@netdonkey Usually, this chamber will collect a thin black film of very fine particles and unlikely to impede the flow to any degree, however, having said that, it wouldn’t harm to clean it out but make sure you isolate by closing the valves on either side of the ‘magna clean’ chamber first! Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@netdonkey definitely give that a clean, following what toodles said, and tell us if it helped.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@netdonkey Do you feel confident to check the filter, you should be able to isolate the valve ether side and normally open a drain on the bottom of the filter to confirm the pressure is gone, then you can unscrew the lid to clean it out, be aware some of these filters are fitted with a magnet and a spring inside, this will need to be assembled back as it was after cleaning.
The code for the fault is low water flow so best to investigate if it is restricted or air locked.
Do you know what the water pressure is in the system?
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@ashp-bobba reasonably confident to have a look at it. The current system pressure is 1.7bar which from googling seems ok.
@netdonkey agreed, sounds ok pressure.
Quick question I just thought of, can you take a picture of the flow sensor assuming the engineers fitted it to the return pipe to the condenser, I remember Samsung explaining to me that this sensor only works in 2 orientations and that there are restrictions, for example (and I am tying to remember a year ago now) it must be flow up and have something like 100mm before the sensor and 300mm after before any fittings to prevent turbulence or air bubbles and prevent it from miss reading, or horizontal with similar restrictions.
Just trying to rule a few things out.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@netdonkey Ok, that looks correct to me and a nice amount of pipework above the sensor.
Does the system fail on flow when heating the water as well or is it just when on heating? Are you able to check what the flow rate is when on hot water?
Let me know how you get on cleaning the in line filter.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@ashp-bobba It trips on both but more frequently with DHW. Re the flow rate when ion DHW, I think its the same FSV but will have a look
@netdonkey Ok. Can you give me the model and serial of the cylinder so I can work out the ports, I cant quite see the badge and different manufacturers use different ways for the bottom mounted buffers which this look like, I am not sure if I am placing the flows the correct way round.
Pink is ASHP flow
Blue is ASHP return
Red Buffer F/R
Orange DHW F/R
Green Circle (assumed heating pump and connections)
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Oh great!
We now have someone else here who can doodle on top of photos
Can I please check @ashp-bobba that my arrow is pointing to the flow sensor which you've been discussing with @netdonkey ?
And I've turned on the light in the cupboard so we can more easily see the black component parts in the gloom.
Net Donkey - you might want to ask Santa for some pipe lagging with a wide bore to insulate around those brass valves.
Any pipes and metalwork within 1-mtr of the cylinder will be sucking heat out of it...
... even the pressure-relief valve and down-pipe on the right, which doesn't have water in it.
BES sell a good range of Kaiflex Class-O insulation with bores up to 54mm.
Glue the slit-sides back together with Impact Adhesive.... the sort you leave to dry on each half before pressing them together.
Save energy... recycle electrons!
@transparent Hello, yes thats correct or at least it appears to look like it, this is the flow sensor that needs to be on the return pipe back to the ASHP condenser and is the little 5 wired bit of magic that causes all them errors when there is a lack of flow
I thought adding arrows to the picture may help as I was trying to work out which part of the circuit was doing what, something was not looking quite correct but I didnt want to work it out until I can see the cylinder diagram and confirmed the location identity of all ports on that multi port cylinder.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
7 months ago
-
Sudden drop in COP
1 year ago
-
Samsung's Cold Shoulder: Should Heat Pump Manufacturers Be More Accountable?
1 year ago
-
Any installer recommendations for Samsung ASHP?
1 year ago
-
Issue with Samsung A2W Heat Pump - Water Outlet Temperature
2 years ago
- 22 Forums
- 2,084 Topics
- 45.9 K Posts
- 27 Online
- 3,377 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
Verified, trusted & experienced installers
Nationwide coverage expanding
Special offers available
Latest Posts
-
RE: My misgivings about installing ASHP and solar panels via the ECO4 scheme...
@editor great article re accreditation. I note ISO/IEC ...
By Bart , 1 hour ago
-
RE: Renewables & Heat Pumps in the News
Here’s a little more technical detail/p>
By Judith , 15 hours ago
-
A good start but I’m glad I didn’t need to learn someth...
By Judith , 15 hours ago
-
RE: Who's your electricity provider and what's your tariff?
I don't (yet), but my PW3 is due to be installed shortl...
By Old_Scientist , 19 hours ago
-
RE: MCS and NAPIT complaints process
@chrislay, is your heat pump complaint still unresolved...
By Mars , 23 hours ago
-
RE: ASHP Install from hell - help please
@saf1973 I’ve been going through old cases on the forum...
By Mars , 23 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@benson I have gone down the Home Assistant and wavesha...
By Grantmethestrength , 1 day ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@aaron There's the rub, the database does not list my ...
By AF1 , 1 day ago
-
RE: Renewable Heating Hub Homeowners' Q&A Podcast
@editor excellent news, congratulations and well deserv...
By ASHP-BOBBA , 2 days ago
-
RE: Vaillant AroTherm Plus 7kW
Depends on the flow temperature; the Czech data sheet i...
By JamesPa , 2 days ago
-
RE: Commencing on an ASHP Installation Process
Yes, it's "doable" if everything goes to plan, they arr...
By Old_Scientist , 3 days ago
-
RE: How not to install a heat pump
You are right. Thinking on this has evolved over the p...
By JamesPa , 3 days ago
-
RE: DHW SET UP with Samsung gen 5
Thats good news indeed, you are very likely almost ther...
By JamesPa , 4 days ago
-
RE: Plate heat exchanger considerations
As far as I can tell my vented system would have a peak...
By Scalextrix , 4 days ago
-
RE: Air Changes per Hour - ACH and the MCS requirement
There have been a few discussions dotted around (e.g. I...
By Declan90 , 4 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Having made some enquiries locally I have found a compa...
By Morgan , 4 days ago