Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
@jamespa Thanks. Did you mean to give examples of the thermocouples?
So at the moment, I will leave things as they are and wait until the heating starts in the Autumn.
Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Mel-Pump app - Octopus Cosy Fixed
10 March 2026 - now 2 x Sigenstor 10 batteries with 8kw Inverter
Posted by: @richard24738@jamespa Thanks. Did you mean to give examples of the thermocouples?
So at the moment, I will leave things as they are and wait until the heating starts in the Autumn.
Yes, and I did (I hope). The word here above is a hyperlink to an Amazon offering.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa Thanks.
Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Mel-Pump app - Octopus Cosy Fixed
10 March 2026 - now 2 x Sigenstor 10 batteries with 8kw Inverter
Hi Richard,
Re: Temperature Measurements:
Water Meters:
Water Meters are the best method to measure the water Temperature within a pipe.
However, Water meters need accurate sensors fitted inside the water flow .
Fitting these sensors can be difficult and expensive.
Thermocouples:
Thermocouples are cheap but can only measure the Temperature of the Water pipe itself, not the Temperature of the water within.
Thermocouples are prone to drift with many ( most) meters fitted with "Offsets Controls " to offset drifting.
Thermocouples can be glued to the pipe with thermal conducting paste, messy and inflexible.
Thermocouples can be attached with commercially available bright Yellow clamps, flexible but costly .
Thermocouple Clamps are readily available on Ebay.
DS18B20 Semiconductors:
These Semiconductors offer a far more accurate , and stable Temperature Measurement when attached to the outside of the water pipe.
The DS18B20 are cheap , however, some fakes have appeared on the market of late.
Several DS18B20 's can be easily attached to one "Arduino" Microprocessor.
Where to fit Temperature Sensors:
Try to fit your sensors at the start of the Radiator water circuit not at the output of the Heat Pump itself.
Heat Pump makers routinely boast of the COP of their devices when measured at the heat Pump itself.
Your Installer will have fitted numerous Lossy buffers, Pipes et al between the Heat Pump and your house, so, try to measure the performance of the total system .........not the Heat Pump itself.
ian
Posted by: @iantelescopeWhere to fit Temperature Sensors:
Try to fit your sensors at the start of the Radiator water circuit not at the output of the Heat Pump itself.
I would say fit them where you need the measurements, which depends on what you are trying to work out! If you are trying to work out the change in flow temperature across the buffer, then fit them either side of the buffer as I suggested upthread.
@iantelescope is right that thermocouples can drift, mostly (I believe) because the temperature of the reference drifts. However with one of the dual sensors I gave the link to (a) the reference is likely to be the same for both sensors and (b) you can always swap the two round, thus checking any measurement. You are only looking for a difference in this case, not an absolute, and you aren't looking to monitor it continuously.
Posted by: @iantelescopeHeat Pump makers routinely boast of the COP of their devices when measured at the heat Pump itself.
Thats not really boosting COP of their devices, and certainly not in any deceptive way. They are quoting the performance of the device they are supplying. They aren't responsible for the rest of the system
Posted by: @iantelescopeYour Installer will have fitted numerous Lossy buffers, Pipes et al between the Heat Pump and your house, so, try to measure the performance of the total system .........not the Heat Pump itself.
Hopefully only one buffer/LLH as reported, and hopefully its within the thermal envelope. That's probably one too many than is actually necessary, but not 'numerous'. Pipes aren't really lossy if they within the thermal envelope, because the 'lost' heat is useful. Outside the thermal envelope they should be well insulated.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Hi Richard.
"Short Cycling, causes and cures"
My Heat Pump has been "Short Cycling " since installation in July 2022 resulting in ink like pipe water.
The "Short cycling" has , at least, three different causes.
I have, finally, discovered the last of the causes of "Short Cycling"
!:Short Cycling Thermostat:
My Heat Pump was, eventually, installed by my installer with an "Honeywell Home " Thermostat.
The "Honeywell Home" Thermostat has a "Cycling Rate Control " which was set to 6 cycles per hour, or, a cycle period of exactly 10 minutes.
I have set the Cycling Rate Control to 3 per hour greatly reducing , but not eliminating, short Cycling.
2: Short Cycling And Water Volume:
My Heat Pump , supplying Two Water circuits had ,already, an inadequate pipe Water Volume.
The Time taken to heat up and release heat from these water volumes resulted in further "Short Cycling".
Samsung , my Heat Pump manufacturer recommended the installation of a Buffer tank.
The buffer tank does , however, increase the system energy losses.
3: Short Cycling and System Cycle control:
My Samsung Heat Pump has a control used to extend cycle time .
The Control switches the Two water Pumps after a 7/8 minute delay.
My Heat Pump, costing to date circa 14K , cannot be economically repaired with the MCS/NIC saying that , " nothing can be now be done".
ian
Posted by: @iantelescope
My Heat Pump, costing to date circa 14K , cannot be economically repaired with the MCS/NIC saying that , " nothing can be now be done".
ian
@iantelescope Both @derek-m and I have made (very similar) suggestions as to how your installation can be improved, explained why implementing them would be expected to make a difference, and subjected those suggestions and the explanations to peer review through this forum. However you have declined to follow the advice offered. It is very unfortunate that your installation is, it seems, sub-optimal, but that doesn't mean that it cant be significantly improved. I am (and doubtless @derek-m is) very sympathetic however it remains the fact that if you change nothing, then nothing will change. MCS/NIC saying 'nothing can now be done' is doubtless a contractual not a technical response.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @iantelescope
My Heat Pump, costing to date circa 14K , cannot be economically repaired with the MCS/NIC saying that , " nothing can be now be done".
ian
@iantelescope Both @derek-m and I have made (very similar) suggestions as to how your installation can be improved, explained why implementing them would be expected to make a difference, and subjected those suggestions and the explanations to peer review through this forum. However you have declined to follow the advice offered. It is very unfortunate that your installation is, it seems, sub-optimal, but that doesn't mean that it cant be significantly improved. I am (and doubtless @derek-m is) very sympathetic however it remains the fact that if you change nothing, then nothing will change. MCS/NIC saying 'nothing can now be done' is doubtless a contractual not a technical response.
As the saying goes "You can take a horse to water, but you cannot force it to drink".
Not sure why my original thread has gone down this route.
Anyway, thanks to everyone for your comments.
Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Mel-Pump app - Octopus Cosy Fixed
10 March 2026 - now 2 x Sigenstor 10 batteries with 8kw Inverter
Posted by: @richard24738Not sure why my original thread has gone down this route.
Anyway, thanks to everyone for your comments.
My comment was not aimed at you or your situation. I was merely reminding James that he, I and others on the forum spent a great deal of time and effort trying to identify the problems with Ian's system and suggest possible solutions.
Most, if not all, of our suggestions were ignored by Ian, who even now continues to moan about his poorly performing system.
@iantelescope Sounds like you have a very similar system to mine. I too have a Honeywell Home thermostat connected to a Samsung 12Kw HT Quiet heat pump plus a backup oil boiler in a bivalent arrangement.
The thermostat controls the HP and when in backup boiler mode, controls the oil boiler. The thermostat is configured to have 3 cycles (20min each cycle) per hour due to oil boilers not liking frequent cycling, 6 cycles is for Gas.
The issue I was having was the thermostat would learn to demand heat for 80% - 90% of the cycle time but my heat pump was set to water pump option 4 (field option #2092) causing the heat pump to start up for 3mins then shutdown for 7 mins during the room thermostat demand time, looking like short cycling but I think it is suppose to be an energy saving thing. However I felt that this was not working very well with the external Honeywell thermostat although probably fine with the built in thermostat.
I have also noticed my HP is required to run for a least 8mins+ due to various eco stages to get full heat output according to the water law (weather comp) so 3 mins was killing the heat output.
I have now changed the field option #2092 to option 3 so now when the Honeywell thermostat demands heat, the circulating pumps run continuously for that period and the compressor runs until it reaches the water law (weather comp) temperature and then either slows down or stops until the circulating water cools enough for it to kick back in.
This has now enabled me to reduce my weather comp curve to 35C @ 10C OAT to 45C @ -2C OAT, the house still gets to 21C and the Honeywell thermostat is practically demanding heat for 90% of each cycle time. The heat pump seems to be a lot happier and now draws 1.4Kw instead of 1.9Kw in electricity. Since adjusting at the end of March 2024 my COP now = 4.4 up from 4.15
Hope this is of some use 🙂
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss, deltaT = 8 degrees
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
4.1Kw Solar Panel Array
34Kwh GivEnergy Stackable Battery System
Posted by: @technogeekThe thermostat controls the HP and when in backup boiler mode, controls the oil boiler. The thermostat is configured to have 3 cycles (20min each cycle) per hour due to oil boilers not liking frequent cycling, 6 cycles is for Gas
... which is essentially the problem, the HP should control the HP!
Posted by: @technogeekI have now changed the field option #2092 to option 3 so now when the Honeywell thermostat demands heat, the circulating pumps run continuously for that period and the compressor runs until it reaches the water law (weather comp) temperature and then either slows down or stops until the circulating water cools enough for it to kick back in.
This has now enabled me to reduce my weather comp curve to 35C @ 10C OAT to 45C @ -2C OAT, the house still gets to 21C and the Honeywell thermostat is practically demanding heat for 90% of each cycle time. The heat pump seems to be a lot happier and now draws 1.4Kw instead of 1.9Kw in electricity. Since adjusting at the end of March 2024 my COP now = 4.4 up from 4.15
& the bold bit solves the problem more or less. Essentially the Honeywell thermostat is doing nothing most of the time and leaving it to the HP to sort itself out.
HPs work best with minimal or no external controls, balanced emitters and the weather compensation curve adjusted so that the HP delivers heat most or all of the time at the lowest possible temperature which results in just enough energy being emitted from the rads/ufh to balance the heat loss from the house. Any departure from this will almost inevitably reduce efficiency. Some external control to mitigate unexpected or intermittent solar gain (or other sources of heat) is usually necessary, but configured as a limiter not a primary controller.
A heat pump which is primarily controlled externally (other than by something like homely which is specifically designed for heat pumps) will almost certainly be an inefficient heat pump.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 620 Online
- 6,994 Members
Join Us!
Worth Watching
Latest Posts
-
-
RE: Brown Oily Residue Blocking Air Vent and Weeping Relief Valve... Anyone Seen This?
OOch thats leaking quite a lot! it looks like...
By JamesPa , 2 minutes ago
-
RE: Indevolt Batteries UK Support & Info Thread
@indevolt-uk Keen to know more about the pricing and wh...
By ChandyKris , 14 minutes ago
-
RE: Our 10 year old Grant heat pump failed
Since my last post on this topic we've reached a conclu...
By Mike Patrick , 2 hours ago
-
RE: Renewables & Heat Pumps in the News
An article on funding for heat pumps in case anyone is ...
By Jeff , 5 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 13 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 17 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 17 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 18 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 19 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 22 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 22 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 1 day ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 1 day ago
-
RE: The Grid Says Yes.. Until It Doesn’t: Why Britain's Net Zero Push is Stalling at the Plug Socket
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 4 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 4 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago