Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Grant Aerona circulation/system pump staying on
Just wonder if other Grant owners (or owners of other makes) have ever had the circulation pump (sometimes called the system pump) stay on permanently. On the control panel, it's the circle symbol with a solid, right-pointing triangle in it. Any ideas welcome.
This is part of the Grant's 'frost protection' system (as opposed to the 'defrost cycle' which we're all familiar with in this type of weather!), which runs the system pump continuously once the outdoor temperature goes below 4C, and stays on until it rises above 7C. There are a number of triggers for the system pump for frost protection, but this seems to be the common one.
You have some control over the 4C/7C mentioned above (parameters 43 11 and 43 12) but I've left mine on their defaults. In the cold snap in December my pump ran for over 10 days continuously, but it's just 100W (or thereabouts), so small fry compared to the rest of the system.
Grant Aerona 3 10kW
Thanks for the reply, and it's what we thought at first but the frost protection symbol doesn't come on. Also, it only started a few days ago (i.e. not in the first cold snap at the start of December). The outdoor temp that triggers this seems to be 5C but just waiting for it to reach this outside to confirm. Another anomoly is the outdoor temp reading on the control panel looking a bit crazy - last night it was 1.5C, then 15 mins later it was 7.5C, then another 15 mins fell back to 2C 🤔
Parameter 43/11 is currently 0C; 43/12 is 1C.
As Mike suggested, the system pump turned off at outdoor temp 7C but how can this is be if 43/11 is 0C and 43/12 is 1C - and why doesn't the frost protect symbol come on...?
I've just checked on my controller and Frost Protection symbol isn't on, even though Frost Protection is running. The explanation of all of the symbols is possibly not accurate/complete in either the Grant or Chofu documentation? e.g. the 'black tap' symbol flashes if in DHW mode but Comfort temp has been reached (so no DHW heating is actually needed), and this is not mentioned in the docs.
As an aside, I've also noticed that the Controller gives temps to 0.5C granularity, but the modbus interface only to the nearest degree. Which is annoying.
Grant Aerona 3 10kW
That's interesting - stupid question here but how do you know frost protection is running if the symbol isn't on?
I'm close enough to the pump to hear it running, but the compressor isn't on, just the pump. And it ties in with the outdoor temp being between 3C and 7C.
tbh, I only really noticed it when I started logging all of the parameters to a database and graphing the output, so could see this 100W of background usage when nothing else was happening, and it tied in to outdoor temp in the right range.
"there are no stupid questions" 😀
Grant Aerona 3 10kW
Thank you for making me not feel stupid 😌 I will try to continue in a similar vein.
If we assume the pump here is coming on in protection mode, the next question is why does it do this at 7C when the parameters are set to 0C/1C?
I've checked the other defrost trigger types (in addition to outdoor temp) and they're both enabled: room temp (10C, hysteresis 1C); outgoing water temp (1.5C, hysteresis 1.5C).
I've noticed, though, that there are two parameters for hysterisis of flow water temperature: 43/14 (set to 3C) and 43/22 (set to 1.5C) - could there be conflict here?
The control panel also says parameter 43/13 is 4C but I can't find an explanation for this one in the Grant manuals.
43 13 = "Backup heater set point during Frost protection" which I guess means that if you have a backup heater, that's when it will start to help with frost protection?! Do you have one?
Your earlier post implied that maybe there's an issue with the outdoor temp sensor? It's just at the back of the HP at the top, so maybe have a look at that or check the PCB connection? Also I think a hysterisis of 1C is a bit low, and might cause cycling of the frost protection on/off a lot. Do you know why they aren't the default values? Was a note placed on the installation guide?
Grant Aerona 3 10kW
@mikefl No back-up heater, so can't be that, but thanks for confirming what the parameter is.
43/11 and 43/12 are set low because antifreeze protects the system down to at least -12C. The manual actually says the antifreeze function can be disabled if 'a suitable concentration of glycol is present in the system water.' It can be turned off at the pump PCB but (I presume) it's still switched on here because the protection symbol did come on during the cold snap in December.
I think we probably need to test some different parameter settings, including hysteresis, to see what happens. Temps should drop low enough later to do this.
And, yes, I do wonder about the outdoor sensor. It looks ok from the outside but, as you say, may be an issue with the PCB connection.
@mikefl The plot thickens. Spoke with a Grant trained engineer who says if the frost protection symbol isn't coming on then neither is the frost protection itself. They've suggested a sensor or PCB issue so this is the next thing to look at with the installer before contacting Grant themselves.
The mysteries of the heat pump...
There's also a parameter (41 22 I think) which controls how long the system pump runs after the compressor is off. I don't think this can run to hours though. My money is still on frost protection though. The indicator may be faulty.
Grant Aerona 3 10kW
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 307 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Our Cosy 9 has been in hush mode for three days. So far...
By KevH , 6 minutes ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 4 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 16 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 18 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 18 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 21 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 1 day ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 1 day ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 3 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 3 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago