Samsung E911 intermittent issue
Posted by: @netdonkey@editor it’s one of their agents. They did say the name of the company but can’t remember it!
just remembered the name! https://atlasservicessolutions.co.uk/
Just a quick update. It looks like it may be the actual Samsung is broken. Whether it's been caused by the 16 litres of glycol the installer put in for our 12 radiator system or not is still to be seen. Waiting for Samsung to open tomorrow to get them to come out
Just an update to let everyone know that we are now all back up and running after 2 weeks of no heat in the coldest January in a while.
We finally had the installed agree to drain the system and flush everything through. When he was disconnecting the ASHP from the outside flow and return he removed some lagging beside the shut off valves and spotted something he hadn't noticed before. The shut off valves also had filters in them
Opened them up and they were caked. Cleaned them out and did another flush for good measure and we are back with heating!
Thanks for everyones input into this!!
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
7 months ago
-
Sudden drop in COP
1 year ago
-
Samsung's Cold Shoulder: Should Heat Pump Manufacturers Be More Accountable?
1 year ago
-
Any installer recommendations for Samsung ASHP?
1 year ago
-
Issue with Samsung A2W Heat Pump - Water Outlet Temperature
3 years ago
- 22 Forums
- 2,087 Topics
- 46 K Posts
- 11 Online
- 3,379 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
-
RE: Commencing on an ASHP Installation Process
And on the second day, we have a completed installation...
By Sheriff Fatman , 3 hours ago
-
RE: Mitsubishi Ecodan Fails to Heat Water despite temperature drop
Its the flow temperature for the heating circuit, it me...
By Gary , 4 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
@dowallydrifter OK. I would recommend you read t...
By JamesPa , 5 hours ago
-
When will heat pumps and install prices come down?
I am currently thinking about having a heat pump instal...
By EGP01 , 8 hours ago
-
RE: Solar to power Heat Pump for DHW
Wow, how big is your heat pump that it is pulling 6kW d...
By Old_Scientist , 10 hours ago
-
Adding battery storage to SolarEdge PV system
Hi, I think I've narrowed down my choice to a Sunsynk 5...
By nazuro1041 , 17 hours ago
-
There are DHW tanks with a built in heat pump that take...
By JamesPa , 1 day ago
-
RE: Vaillant AroTherm Plus 7kW
If the thermostat is connected to the call for heat ter...
By JamesPa , 1 day ago
-
Hi all - I'm diving into the world of ASHPs and I am tr...
By abam48 , 2 days ago
-
RE: Renewables & Heat Pumps in the News
Yes I realise I'm picking this up a week late...... but...
By Transparent , 3 days ago
-
@editor Mars if you have any recommendations for down s...
By abam48 , 3 days ago
-
RE: Surface mount or bury primaries for heat pump installation?
@tomasmcguinness HI, The rules is a best practise, the ...
By ASHP-BOBBA , 3 days ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@cathoderay how did you get a script to run for that- d...
By benson , 3 days ago
-
RE: Renewable Heating Hub Homeowners' Q&A Podcast
@ashp-bobba thank you, and equally so, thank you for ta...
By Mars , 5 days ago
-
@judith good to know… I’ll continue to feed Wattson, an...
By Mars , 5 days ago
-
RE: My misgivings about installing ASHP and solar panels via the ECO4 scheme...
@editor great article re accreditation. I note ISO/IEC ...
By Bart , 6 days ago