Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
New ASHP system - choices
Posted by: @harriupAll heat pumps will hit the point where their minimum output exceeds the heat being taken out by the heating circuit, not oversizing too much means that happens at a higher outside temperature. How the pumps handle the lower demand is really hard to pin down. I know my system when using the weather compensation curve worked just at its minimum power but cycled up to 6 times per hour. Switching to the room adaptive mode slowed the cycle to once per hour or so but with a more complex power consumption as it it often puts a burst of energy in before a pause. But overall this a more efficient mode - better COP. Looking at some similar systems on heatpumpmonitor, though, displays such dissimilar working patterns that it is hard to differentiate what elements are created by the way the house heating system is responding or is programmed.
In an ideal world a heat pump unit would contain two compressors, a nominal 12kW capacity heat pump having one compressor rated at 8kW and one compressor rated at 4kW. The 8kW compressor providing heating during most of the Winter period, with the 8kW plus 4kW meeting demand during particularly cold spells.
As milder weather conditions are encountered the system would changeover from the 8kW compressor to the 4kW one, thereby allowing a much lower thermal energy output without the possibility of cycling, and probably providing an increase in overall efficiency.
Unfortunately we don't yet live in an ideal world.
I believe that most, if not all, heat pumps control the stopping and starting of the compressor based upon the temperature of the LWT and RWT, such that when either of these temperatures reaches a defined limit, the compressor is started or stopped. This of course is more likely to happen during milder weather conditions.
The 'on' period and the 'off' period is therefore dependent upon the limits set within the controller and the actual temperature measurements produced by the LWT and RWT temperature sensors. One of the major determining factors affecting the frequency of cycling could be the location of the LWT and RWT sensors within the system. If the sensors are located within the outdoor unit they are likely to cool at a more rapid rate than if they were located within the home's thermal envelope, and therefore increase the cycling frequency.
- 26 Forums
- 2,676 Topics
- 62.6 K Posts
- 199 Online
- 7,090 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
Why do you want to maintain a specific deltaT? The out...
By JamesPa , 13 minutes ago
-
RE: Heat pump installation quotations
@batpred Excellent, thank you very much!
By sttpd1917 , 43 minutes ago
-
Hopefully this will answer your question. To...
By ASHP-BOBBA , 44 minutes ago
-
RE: Help me keep the faith with my air source heat pump installation
I would be interested to find out if others do this and...
By ASHP-BOBBA , 53 minutes ago
-
Harvest Thermal - ASHP with a smart thermal battery
I thought people here might find this interesting, even...
By springswood , 2 hours ago
-
Don't you dare. You just carry on as you are; as @batpr...
By Majordennisbloodnok , 3 hours ago
-
RE: Heat pump design review please: 5 kW Vaillant aroTHERM Plus heat pump
@ragtime27 some rooms in our house only have one place ...
By Judith , 3 hours ago
-
@mkz, that's very helpful. Even if Urban Plumber are no...
By Majordennisbloodnok , 6 hours ago
-
RE: Several AC coupled batteries
That is a good point, a manufacturers can stop trading,...
By Batpred , 7 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Hi @hanno - good question. The range of hybrid invert...
By Transparent , 7 hours ago
-
RE: GivEnergy inverter tripping due to over-voltage?
@transparent the inverter was installed in 2021 and afa...
By Tim441 , 7 hours ago
-
RE: Say hello and introduce yourself
I hope so, @toodles. It's not often that we see a situa...
By Majordennisbloodnok , 11 hours ago
-
RE: Electricity price predictions
Good point, I do expect the bonus of putting my energy ...
By Batpred , 1 day ago
-
RE: Daikin ESPAltherma and Home Assistant installation
@bash, something we haven't touched on already relates ...
By Majordennisbloodnok , 1 day ago