British Gas versus Octopus: Two possible heat pump routes - how to evaluate them?
@johnmo
If you compared to a 45 design at -7 you are taking a 20% increase in heating costs, if you are forced to flow at 55. @ivanopinion
The object of the exercise for me is to negotiate my way around the 50º design temp through the back door, so to speak. Despite still seeing other 🐙 customers getting 45º design temps my lot won't (or I suspect, can't) budge.
So..... I've been attempting to negotiate slightly bigger radiators to give me a wee bit more room for manoeuvre after the install is done and dusted - I'm hoping for no more than 40º flow temps, preferably less.
I'm shoe-string productions right now - I can't afford to buy new rads. My install team aren't daft, they know perfectly well what I'm doing and so far have played along.
But the -1.3 thing is just an expression of my irritation with a) tick boxes of any sort; b) unreal tick boxes that bear no relation to the reality of the location. 🤷🏻♀️
I disagree it is unlikely. It all depends. 15% is the difference between 5.8kw and 6.7kw, so maybe a 7kw machine would be OK for both levels of heat loss and a 6kw would be too low for both. But 15% is also the difference between 6.5kw and 7.5kw, so a 7kw machine might be OK for one but for the other you'd need the next size up. Which would be overpowered for the vast majority of the year.The jump in heat demand from -1.3 to -7 is about 15% so unlikely to make the next sized heat pump a requirement.Posted by: @Anonymous
If you compared to a 45 design at -7 you are taking a 20% increase in heating costs, if you are forced to flow at 55.Posted by: @Anonymous
For a handful of days per year.
@lucia This technique worked for me; the installers were, as they all seem to be, designing for 50 degrees and I requested and had fitted radiators that provide our very comfortable 22.5 degrees around the whole house and 25/26 degrees in the bathroom at ~35-45 degrees LWT when the temperature is minus 2 or 3 degrees. We are very pleased that I percy veered on this and although our installers were possibly not the best ever team who have worked in our house but at least, they demonstrated a degree of ‘flexibility’ for our installation. I suspect that they would normally treat their average customer as less well informed and remarked to me that they rarely came across customers who knew just what they wanted! Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Sounds like Outfox the Octopus. 😊 . Which is my plan when/if they give me a proposal.
Daikin 6Kw ASHP.
MG4 EV
1926 Semi with loft and wall cavity insulation, all radiator.
@ivanopinion you must of spent ages come up with some vague numbers like that. You didn't even allow for DHW heating
@lucia I got my Octopus contract wohoo! Guess the design temp? yup 50 C. However I am generally pleased at first sight but will be checking over the weekend to try to see how it would be at 45 C . I think the ground floor is OK but I may upgrade some bedroom rads myself. The odd one is they want to change my recently fitted 600 by 600 K2 with one of a lower output. So I'll either let them do it and keep the one they remove or keep the new one.
Daikin 6Kw ASHP.
MG4 EV
1926 Semi with loft and wall cavity insulation, all radiator.
Posted by: @luciaThey want to change a rad for lower output? No way, that's nuts.
Problem best dealt with onsite imho. The onsite plumber will almost certainly be happy to leave you the new rad and knock off an hour early.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@lucia the surveyor did mention the Kraken software glitch which he said he would correct. However there will be two other rads in that room and the difference is small. Still a free rad I can use elsewhere. The referral sounds good but sure where I enter it? I am getting a free service to compensate for the long delay.
Daikin 6Kw ASHP.
MG4 EV
1926 Semi with loft and wall cavity insulation, all radiator.
Posted by: @jancold@lucia the surveyor did mention the Kraken software glitch which he said he would correct. However there will be two other rads in that room and the difference is small. Still a free rad I can use elsewhere. The referral sounds good but sure where I enter it? I am getting a free service to compensate for the long delay.
What Kraken software glitch? 🙈
If you can do your own rad changes there's no worry - me, I've yet to attempt any plumbing at that level, kitchen tap changes are the extent of my expertise. 😁
As for the the referral - you could add it when you sign your contract I guess? They add them to your energy account I believe - so you could use it for the service contract I guess? Or energy bills? Or maybe it won't work - but here: Octopus referral code: 4593442
My installation starts in a week - give thanks, I'm done with boiling saucepans for hot water and no heat. 🥶
@lucia Thanks for the referral I'll put it in my mail to Brad before signing the contract.
Stu , my surveyor said Kraken sometimes replaces radiators with ones of less output which has to be manually corrected, either he forgot or the monster overruled.
Boiling saucepans, no fun! hopefully our boiler will go on till the installation date.
Daikin 6Kw ASHP.
MG4 EV
1926 Semi with loft and wall cavity insulation, all radiator.
-
Vaillant arotherm plus heat pump frost protection
5 months ago
-
Daikin Octopus installation update - I saw my first defrost. 😍😂
5 months ago
-
Daikin Error Code 7H05
8 months ago
-
Vaillant aroTHERM plus not level or flat - what base is best under an external unit?
8 months ago
-
Vaillant Arotherm monobloc error f.788 - ASHP is not working!
8 months ago
- 26 Forums
- 2,104 Topics
- 46.3 K Posts
- 30 Online
- 3,393 Members
Join Us!
Latest Posts
-
@pie_eater I have been thinking of adding cooling to my...
By TechnoGeek , 5 hours ago
-
RE: BUS Grant: removal of all other fossil fuel heat sources
Hi all, thanks for your help. The installer has confirm...
By Rikiarn , 22 hours ago
-
RE: No-code, plug-and-play monitoring for your heat pump
Just in case anyone is looking at Planet Atmo- we've ma...
By benson , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
Agree, but you may have a hard time convincing them, as...
By JamesPa , 1 day ago
-
RE: Seal the Deal: Don't Let Your Heat Pump Leak Energy
Hi - fyi - there's a dead image link in the 'Optimal In...
By seatonian , 2 days ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
@chandykris Horses and beggars…. 😉 Toodles.
By Toodles , 2 days ago
-
RE: Cleaning up after gas meter removed
@agentgeorge Likewise in the loft space; we have 300mm ...
By Toodles , 2 days ago
-
RE: Ecodan consuming 100kwh per day in new build!!!
This particular example is one of the worst I have seen...
By JamesPa , 2 days ago
-
-
RE: Fan running in hot weather ...why?
I wonder if it has some kind of pressure transducer to ...
By ASHP-BOBBA , 3 days ago
-
RE: Cooling with Samsung Gen6 and Flow error
@iaack The system isnt running long enough for any cond...
By EcoBaker , 3 days ago
-
@heacol thanks for confirming we can only hope NAPIT ag...
By Bart , 3 days ago
-
Sorry to hear that @bruce. Sadly I’ve heard from multip...
By Mars , 5 days ago
-
RE: Crystal Ball Time: Communal or even Area Energy Storage?
I am invested in a couple of listed energy storage fund...
By Old_Scientist , 5 days ago
-
RE: Who's your electricity provider and what's your tariff?
That would be my biggest commitment -time to gain great...
By SUNandAIR , 5 days ago
-
RE: Who has a V2G EV installation
As has been discussed on other threads, trying to justi...
By Majordennisbloodnok , 6 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
Thanks @mikeh. Then I will also go back to non smart ta...
By ChandyKris , 6 days ago