Grant 13kW Aerona3 - issues getting zones to temp

435 Posts
14 Users
79 Reactions
54 K Views
(@kenbone)
Estimable Member Member
Joined: 2 years ago
Posts: 44
 

@crimson it all depends, on how many rads/ufh are fully open (no actuators or TRVs, a volumiser won't hurt the system (i have 420l worth), that i can bring in and out of my system, but my system i use for testing products.

Is it the older Aerona 3 unit.



   
ReplyQuote
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 3143
 

Posted by: @crimson

I’m looking at the diagram in the manual and nowhere is there a LLH, item 6 is a volumiser, on the return.

No idea why they’re insisting on the LLH. Should put in a volumiser (80-100 litres) on the return in place of the LLH. Run the flow direct from ASHP to the heating system and DWH, obviously to the valves etc.

And remove the internal pump room pump thats on that, as with no LLH don’t see why would need it.

 

Very frustrated with these guys.

You are correct you dont need the second pump if there is no LLH/Buffer (unless there is a 'head' problem with your downstream system)

Its entirely understandable that you are frustrated.  Sadly, in my work life as well as my home life, I have been there several times with tradespeople of various sorts (but generally plumbers or electricians). 

Its very difficult, in my personal experience, to reason with tradespeople who don't understand what they are talking about.   There are two ways to rationalise this:

a) conscious incompetence

They know they don't understand what they are talking about, but daren't admit it.  So they try to cover themselves by using technoBS.  This works on most people because most people are either not capable of challenging them with logical arguments or don't care to do so. 

b) unconscious incompetence

They don't even realise that they don't understand what they are talking about  So they say what they believe even though its BS.  This works on most people because most people are either not capable of challenging them with logical arguments or dont care to do so. 

In either case arguing with them is difficult.  Perhaps a psychologist would do better than I do, because its probably more a psychological problem than a technical one.  Bizarrely its much easier to argue with someone who does know what they are talking about than with someone who doesn't.  

That said they all know the power of the pound.  Dont pay until you are happy (but make sure you keep a paper trail) but at the same time make sure they remain responsible.  Tricky balance, but the one you somehow need to strike as I know you appreciate.


This post was modified 3 days ago 3 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@crimson)
Honorable Member Member
Joined: 2 years ago
Posts: 230
Topic starter  

I hope out of all of this that I can run the system at a much lower flow temp.

 

Checked back through endless mails on calcs and it looks like rad wise (this is in addition to ASHP oversizing rads at delta 16.5, so rad output divided by 0.237 for non Eskimo and 0.33 for Eskimo - against the room watt requirements- hence me stating over-oversized as its versus those watt calcs)

 

Bedrooms range from:

15-115% over-oversized (only the office I like at 21C and thats 115%, others we have at 18C)

 

Living rooms (Eskimo)

30-45% over-oversized

 

Still have a main bathroom 14% undersized and an en-suite 24% undersized. But I suspect they’ll be fine as both have electric underfloor in addition to those rads/not really rooms we spend time in.

This makes me glad at least that the rad uplifts works seemed a sound thing to have done.

The substantial oversizing was due to simply doubling heights/K1-K2 changes to minimise non plumbing works (removing skirting/decor etc etc)


This post was modified 2 days ago 2 times by Crimson

   
👍