Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Running ASHP efficiently, general thought process. (Low and slow)
Posted by: @boycey@toodles hi, I think you may of mis understood my post, I'm happy with my temps atm, and I'm monitoring them as the oat getting nearer 0C and will tweak as needed. My post was, am I thinking right, aiming to keep the third party stats above the obtainable room temp so they are always calling for heat, ie so the loops are all open and flow temp is just right to keep rooms at, for example 20.5c or whatever the comfortable level is for any one using this thought process. If one can get the weather comp curve just right, the ufh will continually run just the right flow temp, ie low and slow.. is this the right way to try and run my heat pump.
principles are good.
regarding DT3 this may or may not be issue.
May be issue- if flow rate is high (I believe the 5kw model has a low flow rate, less than 14 LPM.) or you have a low loss header with balance issues. Or WC curve is calling for too low a temperature for the HP to keep operating at (leading to cycling)
May not be an issue- if HP is trying to minimise output (modulate) if your WCcurve is asking for a low flow temp and the heat pump can manage to run at that low output without cycling.
three questions- 1 what’s your flow rate compared to optimum in data book? 2 what’s your total emitter heat loss when running at 25c in an ambient of 20c? 3 is the answer to Q2 equal to or higher than the minimum output of the 5kw model? If the output capability is less than the min operating output then there may be short cycling.
questions easy but answers may be bit harder.
maybe try posting an hourly operation graph off MELCloud showing flow and return temps and cycling frequency.
also try moving flow temp up one degree at a time if you want to stop cycling… if that’s a problem.
When ambients are colder cycling should get less. So any problems may be less noticeable.
Also raise your room stat a bit higher incase you’re getting room stat cycling instead of output short cycling. If your WC curve is set accurately to your heat loss temperature gains in room should be very slow.
@sunandair Hi thanks for the questions, im not sure i can answer then fully though but hes what i can say.
1. i have the MCs cert and under floor flow rates from commissioning, Design flow rate 7.2L/M (7 rooms all at 1l/m each) then Actual adds up to 9.8L/M, 2 rooms at 1.5, and 2 at over 2L/M. The cert also say flow rate 45deg and SCOP of 3.65. but i can't see any where near that when i use the consumed and delivered figures on the FTC6.
my pump was set to speed 5 originally approx 14 L/M when we first moved in, ive got it down to speed 2 now =9L/M.
2, not sure where this info is
3, nor this
so ive reduced the pump to what seems a better rate i think, should i be looking at the manifold rates and adjusting them to compliment the pump flow rates now, and bring them closer to 1 for each room?
ill see if i can get the melcloud hourly graphs
That’s great @boycey
it might help to know how warm the room was at 14:00 and what was the outdoor ambient at the same time. It looks like the cycling increases once the floor has been heated for a few hours…. As though it reaches a certain saturation temperature.
your DHW cycle shows it’s keeping a steady DT OF 5c
reverting to space heating also good
interesting that 14:00 graph shows heating after the ramp up.
I think I see return water (black line) coming back a bit too warm so the line curves upwards. forcing the flow temp (LWT) to also rise- until it reaches 30c which is presumably target flow temp so it shuts down for a while
That would suggest insufficient heat is being offloaded into the floors to allow the 30c flow temp to continue, for whatever reason.
Others may have a view as to why. But it does seem to behave differently the next hour.
I think your model heat pump has a minimum output of around 1.9 to 2.4kwh depending on outdoor temperatures.
Do you know the construction of you UF heating is there poured concrete or insulation under it? Spacing of pipes? Floor coverings… These things affect the performance of the heat emitting surface.
@sunandair hi. So if the Delta T is OK when doing DHW that's good, but not so on ufh? Could this be the flow rates on manifold need adjusting, I've reduced the pump flow, not sure what the rates are on the manifold as its behind the washing machine, I'll have to pull it out whilst the system is calling for heat. Am I correct in thinking the flow rates on the manifold could be a bit high, as per the commission doc designed at 1 l/m per room but some were set up at 2 l/m? So maybe by reducing these the delta T for heating would be better?
Oat was around 4 deg at 14:00, rooms at about 20.5 deg stats at about the same or just calling
I don't know the construction, but it's 2 years old, I assume poured concrete with insulation, LVT main living area kitchen/diner/lounge and hall, tiled baths, and carpeted bedrooms. Top floor in block, south facing front and east on one side
hi @boycey I don’t have underfloor heating so can’t comment on what adjustment to the existing setup you might make. hopefully there may be others in this forum who know more about the specifics of Under Floor heating and about flow rates through the manifolds.
My thoughts are drawn, perhaps prematurely, to the carpeted areas and whether you have underlay which might prevent heat radiating. Or whether introducing towel radiators might raise the heat loss to a better level. But this may be far too early or complex to even think about doing at this stage.
So perhaps someone who has UF Heating might offer some advice on how these graph outputs appear or may be adjusted.
-
Surface mount or bury primaries for heat pump installation?
7 hours ago
-
Design Of Cascade System Replacing Undersized ASHP
1 day ago
-
Mitsubishi Ecodan not good enough ?
2 months ago
-
High air source heat pump running costs – Vaillant AroTherm Plus
2 months ago
-
Struggling to get CoP above 3 with 6 kw Ecodan ASHP
3 months ago
- 26 Forums
- 2,692 Topics
- 63.2 K Posts
- 3,336 Online
- 7,102 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Home Alone with Home Assistant (previously A Beginner's Guide to ASHP Monitoring)
Well done, @bontwoody; looks good. Before we get to t...
By Majordennisbloodnok , 12 minutes ago
-
Okay so now another stupid question, can I change the p...
By chastity_outward053@simplelogi , 26 minutes ago
-
-
If you've got long DC cables involved in the rework rem...
By EtchedPixels , 2 hours ago
-
RE: vaillant arotherm plus - Failure - DHW
Vaillant called today and have now changed the inverter...
By trebor12345 , 5 hours ago
-
RE: Surface mount or bury primaries for heat pump installation?
Quick update on this - it's been quite a long time as p...
By tomasmcguinness , 7 hours ago
-
RE: Say hello and introduce yourself
@etchedpixels Ours is a little more involved as one roo...
By Toodles , 22 hours ago
-
RE: Design Of Cascade System Replacing Undersized ASHP
@temperature_gradient thanks but my focus is just getti...
By pash44pump , 1 day ago
-
RE: Home energy storage & battery register
3 x Alpha ess smile5 inverters each with 20kwh 20kw p...
By philmore , 1 day ago
-
RE: GivEnergy inverter tripping due to over-voltage?
I think I ought to go into greater detail on what is re...
By Transparent , 1 day ago
-
RE: How do I set up Tesla Powerwall export for saving sessions since AI Takeover?
@papahuhu We might well have found that a much smaller ...
By Toodles , 2 days ago
-
RE: Summer heat is becoming the new winter cold in the UK. What are you doing about it?
Some pics of my heat solutions… Bought the shut...
By Watcher , 2 days ago
-
RE: Moving growatt axe batteries
@etchedpixels just been informed that you can’t have ba...
By David999 , 3 days ago
-
RE: Anyone have experience with Daikin Multi+ for air to air & hot water?
Maybe, just maybe, if you are prepared to leave the doo...
By JamesPa , 3 days ago