@netdonkey Usually, this chamber will collect a thin black film of very fine particles and unlikely to impede the flow to any degree, however, having said that, it wouldn’t harm to clean it out but make sure you isolate by closing the valves on either side of the ‘magna clean’ chamber first! Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@netdonkey definitely give that a clean, following what toodles said, and tell us if it helped.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@netdonkey Do you feel confident to check the filter, you should be able to isolate the valve ether side and normally open a drain on the bottom of the filter to confirm the pressure is gone, then you can unscrew the lid to clean it out, be aware some of these filters are fitted with a magnet and a spring inside, this will need to be assembled back as it was after cleaning.
The code for the fault is low water flow so best to investigate if it is restricted or air locked.
Do you know what the water pressure is in the system?
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@ashp-bobba reasonably confident to have a look at it. The current system pressure is 1.7bar which from googling seems ok.
@netdonkey agreed, sounds ok pressure.
Quick question I just thought of, can you take a picture of the flow sensor assuming the engineers fitted it to the return pipe to the condenser, I remember Samsung explaining to me that this sensor only works in 2 orientations and that there are restrictions, for example (and I am tying to remember a year ago now) it must be flow up and have something like 100mm before the sensor and 300mm after before any fittings to prevent turbulence or air bubbles and prevent it from miss reading, or horizontal with similar restrictions.
Just trying to rule a few things out.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@netdonkey Ok, that looks correct to me and a nice amount of pipework above the sensor.
Does the system fail on flow when heating the water as well or is it just when on heating? Are you able to check what the flow rate is when on hot water?
Let me know how you get on cleaning the in line filter.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@ashp-bobba It trips on both but more frequently with DHW. Re the flow rate when ion DHW, I think its the same FSV but will have a look
@netdonkey Ok. Can you give me the model and serial of the cylinder so I can work out the ports, I cant quite see the badge and different manufacturers use different ways for the bottom mounted buffers which this look like, I am not sure if I am placing the flows the correct way round.
Pink is ASHP flow
Blue is ASHP return
Red Buffer F/R
Orange DHW F/R
Green Circle (assumed heating pump and connections)
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Oh great!
We now have someone else here who can doodle on top of photos 😀
Can I please check @ashp-bobba that my arrow is pointing to the flow sensor which you've been discussing with @netdonkey ?
And I've turned on the light in the cupboard so we can more easily see the black component parts in the gloom.
Net Donkey - you might want to ask Santa for some pipe lagging with a wide bore to insulate around those brass valves.
Any pipes and metalwork within 1-mtr of the cylinder will be sucking heat out of it...
... even the pressure-relief valve and down-pipe on the right, which doesn't have water in it.
BES sell a good range of Kaiflex Class-O insulation with bores up to 54mm.
Glue the slit-sides back together with Impact Adhesive.... the sort you leave to dry on each half before pressing them together.
Save energy... recycle electrons!
@transparent Hello, yes thats correct or at least it appears to look like it, this is the flow sensor that needs to be on the return pipe back to the ASHP condenser and is the little 5 wired bit of magic that causes all them errors when there is a lack of flow 🙂
I thought adding arrows to the picture may help as I was trying to work out which part of the circuit was doing what, something was not looking quite correct but I didnt want to work it out until I can see the cylinder diagram and confirmed the location identity of all ports on that multi port cylinder.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
-
First time wall mounting an ASHP
4 months ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
4 months ago
-
Samsung problems
6 months ago
-
Sudden drop in COP
7 months ago
-
Samsung's Cold Shoulder: Should Heat Pump Manufacturers Be More Accountable?
2 years ago
- 27 Forums
- 2,520 Topics
- 58.6 K Posts
- 578 Online
- 6,800 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
Yes, here's mine. From the service manual parts numbers...
By bobflux , 5 minutes ago
-
Had to learn the hard way 🤣 now I'm sharing T...
By bobflux , 20 minutes ago
-
RE: Issue with a Grant Air Source Heat Pump & Tado Smart Thermostat
Im assuming from your original post that hysterisis ref...
By JamesPa , 1 hour ago
-
RE: Heat Pump vs New Gas Boiler for Inherited House - Worth the Extra Cost?
Hi @fretless6 Mike, I have experience with Taggas (Re...
By Old_Scientist , 3 hours ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@bobflux With my limited HA skills I can't ad...
By Ubert767 , 5 hours ago
-
RE: Underfloor Heating Installation Issues with Heat Pump
I'm going to install Thermacome ACOSI+ radiant ceiling....
By bobflux , 7 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Now seems a good time to summarise the costs and effici...
By benson , 8 hours ago
-
RE: Tell us about your Solar (PV) setup
@mk4 Charge to 100%, discharge down to 10%.
By bobflux , 9 hours ago
-
RE: Connecting Growatt SPH5000 over wired ethernet rather than wireless
The simplest wired option is usually the Growatt Ethern...
By Jonatan , 15 hours ago
-
RE: Electricity price predictions
@jamespa And it seems some of the nasty public cloud...
By Batpred , 22 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
Technology is rapidly advancing. BBC News reported th...
By Transparent , 1 day ago
-
RE: Do Fridges and Freezers have COP ratings?
@editor Thank you all for your replies and submitted in...
By Toodles , 1 day ago
-
I know and yes. The secondary deltaT wont necessaril...
By JamesPa , 1 day ago
-
RE: Designing heating system with air to water heat pump in France, near Lyon
Just love the way you put it! 🤣
By Batpred , 2 days ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thank you for sharing. So it seems that your Schneid...
By Batpred , 2 days ago
-
RE: Forum updates, announcements & issues
@upnorthandpersonal thanks for the thoughtful, consider...
By Mars , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@mk4 All 21 panels have their own Enphase IQ7a microinv...
By Toodles , 2 days ago
-
RE: Setback savings - fact or fiction?
Great, so you have proven that MELCloud is consistently...
By RobS , 3 days ago
-
RE: Mitsu PUHZ120Y 'Outdoor Temp 'error?
Thanks David & James It almos...
By DavidAlgarve , 3 days ago
-
RE: Surge protection devices SPDs
@trebor12345 - your original Topic about the right type...
By Transparent , 3 days ago
-
RE: Help needed with Samsung AE120RXYDEG
@tomf I’ve been sent this from a service engineer at Sa...
By Mars , 3 days ago
-
RE: Buying large amp bidirectional RCD and RCBO
Yes... I went through this particular headache and ende...
By bobflux , 4 days ago
-
O-oh! Let's take this as an opportunity to 'pass the ...
By Transparent , 4 days ago