Using ECODAN with Hive stat
Hi looking for help. I have an ECODAN and am using the Hive stat. The HP is set for temp compensation etc but I know the Hive is just a dumb on/off switch. The ECODAN ought to be able to modulate but is off more than it is on and I suspect this is down to the dumb Hive which was designed for gas boilers after all. Ought I swap the Hive for Mitsubishi’s own stat or ramp up the Hive to say 30 so it’s calling for heat all of the time and then lower the flow temp to achieve balance and get the house temp that way? My installer says it’s fine with Hive as a dumb switch but I can’t get my head around that
you can do either of those options. Using the Hive is less efficient than using the Mitsubishi controller. This is because the controller can actually modulate the pump. The Hive is just, as you say, on and off. You can make it more efficient, but you cant ever match the pump controller for what it can do.
I am in the process of having my Nest removed for this exact reason.
Posted by: @broosterHi looking for help. I have an ECODAN and am using the Hive stat. The HP is set for temp compensation etc but I know the Hive is just a dumb on/off switch. The ECODAN ought to be able to modulate but is off more than it is on and I suspect this is down to the dumb Hive which was designed for gas boilers after all. Ought I swap the Hive for Mitsubishi’s own stat or ramp up the Hive to say 30 so it’s calling for heat all of the time and then lower the flow temp to achieve balance and get the house temp that way? My installer says it’s fine with Hive as a dumb switch but I can’t get my head around that
Hi Brooster,
Welcome to the forum. Batalto is perfectly correct that a thermostat is not the ideal method of controlling an ASHP.
The Mitsubishi Controller actually contains a temperature sensor, but needs to be located in the room whose temperature you are trying to control. If the controller is not in the correct location then you could try the following.
Set your Hive 1C or 2C above the desired indoor temperature. Ensure that your heat pump is set for Weather Compensation, and adjust the curve to say 25C Water Flow Temperature at an outdoor temperature of 20C and 45C Water Flow Temperature at an outdoor temperature of -5C.
Monitor your system over a period of time and see how it performs. Make small adjustments to the curve if you deem it necessary.
Your installer is an idiot…
turn the hive all the way up and forget about. Or have it removed altogether.
if you’ve got an ecodan then it makes sense to use the Mitsubishi room sensor/controller.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Posted by: @broosterOught I swap the Hive for Mitsubishi’s own stat or ramp up the Hive to say 30 so it’s calling for heat all of the time and then lower the flow temp to achieve balance and get the house temp that way?
Do you have a Mitsubishi controller too? If so, then there's not really any drawback to adjusting the weather compensation curve until you reach balance.
The Hive may just be intended as a safeguard against overheating if the curve isn't quite correct or the Mitsubishi controller goes crazy after a firmware update (which I have seen happen once). It seems a bit like expensive overkill for a safeguard, though.
Posted by: @derek-mIf the controller is not in the correct location then you could try the following.
If the controller is not in the correct location and is a recent version, it is possible to get another sensor and connect it. Not cheap, though.
Posted by: @hughfYour installer is an idiot…
turn the hive all the way up and forget about. Or have it removed altogether.
if you’ve got an ecodan then it makes sense to use the Mitsubishi room sensor/controller.
Exactly what I had to do. Installer put in a Heatmiser stat. Since replaced with proper Mitsubishi sensor/controller. All is good since the change.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
@morgan to be fair I had no idea on installation and already had the Hive. Installer asked and I said keep the Hive having no understanding of the differences and thinking it would run like a gas boiler! Looks like between all the comments Hive has to go…
@mjr I only have the onboard controller on the hwc but it is in the garage so without something (Hive) there is no way for the ASHP to know what is going on in the house. However from all the comments it looks like (as I suspected) Hive goes and Mitsu’s own wireless stat replaces it to talk to the onboard controller on the HWC
Posted by: @brooster@morgan to be fair I had no idea on installation and already had the Hive. Installer asked and I said keep the Hive having no understanding of the differences and thinking it would run like a gas boiler! Looks like between all the comments Hive has to go…
My installer, although I was insisting on full Mitsubishi control components, suggested his hands were tied due to supply issues. Now that is partly true as I had to source and buy the required parts myself and there was a delay. I say partly due because he actually specced Heatmiser in the initial quote. Once I had possession I called him back post commission and he replaced the components for me. It was clear however that he wasn't familiar with them as he was on the phone to Mitsubishi tech support being talked through the install. Basically I think it's just easier for installers to go with a dumb on/off stat as it makes life simpler for them.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
@morgan indeed I suspect you’re right. As I understand it to remove the hive and install the Mitsubishi stat there’s a couple of dip switches need changing one to remove a third party stat and others to install the Mitsu stat; probably not for the faint hearted as a diy project…
The Ecodan actually works quite well with 3rd party room stats and weather compensation. Once you've got your compensation curve about right, use the room stats to stop the house overheating, i.e. set them 1-2 degrees above your target (as others have said). This will switch the ASHP off and let the house cool a bit if it gets too hot. You can also use the rooms stats for setback using their timers. The only slight issue with this is if you have a well balanced compensation curve it takes a while for your house to heat up after a set back. But you can tinker with the timings and it works quite well. It's often said that the ASHP will use a lot of power to heat up from cold. It doesn't really if you're using external stats because the ASHP doesn't 'know' how cold the house is. It only has to heat up the flow temperature and that doesn't take very long.
Weather compensation on its own is also good but unfortunately you can't adjust the offset automatically on a timer; it needs to be done manually.
If you use the Mitsubishi room temp setting mode and controller, the controller does 'know' how cold the house is and, depending on the settings, it will try and achieve the target room temperature by boosting the flow above the weather compensation set point. This could be less efficient
I've just bought a Mitsubishi wireless controller. I've got lots of data on energy use with weather compensation (with and without room stats) from my MMSP so once I've got the Mitsubishi controller set up I'll do some logging and comparison and work out which one is best. 🙂
@kev-m that’s kind of what my installer says but I only have TRVs in each room and from other research I’ve done the advice seems to be to leave them on max and don’t create cold spots as that makes the pump work harder as the emitting area is artificially reduced leaving the pump to work harder to push out the same heat through a smaller available area? TRVs are clearly not as sophisticated as individual stats in each room. That said three rooms face due South and when/if the sun shines they can easily get to 23 with solar gain which kind of throws everything out of whack anyway…
-
Mitsubishi Ecodan 11kw Defrosting Issue.
1 week ago
-
Ecodan consuming 100kwh per day in new build!!!
2 months ago
-
Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
5 months ago
-
Ecodan 11.2kw Wireless thermostat drop outs
5 months ago
-
Mitsubishi Ecodan System Pressure Changes - An Issue or Expected ?
6 months ago
- 26 Forums
- 2,171 Topics
- 47.8 K Posts
- 26 Online
- 5,744 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa if I remember the insulation has a notch cut i...
By AdamK , 3 hours ago
-
RE: Big Changes Coming to Our Heat Pump System
Me too, but still some people look at me as if I'm mad....
By JamesPa , 4 hours ago
-
RE: MCS certificate SCOP vs real-world performance
That may be contributing to lower than expected SCOP. ...
By JamesPa , 5 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
This is the sort of thing I mean. I've added the T1S va...
By benson , 5 hours ago
-
-
RE: Mitsu PAR-WT60R Wireless Controller - options
How it does it's job is something of a mystery although...
By Abernyte , 11 hours ago
-
RE: Powerwall 3 or Myenergi or something else?
Yes I was thinking of outdoor, IP65 batteries with buil...
By Temperature_Gradient , 16 hours ago
-
@jamespa Thanks. Yeah any adjustments Ive made at pr...
By cliffhanger , 19 hours ago
-
RE: How to choose Towel Rails for an ASHP
@rob-nezard yes absolutely. Here is the link and a pho...
By GrahamF , 2 days ago
-
@mixergy Thanks for the update, I would appreciate some...
By bontwoody , 2 days ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
Unfortunately I'm not that well connected 😂 ...
By Scalextrix , 3 days ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
It is interesting to see what our new Grant Aerona 290 ...
By GrahamF , 3 days ago
-
RE: Midea ASHP – how to set weather compensation
I noticed that too and thought the same thing, but then...
By cathodeRay , 3 days ago
-
RE: Ya can’t win! It is S*d’s Law!
@old_scientist If IOF is still running next late spring...
By Toodles , 3 days ago
-
RE: Electricity price predictions
Those of you on Agile will do well tomorrow; there are ...
By Toodles , 3 days ago
-
RE: Who’s Caved and Switched the Heating On Already?
We've been running our Ecodan system, installed in June...
By Sheriff Fatman , 4 days ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 4 days ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 4 days ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 4 days ago