@netdonkey Usually, this chamber will collect a thin black film of very fine particles and unlikely to impede the flow to any degree, however, having said that, it wouldn’t harm to clean it out but make sure you isolate by closing the valves on either side of the ‘magna clean’ chamber first! Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@netdonkey definitely give that a clean, following what toodles said, and tell us if it helped.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@netdonkey Do you feel confident to check the filter, you should be able to isolate the valve ether side and normally open a drain on the bottom of the filter to confirm the pressure is gone, then you can unscrew the lid to clean it out, be aware some of these filters are fitted with a magnet and a spring inside, this will need to be assembled back as it was after cleaning.
The code for the fault is low water flow so best to investigate if it is restricted or air locked.
Do you know what the water pressure is in the system?
@ashp-bobba reasonably confident to have a look at it. The current system pressure is 1.7bar which from googling seems ok.
@netdonkey agreed, sounds ok pressure.
Quick question I just thought of, can you take a picture of the flow sensor assuming the engineers fitted it to the return pipe to the condenser, I remember Samsung explaining to me that this sensor only works in 2 orientations and that there are restrictions, for example (and I am tying to remember a year ago now) it must be flow up and have something like 100mm before the sensor and 300mm after before any fittings to prevent turbulence or air bubbles and prevent it from miss reading, or horizontal with similar restrictions.
Just trying to rule a few things out.
@netdonkey Ok, that looks correct to me and a nice amount of pipework above the sensor.
Does the system fail on flow when heating the water as well or is it just when on heating? Are you able to check what the flow rate is when on hot water?
Let me know how you get on cleaning the in line filter.
@ashp-bobba It trips on both but more frequently with DHW. Re the flow rate when ion DHW, I think its the same FSV but will have a look
@netdonkey Ok. Can you give me the model and serial of the cylinder so I can work out the ports, I cant quite see the badge and different manufacturers use different ways for the bottom mounted buffers which this look like, I am not sure if I am placing the flows the correct way round.
Pink is ASHP flow
Blue is ASHP return
Red Buffer F/R
Orange DHW F/R
Green Circle (assumed heating pump and connections)
Oh great!
We now have someone else here who can doodle on top of photos 😀
Can I please check @ashp-bobba that my arrow is pointing to the flow sensor which you've been discussing with @netdonkey ?
And I've turned on the light in the cupboard so we can more easily see the black component parts in the gloom.
Net Donkey - you might want to ask Santa for some pipe lagging with a wide bore to insulate around those brass valves.
Any pipes and metalwork within 1-mtr of the cylinder will be sucking heat out of it...
... even the pressure-relief valve and down-pipe on the right, which doesn't have water in it.
BES sell a good range of Kaiflex Class-O insulation with bores up to 54mm.
Glue the slit-sides back together with Impact Adhesive.... the sort you leave to dry on each half before pressing them together.
Save energy... recycle electrons!
@transparent Hello, yes thats correct or at least it appears to look like it, this is the flow sensor that needs to be on the return pipe back to the ASHP condenser and is the little 5 wired bit of magic that causes all them errors when there is a lack of flow 🙂
I thought adding arrows to the picture may help as I was trying to work out which part of the circuit was doing what, something was not looking quite correct but I didnt want to work it out until I can see the cylinder diagram and confirmed the location identity of all ports on that multi port cylinder.
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
2 months ago
-
Sudden drop in COP
7 months ago
-
Samsung's Cold Shoulder: Should Heat Pump Manufacturers Be More Accountable?
9 months ago
-
Any installer recommendations for Samsung ASHP?
11 months ago
-
Issue with Samsung A2W Heat Pump - Water Outlet Temperature
2 years ago
- 21 Forums
- 1,814 Topics
- 39.1 K Posts
- 15 Online
- 2,130 Members
Join Us!
Latest Posts
-
RE: Can you work an ASHP too hard?
As someone with an over-sized HP and the lower level of...
By HarriUp , 3 hours ago
-
RE: Best temperature wave form for best economy and efficiency .
I find the graphs somewhat hard to reconcile against th...
By HarriUp , 4 hours ago
-
RE: ASHP and how it should run and potential kw consumption?
You can help things by putting the DHW on to a timed op...
By Judith , 5 hours ago
-
RE: Vaillant Arotherm ASHP gets noisier when it gets colder outside
Quite possibly. As I mentioned above the 'ideal' produ...
By JamesPa , 5 hours ago
-
RE: Is it crucial to get flow temperatures with heat pumps right?
The bodies of TRVs usually have an arrow on them. If i...
By JamesPa , 6 hours ago
-
RE: Say hello and introduce yourself
Thank you Transparent ...much appreciated 😊 ...
By ivanhoew , 7 hours ago
-
RE: ASHP for small garage and workshop
@transparent Hello. This will not be covered on any gra...
By BobTSkutter , 8 hours ago
-
RE: Adding data centre electricity costs to domestic energy bills?
Greg Jackson in the Times again just yesterday promotin...
By IanMK13 , 9 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
Yeah we have a 40l buffer too. Problem is the App doesn...
By MikeH , 10 hours ago
-
Hi, has anybody got a step-by-step installation guide t...
By Potatoman , 13 hours ago
-
RE: Mitsubishi Ecodan 8.5kW Monobloc (FTC5) Defrost Mode
@gary no set backs. Yes see others in various forums ha...
By AlsoCold123456 , 13 hours ago
-
Looking for homeowner to join our podcast as a guest
We’re looking for a homeowner to join us on the Homeown...
By Mars , 18 hours ago
-
Our system is open no hydraulic separation. The volume ...
By Judith , 19 hours ago
-
RE: Mitsubishi Ecodan ASHP general set-up and efficiency
@gary Morning, yes, both of these are set to 3 on physi...
By ngillam , 19 hours ago
-
If the insulation isn’t wet you can over-cover it. It’s...
By Judith , 1 day ago
-
RE: Is My Midea Heat Pump Inherently Defective?
Sadly I think you are right, until someone develops a c...
By JamesPa , 1 day ago
-
RE: How much radiator capacity do I need for an air source heat pump?
Follow-up: it occurs to me that the difference between ...
By Simonwhiteley , 1 day ago
-
RE: The Definitive Guide to Weather Compensation and Curves for Air Source Heat Pumps
@judith thanks…. Every day a school day. tomorrows le...
By SUNandAIR , 1 day ago
-
RE: The good, the bad and the not that great – my heat pump installation
at the bottom of our installers invoice it said we were...
By NetDonkey , 2 days ago
Latest Topics
-
By Potatoman 13 hours ago
-
By DavidAlgarve 1 day ago
-
ASHP for small garage and workshop
By BobTSkutter 1 day ago
-
By ChandyKris 3 days ago
-
Nibe heatpump comms error when freezing
By Toody 3 days ago
-
Is this normal behaviour for my samsung ashp
By wawyed 4 days ago
-
Can you work an ASHP too hard?
By Simonwhiteley 5 days ago
-
By IRMartini 5 days ago
Members Online
No online members at the moment