Posted by: @kev-m@Markc, very interesting. Was your house warm enough with the lower flow? To use the car analogy quoted by someone else, you have better mpg but you're driving further.
How do you scale the MELcloud output to look like that? I could post some of mine but they won't look as neat as yours. My overall consumption is similar but much spikier as I've been varying the room temp using the thermostats.
Have you looksed at the csv output?
The house was equally warm, maintaining 22º for both 50º and 35º flow.
I've photoshopped the screenshots together to make them more readable.
I did look at the CSV output but it seems to totally ignore the date selectors and I always just get the first 4 months worth of data which is useless.
@markc it's important to remember COP isn't just a function of power used, it's also of heat delivered. When you have a cop of 3.5 Vs 2.5 you are delivering far more heat. Looking at your figures at 2.5 you used 22kw so delivered 48kw of heat. At 3.5 you used 24kw but delivered 84kw of heat. Almost double.
Posted by: @batalto@markc it's important to remember COP isn't just a function of power used, it's also of heat delivered. When you have a cop of 3.5 Vs 2.5 you are delivering far more heat. Looking at your figures at 2.5 you used 22kw so delivered 48kw of heat. At 3.5 you used 24kw but delivered 84kw of heat. Almost double.
Good point but where has the extra 36kWh gone? If 48kWh is enough to heat the house - which it is - why hasn't this been delivered at a COP of 3.5?
Hi Mark,
The difference in heating energy used (as shown by the graphs) is easily explained, in the first case with the water flow temperature at 50C, when the system initially switched over from DHW heating to CH, the heat source for the radiators was actually the hot water tank rather than the ASHP.
Comparing individual days is very difficult, since no two days are identical. When I look at my data for the 21-10-21 compared to the 3-11-21, I find that there was over twice as much solar PV generation, so on the 21-10 your home would probably have received more solar gain, hence less heating required. Our energy consumption on 3-11 was 1.5 times that of the 21-10.
Posted by: @batalto@markc it's important to remember COP isn't just a function of power used, it's also of heat delivered. When you have a cop of 3.5 Vs 2.5 you are delivering far more heat. Looking at your figures at 2.5 you used 22kw so delivered 48kw of heat. At 3.5 you used 24kw but delivered 84kw of heat. Almost double.
The higher COP did deliver more heat yes you are correct.
Given that and thinking about it, selecting individual days that had the same outside temp is not accurate enough.
If for example if the days prior to my examples, 20/10 was warm and 02/11 was cold the heating would have more work to do to get up to temp.
The actual air temperature is just one factor, solar gain, not just through the windows, but on the building fabric itself can have a marked effect on heat loss. Also wind and rain can dramatically increase heat loss and hence heat demand.
Here are my figures based on a 6 day test. All factors the same except for flow temperature and outside environment.
Room thermostats were at 22ºC so there will have been moments where the ASHP had no call for heat.
50ºC flow temp with average outside temp of 11.6ºC. Average COP of 2.7. 286kWh of heating produced. 100kWh of energy used.
35ºC flow temp with average outside temp of 7.8ºC. Average COP of 3.4. 478kWh of heating produced. 130kWh of energy used.
So if my maths are correct, if I had been running the ASHP at 50ºC during the period 02/11 - 07/11, I would have used 177kWh as opposed to 130kWh.
Posted by: @markcPosted by: @derek-mThat is fine Mark, whatever suits you best.
Hi @derek-m. How would you like to go about us setting up my compensation curve?
Good Morning Mark,
Whatever is best for you. We can do it via the forum, direct e-mail, telephone or possibly Skype or similar. The choice is yours.
Posted by: @derek-mPosted by: @markcPosted by: @derek-mThat is fine Mark, whatever suits you best.
Hi @derek-m. How would you like to go about us setting up my compensation curve?
Good Morning Mark,
Whatever is best for you. We can do it via the forum, direct e-mail, telephone or possibly Skype or similar. The choice is yours.
Skype is good. I'll send you a direct message with my username.
I’ve managed to gather data for a couple of six day periods where the average outside temp was 11ºC.
I was running the ASHP differently in each period.
10/05 to 15/05
Running at 50ºC flow,
ASHP controlled by multiple thermostats calling for heat when required. (so like a gas boiler would be controlled)
Indoor temp 18ºC for 20 hours and 22ºC for 4 hours in the evening.
73.9kWh energy consumed.
231.8kWh energy produced.
COP was 2.9
08/11 to 13/11
Flow temp controlled by the compensation curve
Thermostats calling for heat constantly (all set at 25ºC)
Indoor temp maintained at 21ºC-22ºC for 24 hours.
64.3kWh energy consumed.
297.4kWh energy produced.
COP was 4.3
From what I have experienced, using the compensation curve delivers a much more consistent and comfortable level of heating.
UHF is constantly warm under foot, whereas with the on/off schedule it was cool for the majority of the day.
The large thermal mass of my UFH no doubt helps running the system at a constant 22ºC be more efficient compared to an on/off schedule.
-
Struggling to get CoP above 3 with 6 kw Ecodan ASHP
3 hours ago
-
Running my new Nibe ASHP efficiently
1 month ago
-
Have Consumers Been Lied to About the Efficiency of Heat Pumps Made in China?
7 months ago
-
Ecodan consuming 100kwh per day in new build!!!
7 months ago
-
Help with understanding my Mitsubishi Ecodan air source heat pump
10 months ago
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 258 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Setback savings - fact or fiction?
@cathoderay The input power is largely determined by...
By RobS , 31 minutes ago
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
@editor, this is now an example of greenwashing in the ...
By Majordennisbloodnok , 42 minutes ago
-
RE: Electricity price predictions
@transparent Im impressed by all your work on this. ...
By JamesPa , 2 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Just to wrap this up here for future readers: The S...
By Batpred , 2 hours ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Welcome to the forums.I assume that you're getting the ...
By Sheriff Fatman , 3 hours ago
-
RE: What determines the SOC of a battery?
I agree. Fogstar confirmed that the Seplos BMS does ...
By Batpred , 3 hours ago
-
RE: Say hello and introduce yourself
@editor @kev1964-irl This discussion might be best had ...
By GC61 , 4 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@benson — as @tasos suggests, plotting multiple variabl...
By cathodeRay , 6 hours ago
-
@painter26 — as @jamespa says, it's for filling and re-...
By cathodeRay , 8 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 19 hours ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 20 hours ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 24 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 24 hours ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 1 day ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 1 day ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 1 day ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 1 day ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 2 days ago
-
RE: DIY solar upgrade - Considering adding more panels
I know this is a bit old, but it made me wonder what co...
By Batpred , 2 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@majordennisbloodnok Daikin, take note! (In fact, I hav...
By Toodles , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
@mk4 — good work! First, I agree, no evidence of cycl...
By cathodeRay , 2 days ago