Grant 13kW Aerona3 - issues getting zones to temp
@crimson it all depends, on how many rads/ufh are fully open (no actuators or TRVs, a volumiser won't hurt the system (i have 420l worth), that i can bring in and out of my system, but my system i use for testing products.
Is it the older Aerona 3 unit.
Posted by: @crimsonI’m looking at the diagram in the manual and nowhere is there a LLH, item 6 is a volumiser, on the return.
No idea why they’re insisting on the LLH. Should put in a volumiser (80-100 litres) on the return in place of the LLH. Run the flow direct from ASHP to the heating system and DWH, obviously to the valves etc.
And remove the internal pump room pump thats on that, as with no LLH don’t see why would need it.
Very frustrated with these guys.
You are correct you dont need the second pump if there is no LLH/Buffer (unless there is a 'head' problem with your downstream system)
Its entirely understandable that you are frustrated. Sadly, in my work life as well as my home life, I have been there several times with tradespeople of various sorts (but generally plumbers or electricians).
Its very difficult, in my personal experience, to reason with tradespeople who don't understand what they are talking about. There are two ways to rationalise this:
a) conscious incompetence
They know they don't understand what they are talking about, but daren't admit it. So they try to cover themselves by using technoBS. This works on most people because most people are either not capable of challenging them with logical arguments or don't care to do so.
b) unconscious incompetence
They don't even realise that they don't understand what they are talking about So they say what they believe even though its BS. This works on most people because most people are either not capable of challenging them with logical arguments or dont care to do so.
In either case arguing with them is difficult. Perhaps a psychologist would do better than I do, because its probably more a psychological problem than a technical one. Bizarrely its much easier to argue with someone who does know what they are talking about than with someone who doesn't.
That said they all know the power of the pound. Dont pay until you are happy (but make sure you keep a paper trail) but at the same time make sure they remain responsible. Tricky balance, but the one you somehow need to strike as I know you appreciate.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I hope out of all of this that I can run the system at a much lower flow temp.
Checked back through endless mails on calcs and it looks like rad wise (this is in addition to ASHP oversizing rads at delta 16.5, so rad output divided by 0.237 for non Eskimo and 0.33 for Eskimo - against the room watt requirements- hence me stating over-oversized as its versus those watt calcs)
Bedrooms range from:
15-115% over-oversized (only the office I like at 21C and thats 115%, others we have at 18C)
Living rooms (Eskimo)
30-45% over-oversized
Still have a main bathroom 14% undersized and an en-suite 24% undersized. But I suspect they’ll be fine as both have electric underfloor in addition to those rads/not really rooms we spend time in.
This makes me glad at least that the rad uplifts works seemed a sound thing to have done.
The substantial oversizing was due to simply doubling heights/K1-K2 changes to minimise non plumbing works (removing skirting/decor etc etc)
- 26 Forums
- 2,227 Topics
- 49.5 K Posts
- 445 Online
- 5,892 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa ok got home and I can indeed set the flow temp...
By AdamK , 2 hours ago
-
I'll leave it tonight and post the graph tomorrow to se...
By bontwoody , 3 hours ago
-
RE: New Fogstar 15.5kWh upright solution
That's odd. I can't see anything in the Sunsynk manua...
By Transparent , 3 hours ago
-
It’s my sole reason to always deter homeowners from goi...
By Mars , 5 hours ago
-
Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
I ended up with a Solis S6-EH1P8K-L-PLUS (8 kW) hybrid ...
By Batpred , 5 hours ago
-
RE: Options on flushing my system
@grantmethestrength with your pragmatic approach and &#...
By SUNandAIR , 7 hours ago
-
RE: Samsung Heat Pump – Can't Activate TW2 Pipe Sensor (for Delta T Control)
@batpred For the moment I'm sticking with what I have, ...
By bubuontheweb , 8 hours ago
-
RE: Electricity price predictions
Nice to be back on track! If we all had the interest, s...
By Batpred , 9 hours ago
-
RE: Say hello and introduce yourself
I think this is where we may differ. Nothing makes sen...
By JamesPa , 9 hours ago
-
RE: Daikin Octopus installation update - I saw my first defrost. 😍😂
Enable installer mode - 5678 Enter the Space Heating/...
By RadWhisperer , 9 hours ago
-
Is your installer MCS certified? If so, they should reg...
By Old_Scientist , 9 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
@hcas So the answer from Mitsu was: To Confirm you ca...
By bontwoody , 12 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Grant Aerona 3 10 HPID10R32
By MDG , 13 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I don't know! The Midea manuals and what actually happe...
By cathodeRay , 13 hours ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
If you’re interested in finding out which of your neigh...
By AgentGeorge , 14 hours ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
It is a crazy situation. It also seems not enough 400kv...
By Batpred , 16 hours ago
-
RE: Rate the quality of your heat pump design and installation
More like Octopus wanted to fit a Cosy 6 at the end of ...
By RadWhisperer , 19 hours ago
-
RE: How good is the app support for your heat pump?
Yes. Personally I would only use a heating control app ...
By Batpred , 1 day ago