Samsung E911 intermittent issue
Hi all,
Been having a trawl through the forums for the E911 and have a few other queries.
I have a AE080CXYDEK which was installed back in June and has been working well. Recently, however, we have had a couple of E911 errors which has led me to dig into our install a bit more.
Using our MIM i can see the flow is around 7.2-7.4lpm which is almost at the HP's minimum in which the E911 error starts. I have queried our installer (electrician who installed the solar and battery and subsequently subbed the ASHP install out) and it's taking a while to get anywhere. So my queries are as follows:
We have a Evosta 3 set to fixed curve regulation mode level3. Is this correct?
It looks like the Evosta has been installed upside down but I assume it was done this way due to the flow direct?
I can stop it from erroring by only running the heating and within 15 mins of powering on the DHW it trips (subsequently in the last 12hrs I have had both running and it hasn't tripped). Does this narrow down what the issue could be?
In another thread, Mars mentioned checking the Y strainer. Is this easy to do as a novice or should I be pushing to get the plumber to come out and check. If it's easy where is it usually located and what does it look like?
How happy are other plumbers to come out and diagnose a system they havent put it and is it worth doing this?
Thanks!
@netdonkey The model number for your Samsung indicates it is an 8kW system? The flow rates you are indicating only provide around 2.5kW and the code E911 is related to lack of flow, airlocks, restrictions on flow or other flow sensor issues.
Samsung send an inline strainer with their systems, if this was fitted it will collect debris from the system and block (this is its job) this will need checking 1st, also its worth confirming the length of the primary pipework from the condenser to the plant room (from the condenser to the manifold or plant room, buffer or 1st secondary distribution pipework valves). It worth making sure this pipework is the correct size for the flow rate and distance it serving. 8Kw will need a minimum of 28mm on a short run.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@ashp-bobba Thanks. The pipework run from the ASHP to main plant is around 13m. Would the strainer be near the pump or the main plant? I assume the strain would be on the return to protect the pump?
@netdonkey The strainer can be anywhere on the rerun line from the airing cupboard / plant room to the ASHP condenser, so this could be in that room or at the condenser, they look like a Y shape: linked here for you to see.
Please clarify 2 things if you can?
13m from the condenser to the plant room as the main ASHP pipes
What size is the pipework from the condenser (most manufacturers need you to limit the run to a max 10M or calculate an upsize in pipework and pump to cope with the length of run).
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Posted by: @netdonkeyWould the strainer be near the pump or the main plant?
On our system, originally, it was inside the heat pump unit (we don’t have a Samsung). It was a bloody stupid location because we had to remove heat pump side panels to access it, so we had the installers move it into our plant room. See photo.
I asked installers specifically about Y strainers on a recent podcast and they should be fitted on every installation, so you should have one somewhere.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@netdonkey Should be shut of valves either side. the nut can be a bit tight on some of them, be sure to support the pipe when you try.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@netdonkey do exactly what @ashp-bobba says above.
Cleaning it is really easy once you've popped the nut off. It's got a little gauze filter/mesh inside. Give that a rinse under a tap, but before you do, check to see how many corrosive bits are in there as a reference.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@editor Can't see anything that resembles a Y filter. There does seem to be a big black fillter (pic attached) which might be a filter?
Before and after the Evosta3 circulation pump there are valves. Is it worth making sure those are fully open?
The heat pump has just came on, the pipes near the water tank start to get a bit warmer and then the HP goes off again so sounds like it might be cycling?
@netdonkey The filter in the first photo looks saucespiciously like a ‘MagnaClean’ type filter; as the flow passes through this, the larger volume of the chamber reduces speed of flow and allows a magnet to attract and retain any particles of ferrous material that passes through the pipework. This chamber is normally cleaned out during any servicing work. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
-
First time wall mounting an ASHP
4 months ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
4 months ago
-
Samsung problems
6 months ago
-
Sudden drop in COP
7 months ago
-
Samsung's Cold Shoulder: Should Heat Pump Manufacturers Be More Accountable?
2 years ago
- 27 Forums
- 2,520 Topics
- 58.6 K Posts
- 488 Online
- 6,800 Members
Join Us!
Worth Watching
Latest Posts
-
@grahamf It was due to the clearances, would have prefe...
By Renewables345 , 28 minutes ago
-
RE: Heat Pump vs New Gas Boiler for Inherited House - Worth the Extra Cost?
Hi @fretless6 Mike, I have experience with Taggas (Re...
By Old_Scientist , 2 hours ago
-
RE: Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
Hi @bobflux thanks for pointing out the difference in t...
By DaveC , 2 hours ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@bobflux With my limited HA skills I can't ad...
By Ubert767 , 3 hours ago
-
RE: Underfloor Heating Installation Issues with Heat Pump
I'm going to install Thermacome ACOSI+ radiant ceiling....
By bobflux , 5 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Now seems a good time to summarise the costs and effici...
By benson , 6 hours ago
-
RE: Tell us about your Solar (PV) setup
@mk4 Charge to 100%, discharge down to 10%.
By bobflux , 8 hours ago
-
RE: Connecting Growatt SPH5000 over wired ethernet rather than wireless
The simplest wired option is usually the Growatt Ethern...
By Jonatan , 13 hours ago
-
RE: Electricity price predictions
@jamespa And it seems some of the nasty public cloud...
By Batpred , 20 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
Technology is rapidly advancing. BBC News reported th...
By Transparent , 23 hours ago
-
What matters for flow and pressure drop is internal dia...
By bobflux , 24 hours ago
-
RE: Do Fridges and Freezers have COP ratings?
@editor Thank you all for your replies and submitted in...
By Toodles , 1 day ago
-
I know and yes. The secondary deltaT wont necessaril...
By JamesPa , 1 day ago
-
RE: Designing heating system with air to water heat pump in France, near Lyon
Just love the way you put it! 🤣
By Batpred , 2 days ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thank you for sharing. So it seems that your Schneid...
By Batpred , 2 days ago
-
RE: Forum updates, announcements & issues
@upnorthandpersonal thanks for the thoughtful, consider...
By Mars , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@mk4 All 21 panels have their own Enphase IQ7a microinv...
By Toodles , 2 days ago
-
RE: Setback savings - fact or fiction?
Great, so you have proven that MELCloud is consistently...
By RobS , 3 days ago
-
RE: Mitsu PUHZ120Y 'Outdoor Temp 'error?
Thanks David & James It almos...
By DavidAlgarve , 3 days ago
-
RE: Surge protection devices SPDs
@trebor12345 - your original Topic about the right type...
By Transparent , 3 days ago
-
RE: Help needed with Samsung AE120RXYDEG
@tomf I’ve been sent this from a service engineer at Sa...
By Mars , 3 days ago
-
RE: Buying large amp bidirectional RCD and RCBO
Yes... I went through this particular headache and ende...
By bobflux , 4 days ago
-
O-oh! Let's take this as an opportunity to 'pass the ...
By Transparent , 4 days ago