Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
@jamespa & @johnmo
What will happen to my efficiency ?
@jamesPa "Only when close to the target temperature would I expect it to invoke cycling."
You are , james , again, perfectly correct , the Oscillations , wrongly attributed to "short cycling " , only occur when the Temperature approaches the target Temperature. Outwith the Target Temperature the Thermostat just switches ON or OFF.
Your comment that "The purpose of this is to avoid overshoot" now makes sense .
I stand corrected, raising the Temperature by a significant amount will force the Thermostat out of it's close approach algorithm forcing the Heat Pump to be always ON.
What will happen to my efficiency ?
Surely , there Must be a cheap replacement Thermostat that does NOT cause " Cycling"?
A simple Thermostat controlled by variable "Hysteresis" would do me just fine!
In Greek Hysteresis translates as Madness! Time for a darkened room!
Posted by: @iantelescopeI stand corrected, raising the Temperature by a significant amount will force the Thermostat out of it's close approach algorithm forcing the Heat Pump to be always ON.
What will happen to my efficiency ?
The heat pump should always be on, that's the whole point. The weather compensation curve (water law) needs to be adjusted so that, with the heat pump always on, the house reaches the correct temperature. This is the most efficient way to run a heat pump (or a gas boiler for that matter, but in the UK we sadly ignore this capability of most gas boilers).
The only purpose of the thermostat is to switch off if there is an unusual condition such as excess solar gain (and to satisfy building regs which for some unfathomable reason specify that one must be fitted,). Other than in this unusual circumstance the thermostat should not be controlling the heat pump, that is what the heat pumps native controller is for!
This is a complete reversal of the way we have run heating systems in recent years in the UK, we need to get used to it! Other countries, notably Germany, have been running their gas boilers on weather compensation for many years, which probably makes the transition easier.
Once you get it basically working, it may make sense to heat only during the daytime at either end of the season (using the timer function of the thermostat). However you should consider this a refinement on the basic principle of 24*7 operation at the lowest possible flow temp to achieve the room temperature you want with thermostat and TRAs permanently 'on'.
Done correctly this gives better comfort for less energy!
One further thought, if you are going to replace the thermostat consider instead a homely. This is essentially a learning intelligent thermostat/timer designed specifically for heat pumps. It can interface with Samsung and reputedly delivers good results, essentially auto adapting your WC curve to suit your house. TBH in your situation I would either keep the existing thermostat or replace it with a homely. I wouldn't replace it with another thermostat unless I happened to have one kicking around.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Again , I now understand.
I should , initially, use the Samsung Water Law to allow the outdoor Temperature to control the pipe water Temperature with the Thermostat Temperature raised to such a level that it is permanently ON, and permanently out of the way.
I have extensively used the Samsung Water Law to adjust for the low winter temperatures , routinely setting the Water Law to "start" at a Water Temperature of + 45 C when the outdoor Temperature is -5 in Winter.
This Water Law -5 C ordinate with a coordinate of +45 C is recommended by Samsung for Scotland.
I still would like a Thermostat without Cycling !
Posted by: @AnonymousJust add - I don't believe your cycling is anything to do your thermostat, I believe it's a red herring.
Your current flow path of water from the heat pump is 2 port valve, buffer then HEX and back to the ASHP. The issue, which I believe is going on, is the pressure drop across the HEX is higher than the buffer. So water (or most of it) just takes a short cut and bypasses through buffer straight back to the ASHP. So your return temp goes up too quickly and the heat pump just shuts down.
I think that you are wrong, the cycling still occurs with the buffer tank isolated. Ian and I went through all this months ago.
Posted by: @iantelescopeAgain , I now understand.
I should , initially, use the Samsung Water Law to allow the outdoor Temperature to control the pipe water Temperature with the Thermostat Temperature raised to such a level that it is permanently ON, and permanently out of the way.
I have extensively used the Samsung Water Law to adjust for the low winter temperatures , routinely setting the Water Law to "start" at a Water Temperature of + 45 C when the outdoor Temperature is -5 in Winter.
This Water Law -5 C ordinate with a coordinate of +45 C is recommended by Samsung for Scotland
Exactly.
See also my comment above (following an edit so you may need to re-read) about replacing the thermostat with a homely. Imho your best options are (1) keep the existing thermostat or (2) replace the existing thermostat with a homely which is specifically designed for heat pumps.
If I were you I would do (1) intiially and then (2) only if I proved the need.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Incidentally you may be wondering how we got to a point where loads of 'controls' are available which don't actually help much and in some cases hinder. The answer is twofold
1 Some of these work better (or less badly) with gas or oil boilers than they do with heat pumps
2 In the UK we lost our way when, unlike some other countries, we shunned weather compensation for gas boilers. The consequence is that most of us have been paying probably 5-10% more than we need to for our heating since the 90s when condensing boilers were introduced, and 'enjoying' poorer comfort and requiring more user intervention in addition!
Of course the industry has responded with a variety of over-sold add on controls which go some way to correcting the initial error, but which are largely inappropriate to low temperature heating systems such as a properly adjusted condensing boiler or a heat pump.
It's a sad situation perhaps only clear with 20:20 hindsight, but is making the transition to heat pumps more difficult because it requires consumer re-education as well as plumbing.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
No Thermostat , Water Law Offset alone?
I have been pondering my current Heat Pump controlled by Weather Compensation and a Thermostat .
The Thermostat directly controls the Radiator , Secondary Water loop.
Currently, without a Thermostat I would be unable to get any heat!
After my upgrade could I permanently short out the Thermostat using the Water Law Offset Control alone ?
Essentially No Thermostat with the Heat Pump controlled by Weather compensation offset ?
Posted by: @iantelescopeNo Thermostat , Water Law Offset alone?
I have been pondering my current Heat Pump controlled by Weather Compensation and a Thermostat .
The Thermostat directly controls the Radiator , Secondary Water loop.
Currently, without a Thermostat I would be unable to get any heat!
After my upgrade could I permanently short out the Thermostat using the Water Law Offset Control alone ?
-- Attachment is not available --
Essentially No Thermostat with the Heat Pump controlled by Weather compensation offset ?
That's a valid control strategy imho and indeed how Samsung most likely intends it's equipment to be used. My earlier suggestion to set the thermostat to say 30C achieves exactly the same effect which is why I made it.
There are however a few reasons why you may want to retain the thermostat:
a. I think building regs require one (only god knows why)
b. Your thermostat has a timer function which may be more convenient to use than the Samsung one. Whilst 24*7 operation is undoubtedly the way to go initially and for the height of the heating season, I think it's a fair bet you will want to do part time heating at either of the season to minimise cycling. You may also want to do a nighttime setback (implemented by switching off) in the shoulder season and it might be useful for this.
c. If you remove it you have to cover yo wires and a hole, By leaving it in place abd simply setting the temp high you avoid this.
d. It may yet prove useful as a temperature limiter
As I say above, I would personally either retain it but set the temperature well above the desired level or swap it for a homely, but your suggestion is also valid.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Rebuild:
I have arranged with my Plumber to start the strip-down on Wed next week.
It should not be quite as difficult as I first thought.
Homely:
Nobody , including amazon has a "homely" Thermostat .
Has it been discontinued ?
Many thanks ,ian
@iantelescope Homely are still very much alive, I have been corresponding with them in the last few days:
Will take you to their site.
Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Also, Homely supply to trained installers and one such can install a Homely system for you. No doubt they can give you details of fitters in your neck of the woods. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
"Trained installers" are an extinct species in Scotland.
Many thanks Toodles for the information about homely.
Do they ONLY sell to "trained installers" ?
"Trained installers" are an extinct species in Scotland.
- 26 Forums
- 2,607 Topics
- 60.8 K Posts
- 297 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
@editor, I hear that too. I can confirm that out of ...
By ASHP-BOBBA , 7 hours ago
-
End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
As many of you know, our Global Energy Systems heat pum...
By Mars , 7 hours ago
-
@derbygraham fully agree with James, and it’d be good t...
By Mars , 8 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Finally got around to installing and setting up the Sol...
By Mars , 8 hours ago
-
Unfortunately its a function of the physics. Max heat ...
By JamesPa , 9 hours ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 9 hours ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 10 hours ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 12 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 13 hours ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 15 hours ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 17 hours ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 21 hours ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 1 day ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 2 days ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Many thanks for your, and the subsequent, answers tk qu...
By KevH , 2 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 3 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 3 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 4 days ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 4 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@optimistic-optimiser I have has a Daikin for a few yea...
By madsid , 4 days ago
-
RE: UK DIY Battery: SEPLOS 48V 200Ah x2 + Sunsynk 8K – Safe Installation for Garage Conversion
The rule of thumb is to ensure that you can isolate any...
By Transparent , 4 days ago