Samsung E911 intermittent issue
Hi all,
Been having a trawl through the forums for the E911 and have a few other queries.
I have a AE080CXYDEK which was installed back in June and has been working well. Recently, however, we have had a couple of E911 errors which has led me to dig into our install a bit more.
Using our MIM i can see the flow is around 7.2-7.4lpm which is almost at the HP's minimum in which the E911 error starts. I have queried our installer (electrician who installed the solar and battery and subsequently subbed the ASHP install out) and it's taking a while to get anywhere. So my queries are as follows:
We have a Evosta 3 set to fixed curve regulation mode level3. Is this correct?
It looks like the Evosta has been installed upside down but I assume it was done this way due to the flow direct?
I can stop it from erroring by only running the heating and within 15 mins of powering on the DHW it trips (subsequently in the last 12hrs I have had both running and it hasn't tripped). Does this narrow down what the issue could be?
In another thread, Mars mentioned checking the Y strainer. Is this easy to do as a novice or should I be pushing to get the plumber to come out and check. If it's easy where is it usually located and what does it look like?
How happy are other plumbers to come out and diagnose a system they havent put it and is it worth doing this?
Thanks!
@netdonkey The model number for your Samsung indicates it is an 8kW system? The flow rates you are indicating only provide around 2.5kW and the code E911 is related to lack of flow, airlocks, restrictions on flow or other flow sensor issues.
Samsung send an inline strainer with their systems, if this was fitted it will collect debris from the system and block (this is its job) this will need checking 1st, also its worth confirming the length of the primary pipework from the condenser to the plant room (from the condenser to the manifold or plant room, buffer or 1st secondary distribution pipework valves). It worth making sure this pipework is the correct size for the flow rate and distance it serving. 8Kw will need a minimum of 28mm on a short run.
@ashp-bobba Thanks. The pipework run from the ASHP to main plant is around 13m. Would the strainer be near the pump or the main plant? I assume the strain would be on the return to protect the pump?
@netdonkey The strainer can be anywhere on the rerun line from the airing cupboard / plant room to the ASHP condenser, so this could be in that room or at the condenser, they look like a Y shape: linked here for you to see.
Please clarify 2 things if you can?
13m from the condenser to the plant room as the main ASHP pipes
What size is the pipework from the condenser (most manufacturers need you to limit the run to a max 10M or calculate an upsize in pipework and pump to cope with the length of run).
Posted by: @netdonkeyWould the strainer be near the pump or the main plant?
On our system, originally, it was inside the heat pump unit (we don’t have a Samsung). It was a bloody stupid location because we had to remove heat pump side panels to access it, so we had the installers move it into our plant room. See photo.
I asked installers specifically about Y strainers on a recent podcast and they should be fitted on every installation, so you should have one somewhere.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@netdonkey Should be shut of valves either side. the nut can be a bit tight on some of them, be sure to support the pipe when you try.
@netdonkey do exactly what @ashp-bobba says above.
Cleaning it is really easy once you've popped the nut off. It's got a little gauze filter/mesh inside. Give that a rinse under a tap, but before you do, check to see how many corrosive bits are in there as a reference.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor Can't see anything that resembles a Y filter. There does seem to be a big black fillter (pic attached) which might be a filter?
Before and after the Evosta3 circulation pump there are valves. Is it worth making sure those are fully open?
The heat pump has just came on, the pipes near the water tank start to get a bit warmer and then the HP goes off again so sounds like it might be cycling?
@netdonkey The filter in the first photo looks saucespiciously like a ‘MagnaClean’ type filter; as the flow passes through this, the larger volume of the chamber reduces speed of flow and allows a magnet to attract and retain any particles of ferrous material that passes through the pipework. This chamber is normally cleaned out during any servicing work. Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
5 months ago
-
Sudden drop in COP
10 months ago
-
Samsung's Cold Shoulder: Should Heat Pump Manufacturers Be More Accountable?
1 year ago
-
Any installer recommendations for Samsung ASHP?
1 year ago
-
Issue with Samsung A2W Heat Pump - Water Outlet Temperature
2 years ago
- 22 Forums
- 2,034 Topics
- 44.3 K Posts
- 59 Online
- 3,237 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: The Great British Heat Pump Quiz
@editor I thought it was great, I was more focused on w...
By ASHP-BOBBA , 1 minute ago
-
RE: Career change – entering the world of heating and heat pumps
Most people here (including me) arent in the industry, ...
By JamesPa , 16 minutes ago
-
RE: Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
@cbrenewable Can you look on the side of the pump body,...
By ASHP-BOBBA , 20 minutes ago
-
Height above ground level matters only when you're cons...
By Transparent , 52 minutes ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
I am drawing the same conclusion that this system for s...
By trebor12345 , 2 hours ago
-
RE: help sizing rads based on room by room heat loss
@jamespa heat loss list on first post. it’s the one t...
By AdamK , 3 hours ago
-
RE: Agile: average import cost vs other tariffs?
@toodles thanks for the analysis. I'll be really intere...
By Old_Scientist , 14 hours ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
@phoenix15 I'm no plumber so please don't take this as ...
By dnagre , 17 hours ago
-
RE: Is this normal? Click of the DHW returning to space heating
@grantmethestrength Oh sorry to hear that, there should...
By ASHP-BOBBA , 21 hours ago
-
@ashp-bobba TBH the ladies are rather disorganised, so ...
By Cathyem1 , 21 hours ago
-
The Rise and Fall of Europe’s Most Generous Green Subsidy
This story came to my attention thanks to Graham Hendra...
By Mars , 22 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
And for those of us without an automatic irrigation sys...
By Majordennisbloodnok , 22 hours ago
-
Logically, the lower frequency = more gentle, yes, but ...
By SUNandAIR , 1 day ago
-
RE: Ideal Logic ASHP - change from 55°C to 35°C Heating?
Good point. I’ll keep my eye on the manifold temperatur...
By Tomdad , 1 day ago
-
RE: How hard and expensive would it be to change panel and add battery?
@transparent It is a setting that Octopus make via the ...
By Toodles , 1 day ago
-
RE: Performance of Heat Pumps in Mild Weather
@heatgeek The flow rate isnt controlled by Mitsub...
By RobS , 1 day ago
-
RE: Say hello and introduce yourself
I might put a couple of speakers in the ceiling if fund...
By Fingers , 2 days ago
-
RE: Bathroom Radiator replacement
@rob-nezard can you please offer your professional advi...
By Mars , 2 days ago
-