Samsung E911 intermittent issue
Hi all,
Been having a trawl through the forums for the E911 and have a few other queries.
I have a AE080CXYDEK which was installed back in June and has been working well. Recently, however, we have had a couple of E911 errors which has led me to dig into our install a bit more.
Using our MIM i can see the flow is around 7.2-7.4lpm which is almost at the HP's minimum in which the E911 error starts. I have queried our installer (electrician who installed the solar and battery and subsequently subbed the ASHP install out) and it's taking a while to get anywhere. So my queries are as follows:
We have a Evosta 3 set to fixed curve regulation mode level3. Is this correct?
It looks like the Evosta has been installed upside down but I assume it was done this way due to the flow direct?
I can stop it from erroring by only running the heating and within 15 mins of powering on the DHW it trips (subsequently in the last 12hrs I have had both running and it hasn't tripped). Does this narrow down what the issue could be?
In another thread, Mars mentioned checking the Y strainer. Is this easy to do as a novice or should I be pushing to get the plumber to come out and check. If it's easy where is it usually located and what does it look like?
How happy are other plumbers to come out and diagnose a system they havent put it and is it worth doing this?
Thanks!
@netdonkey The model number for your Samsung indicates it is an 8kW system? The flow rates you are indicating only provide around 2.5kW and the code E911 is related to lack of flow, airlocks, restrictions on flow or other flow sensor issues.
Samsung send an inline strainer with their systems, if this was fitted it will collect debris from the system and block (this is its job) this will need checking 1st, also its worth confirming the length of the primary pipework from the condenser to the plant room (from the condenser to the manifold or plant room, buffer or 1st secondary distribution pipework valves). It worth making sure this pipework is the correct size for the flow rate and distance it serving. 8Kw will need a minimum of 28mm on a short run.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@ashp-bobba Thanks. The pipework run from the ASHP to main plant is around 13m. Would the strainer be near the pump or the main plant? I assume the strain would be on the return to protect the pump?
@netdonkey The strainer can be anywhere on the rerun line from the airing cupboard / plant room to the ASHP condenser, so this could be in that room or at the condenser, they look like a Y shape: linked here for you to see.
Please clarify 2 things if you can?
13m from the condenser to the plant room as the main ASHP pipes
What size is the pipework from the condenser (most manufacturers need you to limit the run to a max 10M or calculate an upsize in pipework and pump to cope with the length of run).
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Posted by: @netdonkeyWould the strainer be near the pump or the main plant?
On our system, originally, it was inside the heat pump unit (we don’t have a Samsung). It was a bloody stupid location because we had to remove heat pump side panels to access it, so we had the installers move it into our plant room. See photo.
I asked installers specifically about Y strainers on a recent podcast and they should be fitted on every installation, so you should have one somewhere.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@netdonkey Should be shut of valves either side. the nut can be a bit tight on some of them, be sure to support the pipe when you try.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@netdonkey do exactly what @ashp-bobba says above.
Cleaning it is really easy once you've popped the nut off. It's got a little gauze filter/mesh inside. Give that a rinse under a tap, but before you do, check to see how many corrosive bits are in there as a reference.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@editor Can't see anything that resembles a Y filter. There does seem to be a big black fillter (pic attached) which might be a filter?
Before and after the Evosta3 circulation pump there are valves. Is it worth making sure those are fully open?
The heat pump has just came on, the pipes near the water tank start to get a bit warmer and then the HP goes off again so sounds like it might be cycling?
@netdonkey The filter in the first photo looks saucespiciously like a ‘MagnaClean’ type filter; as the flow passes through this, the larger volume of the chamber reduces speed of flow and allows a magnet to attract and retain any particles of ferrous material that passes through the pipework. This chamber is normally cleaned out during any servicing work. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
-
First time wall mounting an ASHP
2 months ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
3 months ago
-
Samsung problems
4 months ago
-
Sudden drop in COP
5 months ago
-
Samsung's Cold Shoulder: Should Heat Pump Manufacturers Be More Accountable?
2 years ago
- 26 Forums
- 2,406 Topics
- 54.6 K Posts
- 380 Online
- 6,092 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Speedcomfort radiator fans
Good idea, @deltona. I'll have a look around.
By Majordennisbloodnok , 19 minutes ago
-
RE: GSHP WOES! Midland based engineer recommendations?
@johnbroome, I've just connected you with a highly reco...
By Mars , 24 minutes ago
-
RE: Considering MLCP (Multi-Layer Composite Pipe) for ASHP
I agree, I wouldn't and I didn't. That doesn't however...
By JamesPa , 28 minutes ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
On closer observation, I had missed that the latest EIC...
By Batpred , 28 minutes ago
-
RE: Post-Traumatic Heat Pump Stress Disorder
@jamespa, we have got this topic, which all the mods ca...
By Mars , 2 hours ago
-
RE: Sunsynk Whole House Backup Issue
Hi @lostandconfused - you're in luck.And you're quite r...
By Transparent , 2 hours ago
-
Things have gone quiet with you @drei. Any updates?
By Mars , 3 hours ago
-
RE: Passiv Smart Thermostat - Help & Forum Support
Thanks @tim441. Interesting timing, as Passiv are a cur...
By Mars , 4 hours ago
-
Hi everyone, I have a two year old Marlec Solar iBoos...
By Tallmarc , 7 hours ago
-
RE: Please help with the settings ecodan
Are you trying to address any particular performance is...
By Sheriff Fatman , 13 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
🤣 Well, I never managed to get the HA solis "...
By Batpred , 14 hours ago
-
RE: Experience - New Build / Complete New Heating System
Your sap clculations should give you a heat loss figure...
By JohnnyB , 14 hours ago
-
RE: Vaillant aroTherm not heating with many faults
@editor hmmm, our engineers Rae, Craig, Naz, Rob and Ry...
By ASHP-BOBBA , 15 hours ago
-
RE: I’m glad the cold spell is over!
@editor as a reply for this date the 6th of Jan in o...
By Nursethescreens , 17 hours ago
-
RE: Heat loss based on gas usage
@jamespa Thanks. The numbers posted above were jus...
By Bash , 17 hours ago
-
RE: Heat pump not reaching flow temperature
I would describe this as either a fault or a configurat...
By JamesPa , 18 hours ago
-
RE: New Daikin 11kW Altherma 3M install - is it working as it should?
I forgot to mention: Octopus measured our heat loss at ...
By Toodles , 21 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: @davec Manufacturer: Peak Energy Mode...
By DaveC , 21 hours ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
Well, the guy came out, turned the heat pump to max, we...
By razz , 21 hours ago