@uk_pete_2000 to be honest we are still learning so trying to find the best place for it however this is mainly redundant now as we have moved over to full WC. As I say we are just starting this journey and as a Yorkshireman I already ruing the last few decisions I have made (wincing at the smart meter every time I walked past it) but with the help of the good people on this forum we are getting there!
Regards
Si.
Kind Regards
Si
——————————————————————————
Grant Aerona3 13kW
13 x 435w + 13x 480w Solar Panels
Sigenergy 10kW Inverter
16kW Sigenstor battery
Posted by: @grantmethestrength@uk_pete_2000 to be honest we are still learning so trying to find the best place for it however this is mainly redundant now as we have moved over to full WC. As I say we are just starting this journey and as a Yorkshireman I already ruing the last few decisions I have made (wincing at the smart meter every time I walked past it) but with the help of the good people on this forum we are getting there!
Regards
Si.
Sitck with it, if you get your WC curve down to the lowest possible consistent with heating the house you should have an efficient system and plenty on here are keen to help. Also remember that high consumption now will be balanced by much lower consumption in the shoulder and low heating seasons, when you need less heat and your heat pump produces it more efficiently.
If you haven't already you may also need to 'balance' the radiators, ie adjust the lockshield valves to get either the same temperatures in all rooms or the temperature differential you want. This is a bit trial and error but pays dividends once you get it right. Its made easier by the fact that rooms are generally poorly insulated from each other, so heat gets shared anyway.
As to setbacks, the commentator above and your installer are right that a modest setback during the Cosy expensive rate and/or overnight if you wish can make sense, but ideally you need to vary the flow temperature not just turn it off. Some heat pump controllers (eg ideal, Vaillant, possibly others) are designed to do this (they 'disguise' it as changing the room temperature, even if you are operating on pure WC, to make it more user friendly. 'Under the hood' they are just changing the flow temperature). I dont know if the Grant controller can do this, either maybe another Grant owner can comment. That said just turning off for the 3 hr expensive Cosy peak probably will be OK as long as the house doesn't cool by more than a fraction of a degree.
Im personally doubtful about Cosy as a practical tarrif unless you have a battery or a very smart controller designed for tariff optimisation, like Homeley or Havenwise. After doing some analysis I went for Eon Smart Drive which gives you 7 hrs at 7p/kWh overnight, easier to manage! I do have an EV but it will still help my heat pump costs. However these things are cricitcally dependent on your personal and house circumstances.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa Thanks for the words of encouragement I dialled down the weather comp to 38c @ 0c last night and even though it was 0 outside the house never went below 21 which was too hot, so down it goes again!! The Grant does have an eco and nightime mode I am going to look into those as that seems to be the best way to modulate it.
The pump is cycling a lot but I guess it is not short cycling so that is a good thing, still burning way too much electricity! I would be interested to know how other similar Aerona3 13 kwh compare for normal jogging power draw.
Regards
Si.
Kind Regards
Si
——————————————————————————
Grant Aerona3 13kW
13 x 435w + 13x 480w Solar Panels
Sigenergy 10kW Inverter
16kW Sigenstor battery
Posted by: @grantmethestrengthThe pump is cycling a lot but I guess it is not short cycling so that is a good thing
Is it cycling or defrost. More likely the latter at current overnight temperature
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaSome heat pump controllers (eg ideal, Vaillant, possibly others) are designed to do this (they 'disguise' it as changing the room temperature
Thank you for that, on those HP that have this facility then setback will work.
The Grant doesn't have this, but it may be included in the new controller.
Posted by: @grantmethestrengthThe Grant does have an eco and nightime mode
I just looking into those myself. From what I gather you just put a wire between the two contacts to turn it on. You could use a Grant EP001 (edit should read EP002) and a mains switch inside the house and just run a 12v wire outside, connect to each side of the terminal. Then you can turn on/off those settings when required.
Not sure if you can switch them on via modbus, without the wires.
I did find a note somewhere that one will slow it down and the other will effect the compressor by 50%, but it also seemed to indicate the the compressor may run at this setting all the time. At present my compressor runs below 40%
@grantmethestrength i had 2x10kw grant aeronas installed in 2021 and am still learning and have ongoing projects to better insulate pipe runs etc. and putting stud wall in the garage to make a plant room to improve heat loss where the cylinder and incoming pipework from the HP are.
I have WC on and have long pipe runs in a dormer so the furthest bedrooms are always on the cooler side especially my sons which has also has 3 external walls which doesn't help.
I've never got my head around why 2 HP were installed rather than a 17kw single unit but that was the installers perogative at the time. I also don't understand why the heating is switched off when heating the HW cylinder and would much rather heat the cylinder via immersion at TOU tariff overnight to give consistent heating but it was never set up that way.
@allyfish has provided invaluable resources and I have adjusted flows etc which has helped with running costs but is still hellishly expensive November to March to run only to be offset in the warmer months.
I'm hoping that when the HP (?20 year life span) do need replacing the technology then will at least half the running costs.
2 10kw Grant Aerona3
Heat loss calc 16.5 kw @ -2.8 degrees
4.32 PV
Posted by: @uk_pete_2000Posted by: @jamespaSome heat pump controllers (eg ideal, Vaillant, possibly others) are designed to do this (they 'disguise' it as changing the room temperature
Thank you for that, on those HP that have this facility then setback will work.
The Grant doesn't have this, but it may be included in the new controller.
It's actually quite a revelation to see how Vaillant and ideal have designed the UI to WC. I suspect this because they have 20 plus years of experience of compulsory WC (for boilers) in some mainland european markets, so have worked out how to present it to the 'punter' in a way they have some chance of understanding
What they have done is actually quite simple, but goes a long way to bridging the gap between the human desire to control based on IAT, and the fact, dominated by unavoidable physics and the dynamics of control loops, that control based on OAT works better.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @bretixI also don't understand why the heating is switched off when heating the HW cylinder and would much rather heat the cylinder via immersion at TOU tariff overnight to give consistent heating but it was never set up that way.
This is simple. Heat pumps and boilers can only supply water at one flow temperature at any one time. You need a higher ft for the dhw than you need for space heating, so it's inevitably one or the other. The only way to avoid this is to operate permanently at the much higher temp needed for dhw, which makes space heating inefficient both for boilers and heat pumps.
In the UK we have historically suffered this inefficiency for boilers, costing us for the past 20.years an additional 10% on our gas consumption as well as a reduction in comfort. Other countries with more advanced heating industries have operated in either-or mode for decades. You could still heat both dhw and space simultaneously with a heat pump, but efficiency has become more important because of rising energy prices, so the general choice is not to.
There is nothing at all to stop you turning off the dhw cycle on your heat pump and heating overnight or whenever you have cheap electricity via the immersion. It's entirely your choice.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Some where, someone said they had two HP. with this setup and some changes to the pipes, you could have one HP deal with DHW and CH and the other one just looking after the CH
Allows the best of both
Posted by: @uk_pete_2000Some where, someone said they had two HP. with this setup and some changes to the pipes, you could have one HP deal with DHW and CH and the other one just looking after the CH
Allows the best of both
You can (just like you can have two boilers) but unless you use vast amounts of dhw to the extent that the dhw is a material proportion of the total daily energy demand, there is not much point. Better just to tweak your settings to do whatever it is you want to do.
Most of the time your ashp has plenty of excess capacity assuming it's designed to cope with the standard requirements. If it is getting challenged on the coldest days because it is well matched to the demand, switch on the immersion during a cheap rate period. That will only be necessary for a handful of days per year.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @uk_pete_2000Some where, someone said they had two HP. with this setup and some changes to the pipes, you could have one HP deal with DHW and CH and the other one just looking after the CH
Allows the best of both
You can (just like you can have two boilers) but unless you use vast amounts of dhw to the extent that the dhw is a material proportion of the total daily energy demand, there is not much point. Better just to tweak your settings to do whatever it is you want to do.
Most of the time your ashp has plenty of excess capacity assuming it's designed to cope with the standard requirements. If it is getting challenged on the coldest days because it is well matched to the demand, switch on the immersion during a cheap rate period. That will only be necessary for a handful of days per year.
Sorry I think you lost the point. The main question was about the CH turning off when DHW was being called for.
So having two HP, that person can have one looking after DHW & CH, while the other one just deals with CH. That way the house will always receive heat and the DHW request will not effect it.
- 26 Forums
- 2,418 Topics
- 54.8 K Posts
- 332 Online
- 6,098 Members
Join Us!
Worth Watching
Latest Posts
-
Is my Samsung gen6 outside air temp sensor missing a sheath/sleeve?
Good afternoon Been having some niggles with cycling ...
By Papahuhu , 4 minutes ago
-
Perhaps I am just a fuss pot - but I am curious too!
With all the talk in the past about reducing ‘distortio...
By Toodles , 11 minutes ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
One more earthing question occurs to me. If, as now se...
By JamesPa , 38 minutes ago
-
RE: Daikin Wireless Thermostat
@bash We have a Daikin EDLA08 Monobloc standing by our ...
By Toodles , 46 minutes ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
Thats great thanks. TBH setting the low end o...
By JamesPa , 48 minutes ago
-
RE: Say hello and introduce yourself
@mrfield, welcome to the forums. Please go here and ...
By Mars , 2 hours ago
-
RE: Reliable, easy to use home battery options
Clearly aware we are talking about safety here. But a s...
By Batpred , 2 hours ago
-
RE: Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
@ashp-bobba Thanks for the reply. Would it not work ...
By Patch321 , 2 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
I did not hear back from the tech team. (Assume they ar...
By swwils , 3 hours ago
-
RE: How to use my Hanchu battery storage for home without it feeding back into the grid?
Hi. My Hanchu battery system is controlled by the (Lux...
By SKD , 5 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
In the Home Assistant firmware the data points...
By F1p , 16 hours ago
-
RE: GSHP WOES! Midland based engineer recommendations?
@johnbroome if it is not the pressure in the expansion ...
By ASHP-BOBBA , 17 hours ago
-
So I hear the export MPAN that UKPN assigned should be ...
By Batpred , 20 hours ago
-
RE: Ideal HP290 14kW ASHP - how to optimise
Roughly this should cost you £250-£300 per peak month a...
By ASHP-BOBBA , 21 hours ago
-
RE: New Daikin 11kW Altherma 3M install - is it working as it should?
@toodles Thank you for your input. As the days have got...
By Synthbuilder , 1 day ago
-
RE: Fan unit Making terrible noise HELP!!
@gutoffowc Oh no, sorry to hear that, are you in the Ke...
By ASHP-BOBBA , 1 day ago
-
RE: Sunsynk Whole House Backup Issue
@sheriff-fatman - could you please re-post that in the ...
By Transparent , 1 day ago
-
RE: Running my new Nibe ASHP efficiently
I didn't. I spent a while manually messing around with ...
By jamieheatpumpnew , 1 day ago
-
RE: I’m glad the cold spell is over!
I comparison with the 65kWh used above yesterday was on...
By Judith , 1 day ago