Hoped for improveme...
Hoped for improvements not being realised on my Mitsubishi heat pump
6 Users
12 Reactions
(@davidalgarve)
@jamespa Hello James and thanks again.
The rads are connected in parallel and there are two runs of 22mm running down the sides of the house, in the ceiling of the ground floor, with short 15mm branches running up or down to radiators. Recent pipework is composite and 25mm.
Upstairs is main living area with 3 bedrooms, but we converted ground floor for master bedroom and additional sitting room/ office.
I will see what I can get from MelPump, but we have not had really cold weather this year (just very wet) and I am not sure what MelPump can provide from last year
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
Posted by: @davidalgarve
Woah - is that single run (flow and return) rather than two runs (2* flow and 2* return) in parallel and roughly how much of this is there please and where in the system?
Is that 2*2 (2* flow and 2* return) or 1*2 (flow and return?)
Depending on your answers pipework may well be a problem, workable of course once we have the data
(@davidalgarve)
@jamespa There are two 22mm flow and two 22mm returns shortly after rising from the heat pump where 25mm composite material pipework is used. I think this is the pipework coming out of the Ecodan.
I stress that this latter pipework was what was in place before the second pump was removed and when we were comfortable.
Fronius EV Charger
Kia e- Niro 64kW
OK, 2*22mm good, 1*25mm composite somewhere between pretty bad and unacceptable unless its very short with swept bends only.
Do you know roughly how long the 25mm run is, was this put in when the heat pump was fitted and what exactly does it connect at either end?  Also does it have swept bends or elbows where it turns corners?
Noted, I think the point is that your setup is marginal due TBC to the 25mm composite, so the buffer plus extra pump just got it to working, one pump alone the other side of the margin.  Lets focus for now on the pipework and see where that takes us.  My sense is we may be converging on an explanation for all or at least most of the observed phenomena.  Once we have an explanation we can move to a fix!
This post was modified 2 weeks ago 3 times by JamesPa
This post was modified 1 week ago by JamesPa
(@davidalgarve)
@jamespa Hello James. I am a little "under the weather" literally and metaphorically, so delayed response.
1 - The approximately 2m of 25mm pipework was put in originally, but modified twice, the first when DHW was added and the second when the buffer tank was changed to a return line volumiser. I now see that the pipe between the Ecodan and the 3 way valve is 32mm 9not 25mm) and has two elbows. More on this later.
2 - I am much closer to the pipe restriction argument than I was, but I still find it strange that the flow rate(s) are much the same on house or DHW with vastly different pipework runs.
I have spent  some time looking at the set up and thinking about it and I have come to the conclusion that neither the DHW pipework nor the radiator/ volumiser pipework is acceptable, irrespective of if a second pump is used.
I may be able to reduce the number of elbows (more so on DHW), but Plex pipework will have to be used and the only form of 90Deg fitting I have found so far, is a very sharp elbow, of which my installation has quite a few.
It is very difficult at any time to find a decent contractor here and it will be impossible to find one that will work to my instructions with e.g. straight Plex fittings combined with, perhaps, oversized elbows. Consequently, I may have to do this modification myself, but think I will have to wait until the heating season is over.
I cannot contemplate making any changes to the copper radiator pipework - I am an old man and one way or another, I will be moving on in the not too distant future!
In looking at a better pipework layout adjacent to the Ecodan, it occurs to me that the pipe run could, possibly, be better if the volumiser was to be in the flow rather than the return.
I will add a preliminary sketch and would appreciate your assessment on the relative merits of locating the tank in the flow or return.
I am quite undecided on making provision for a second pump in the repipe, but it would be expensive and sizing would be something of a guess.
As ever, your comments appreciated.
Fronius EV Charger
Kia e- Niro 64kW
OK.
Im sorry to hear you are not feeling well and wish you a speedy recovery.
In a slightly perverse way I was hoping you were going to tell me that the 25mm pipework was much longer, as this would have explained everything.  As it is Im not sure we yet have an explanation and until we have one I wouldn't be confident about a solution!  However I think its worth fleshing out what the explanation would have been as it may yet turn out to have elements of truth.
So in summary you have a poor flow rate now, without a buffer.  When you had a buffer you had a not great flow rate (ie << target) in the primary, we dont know about the secondary.  Furthermore the flow rate for DHW is roughly the same as for space heating.  The poor flow rate now is causing a high DT, which of course is reducing efficiency.  Furthermore I suspect that there may be loops in the space heating where the flow rate is reasonable and the DT OK, and loops where it is very poor, causing cold areas.  This could be significantly exacerbated by the change of buffer and more specifically the removal of the secondary pump.
Logical conclusion which would explain these would be that there is a major head loss/resistance in the common parts of the primary which, if you had told me that there was 10m of plastic pipe (20m in total out and back and bearing in mind that the ID of 20mm plastic is the same/less than the ID of 22mm copper) and a fair few elbows would have been correct.  However you didn't, leaving still the question why is the flow rate low still a mystery.  Something has to be throttling it! (An alternative explanation btw is that the pump is faulty)
There is a calculator here which calculates the head loss through plastic pipe which, in combination with the pump curve should allow one to calculate either throughput given head or head given throughput.  Here is a screenshot.  Putting in figures based on what you have said suggests 1m headloss max, whereas the pump is  supposedly good for 7m (5m at 32l/min)
Nevertheless it does seem likely that the head loss in what was the primary must be significant.  Perhaps there are other restrictions - eg a filter (other than the one in the heat pump) which is too small, more bends than allowed for, undersized shut off valves, that 3 way valve (what model?) etc.  I do think this explanation is worth pursuing if only to rule it out, and an examination of what is actually there will flush this out.
As to the copper pipework 2*22mm should  be sufficient assuming that the two halves are reasonably balanced in their demands, the runs aren't extremely long and it doesn't downsize to 15mm immediately it becomes invisible.
I would suggest that the next step is to take another look at what was the primary to assess if its possible that the head loss is quite a bit higher than the calculation based on 2*2m plus a couple of elbows would suggest.
In terms of solution, until we have worked out an explanation I hesitate to speculate but just swapping the volumiser between flow and return wont fix it unless it removes an obstruction.  Finding the obstructions and removing them is the best solution,l alternatively I think it is a second pump.  Im not sure it needs to be sized accurately as the current pump is adjustable, so in principle all you need is to 'lose' say 4m of head at 32l/h, which the pump you already have is perfectly sized to do.  Id want to check with someone who is familiar with putting two pumps in series first, but cant see why this wont work
This post was modified 1 week ago 5 times by JamesPa
PS to above:  This page from the R32 manual suggests a much less capable water pump might be fitted than the one you have quoted - something isnt stacking up, do you happen to have the model number of the Hydrobox?.  It also suggests that 2 pumps may be necessary.  The curves below may of course account for the head loss of the hydrobox itself.
This post was modified 1 week ago 3 times by JamesPa
(@davidalgarve)
@jamespa Hello James. Thank you for the new comments.
Dealing with new questions first:
My Ecodan spec is an EHSC VM20.UK
IMG 0779
I had previously obtained the pump curve as published by Mitsu for the EHSC, but once I gained access to the Grundfos pump I felt that this would be a much more reliable source for information on the specification. here:
IMG 2210
Note that this model has neither on board control or local status indication and in this respect, resembles the one in the brochure referred to as UPM3 with two PWM profiles. Consequently I am reasonably confident that this is the data we can use.
Screenshot 2026 02 09 at 16.25.11
I have also been wondering about the 3 way valve and whilst I think it is generally a reasonable choice, I do now wonder about the sizing at 20mm
See below:
IMG 2226
However, the more I look at the pipework, the more I am dismayed at the number of severe elbows, e.g. this 3/4" one after the 3 way valve.
IMG 2227
My suggestion of putting the volumiser in the flow rather than the return was more aimed at reducing the number of elbows rather than an inherent advantage in one or the other.
It may well be necessary to fit a second pump, but I don't want to go to the expense of a new pump before seeing what can be achieved with improved pipework. I don't favour installing the old pump because, although it is a PWM, I don't have the speed change control.
I continue to search for Pex pipe and fittings and so far I can only find straight couplings or severe elbows in 22mm and there is little available in 32mm.
Incidentally, I note that the current return from the volumiser is, in fact, 32mm, so I would aim to retain a longer length of this if I do re-pipe.
I am still trying to think of someone I could trust and that would be willing to do the re-piping, but I will almost certainly wait until the end of the heating season now.
Fronius EV Charger
Kia e- Niro 64kW
Thaks for the response, either the pump is faulty or there must be restrictions somewhere so I think you are now on to it.  Probably worth tracking down all the bends then thinking about a more sane route and how you can use swept bends.  A 3/4" elbow is madness if you are trying to get 32l/min through!  32mm copper pipework is what you really need until it splits to 2*22; you might just get away with 28mm but its taking a big risk.  32mm pipework is rather clumsy so short lengths and few bends is rather desirable to say the least.
Fair enough
Thats 1m head loss at 32l/min according to the data sheet.  Based on the performance curve you need somehow to save about 3m of head loss; swapping this for a 32mm one wont be cheap, but will make a big contribution.
I think thats sensible TBH if you are prepared to experiment.  Its flow rate that matters and the heat pump measures that, so it doesn't have to be done in the heating season.  A good plan for route and pipe sizing (as well as some approx calculations) is the key to making this work, and you perhaps consider some temporary 'experimental' links to diagnose head loss in each part as you go along so you know where to focus.  I note that the rating plarte for the IDU says 'allowance for 3 pumps' so Im guessing that there are additional PWM connections available if you need them.
Im pretty confident that the problem is now identified, which is more than half the battle!
This post was modified 7 days ago by JamesPa
(@davidalgarve)
@jamespa Thank you James.
One of the most effective changes that I could make, is to reconnect the 3 way valve to the top left connection on the volumiser, (where it was originally in buffer tank configuration) and this would eliminate a number of reducers and elbows and a length of pipework.
The bottom connection on the same side of the tank would give the straightest, simplest route for onwards to the radiators.
Obviously, in the case of a buffer, it is essential to make connections across the tank, but is it just as desirable in a volumiser?
Fronius EV Charger
Kia e- Niro 64kW
No, what you want in a volumiser is to ensure that the whole tank is 'engaged' ie you dont get dead spots or stratification, otherwise you are reducing its effective volume.  So (at least as far as I can see applying 'first principles') in and out on the same side is fine so long as one is at the top and the other at the bottom (preferably in at the top and out at the bottom so the flow is in the opposite direction to any stratification which does occur).
(@davidalgarve)
@jamespa Thank you again.
In that case, that is the first thing I will try.
This tank is located in an attached pump room and insulated, but it will probably be worthwhile to box it in with additional insulation in view of the higher temperatures.
Fronius EV Charger
Kia e- Niro 64kW
Page 5 / 6