@adamk Is your vibration the one with the base thats slightly unlevelled and large glass doors reverberating? forgive me if I confused you with another


Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.


   
ReplyQuote
(@adamk)
Reputable Member Member
Joined: 7 months ago
Posts: 122
Topic starter  

@ashp-bobba sounds like me yep.



   
ReplyQuote
(@jamespa)
Illustrious Member Moderator
Joined: 2 years ago
Posts: 2936
 

Posted by: @adamk

@drei I’ve not been able to find a local installer let alone someone who can pop round to have a look. I think I might be the only Vaillant 7kw in a 20 mile radius. My issue, after they finally sort the breakers out in October (only 3 months of chasing), will be hopefully only be the humming noise which whilst drives me nuts I would think is fixable even if I have to get the primaries run around the outside of the house and abandon the ones in the ceiling.

By way of encouragement I think you are right about the hum, its fixable.

 

Regarding the breakers I really wouldn't fret about these. 

Best practice is a Type B RCD (which protects people against electrocution in the event of several types of fault) + an MCB.  However the IET regulations, which are definitive, don't require an RCD for fixed external plant.  This is left to the discretion/judgement of the sparks, who is free to do a risk assessment and conclude that an MCB alone (which protects the cable from fire, and thus the building ditto, but doesn't really protect people at all) is required. 

Now if you read very carefully the Vaillant instructions they say 'if the installation requires it then a type B RCD must be used'.  The key here is the wording ''if the installation requires it', ie Vaillant are not saying it does, they too are leaving this to the sparks judgement and local regulations.  They are only saying that if the sparks determines that an RCD is required then it must be type B.

Thus a MCB only is consistent, at least in my reading, with both the IET regs and the Vaillant rubric.  Since a Type A RCD (the default) offers more protection that an MCB alone, it follows that this is no less safe than something that is perfectly acceptable.  As the RCD cant damage the heat pump, it is no worse than just having an MCB, which is legit.

I'm not saying that you shouldn't insist on the swap out, merely that I wouldn't stress about it in the mean time.  There are, after all, plenty of houses where all the internal circuits are protected only by MCBs or even fuses.  The protected circuits will include the ring main, into which you plug a variety of devices on flexible leads, and which are much more likely to develop a potentially dangerous fault than a fixed ASHP (like, for example, a steam iron)

When this issue first came up in another thread, I searched for any case of a person being killed or injured by an aircon unit, of which there must be millions in the UK, many protected only by MCBs.  I found one case of an engineer who was killed due to faulty wiring whilst he was servicing an aircon unit, but the wiring in question had nothing to do with the unit.  Of course I cant guarantee that my search was comprehensive, as I have access only to the same information as you, but its clearly an event which is highly unlikely to occur

FWIW my ASHP is on a MCB only, because this is what would fit in the existing CU and my electrician, who I have known for 12 years, have interrogated on many occasions and thoroughly trust, assessed that his was sufficient.  I'm guessing yours did the same.  In my case this will likely change when the CU gets replaced, which will likely occur when I decide to add an EV charger and an induction hob.  Until then it can live on the MCB alone!

I reiterate that I'm not saying that you shouldn't insist on the swap out, merely that I wouldn't stress about it in the mean time.

 


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   