to the heat emitters, the return water from the heat emitters flows in at the bottom section of the buffer tank, with the final connections being the return water flowing out, near the bottom of the tank, to the heat pump. Unless the pipes are connected correctly and the flow rates are balanced, there may be mixing of the flow and return within the tank, which can seriously affect overall efficiency.
Posted by: @squonk@iancalderbank Thanks, that's an interesting article. My installation matches Option 1 (the least efficient one) so there is clearly scope for improvement. When I spoke to Vaillant they stated that the buffer tank is in fact a volumiser. I must admit I'm a little sketchy on the difference, might have to read the article again! The reason they gave for having it was that the heat pump needs a minimum circulating volume of 150l to work efficiently, and for the defrost cycle to work. I did some rough calculations and I reckon we've got about 85l in the floor and 45l in the buffer, so still a bit low by that measure. The Vaillant design documents also specify that weather compensation should be off for the system layout which I have, although I've never found a satisfactory explanation for that one.
your system as built has a minimum circulating volume of 45L. i.e. just the buffer. so that must be the min vol needed by vaillant. In your system its entirely possible for the secondary to be all off, and the buffer is the only thing in play. in fact thats why this system design was arrived at (plenty of other manufacturers have the exact same) - the ashp-to-buffer loop by itself is designed to satisfy the min volume and min flow rate, so that the ASHP doesn't cut out due to low flow, or struggle to defrost, regardless of how bad or good the min volume and min flow rate are on the buffer-to-emitters loop. but now people are realising that the mixing in the buffer is a heavy tax to pay on efficiency so are designing it without the buffer - but in doing so you have to be aware of the volume flow rate needs of the heat pump.
A buffer tank used as volumiser only has 2 pipes, one in one out. Logically speaking it makes one section of pipework very very fat and thats all. your buffer, whilst its adding volume, is not "a volumiser" in the classic sense, as it has 4 pipes: 2 in 2 out (one pair of which we know is the wrong way round).
pages 2 and 3 of this schematic from midsummer wholesale for samsung(yes I know you have a vaillant, but the basics are the same) are a pretty good simplified view of a 2 loop "buffer system" (page2) versus a 1 loop volumiser system (page 3).
given that you need to get a professional in anyway, I'd really recommend you speak to heacol's company as they should be able to sort all of it for you. message heacol on this forum or contact via https://ultimaterenewables.com/
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @iancalderbankA buffer tank used as volumiser only has 2 pipes, one in one out. Logically speaking it makes one section of pipework very very fat and thats all. your buffer, whilst its adding volume, is not "a volumiser" in the classic sense, as it has 4 pipes: 2 in 2 out (one pair of which we know is the wrong way round).
Apologies for late arrival to this thread.
Accepting the obvious and hidden problems with this installation… Is it fare to say it may be easier to put right than first thought? For a knowledgable person?
Forgiving the reverse piping and illogical header flow, couldn’t the “fat pipe” header be re-piped with just 2 connections providing a warm volumized tank with deliberate mixing occurring to balance the return temps? Just capping off the other two connectors.
The position of this tank on the primary return (as suggested above) makes sense as it means there is a reservoir of warm water closest to the heat pump ready to defrost the heat pump when required.
see sketch
Obviously it’s not that simple regarding the existing underfloor zones or secondary pumps (if there are any added complications) but I don’t think that’s been discussed in detail as yet.
one other thought I had was the spacing of the underfloor pipes since 100mm is now being recommended and if the spacing is wider this may also add to the under-performing heating. Although, since the system hasn’t worked properly yet this might not be an issue at all, but worth mentioning as a precautionary check.
@sunandair yes . your diagram is exactly what we are suggesting to the OP should be their target state - to be reached when a decent period of system downtime is possible. All quite do-able. They want to get a "knowledgeable person" in to do it for them, which is fair enough.
I don't know about the UFH spacing, not qualified.
I also suggested a quick-fix interim approach of the outdoor pipe swap to get them out of the current "wrong flow" situation with the 4 pipe buffer - but given that the crossed pipe maybe between the diverter and the buffer, rather than between the ASHP and the diverter (to be confirmed by thermometer testing around the diverter that the OP is yet to have time to do) , that may not be of any value.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 265 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Hush mode now released. I've not tried it yet. Should b...
By swwils , 50 minutes ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 58 minutes ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 13 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 15 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 15 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 18 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 24 hours ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 24 hours ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago