Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
New ASHP system - choices
Posted by: @harriupAll heat pumps will hit the point where their minimum output exceeds the heat being taken out by the heating circuit, not oversizing too much means that happens at a higher outside temperature. How the pumps handle the lower demand is really hard to pin down. I know my system when using the weather compensation curve worked just at its minimum power but cycled up to 6 times per hour. Switching to the room adaptive mode slowed the cycle to once per hour or so but with a more complex power consumption as it it often puts a burst of energy in before a pause. But overall this a more efficient mode - better COP. Looking at some similar systems on heatpumpmonitor, though, displays such dissimilar working patterns that it is hard to differentiate what elements are created by the way the house heating system is responding or is programmed.
In an ideal world a heat pump unit would contain two compressors, a nominal 12kW capacity heat pump having one compressor rated at 8kW and one compressor rated at 4kW. The 8kW compressor providing heating during most of the Winter period, with the 8kW plus 4kW meeting demand during particularly cold spells.
As milder weather conditions are encountered the system would changeover from the 8kW compressor to the 4kW one, thereby allowing a much lower thermal energy output without the possibility of cycling, and probably providing an increase in overall efficiency.
Unfortunately we don't yet live in an ideal world.
I believe that most, if not all, heat pumps control the stopping and starting of the compressor based upon the temperature of the LWT and RWT, such that when either of these temperatures reaches a defined limit, the compressor is started or stopped. This of course is more likely to happen during milder weather conditions.
The 'on' period and the 'off' period is therefore dependent upon the limits set within the controller and the actual temperature measurements produced by the LWT and RWT temperature sensors. One of the major determining factors affecting the frequency of cycling could be the location of the LWT and RWT sensors within the system. If the sensors are located within the outdoor unit they are likely to cool at a more rapid rate than if they were located within the home's thermal envelope, and therefore increase the cycling frequency.
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 755 Online
- 6,994 Members
Join Us!
Worth Watching
Latest Posts
-
Brown Oily Residue Blocking Air Vent and Weeping Relief Valve... Anyone Seen This?
My installation is 4 years old. After about 18 months a...
By seoras , 2 hours ago
-
RE: Renewables & Heat Pumps in the News
An article on funding for heat pumps in case anyone is ...
By Jeff , 3 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks @editor , @indevolt-uk Subject to any comments ...
By JamesPa , 11 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 11 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 15 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 15 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 16 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 17 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 19 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 19 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 1 day ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 1 day ago
-
RE: The Grid Says Yes.. Until It Doesn’t: Why Britain's Net Zero Push is Stalling at the Plug Socket
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 4 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 4 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago
-
That’s the solar up and running, I don’t think it’s the...
By David999 , 4 days ago
-
RE: Seeking ideas / information / commiseration - Pure Drive
I agree with @colinc that you can reuse some of it. A s...
By Batpred , 4 days ago