Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Evaporator Temperature
Interested in hearing from others on their Heat Pump evaporator temperature just prior to a defrost. A few other bits of data might be useful. My details are:
Evaporator -23C. OAT -4C. Defrost cycle every 46 minutes. Southern England.
Hitachi Yutaki SCombi Heat Pump
(Indoor Unit ) RWD-3.0RW1E-220S-K
(Outdoor Unit) RAS-3WHVRP1
2024 build bungalow, Southern england, 179 m2, 14w/m2
Underfloor heating all fully open
7KW heat pump
50 litre buffer tank (4 port)
3.6KW solar panels
For an air-source heat pump the minimum evaporating temperature depends on the compressor design and the manufacturer’s operating envelope.
Typical minimum evaporator (saturation) temperature for R32 heat pumps
–25 °C to –30 °C which is common for modern domestic R32 ASHPs.
Note, some manufacturers restrict operation to –20 °C for efficiency and reliability reasons (reduced thermal stress).
High-performance “cold-climate” units may reach –35 °C, but these are less common in the UK/EU market.
Why the limit exists
At very low evaporating temperatures:
Suction pressure drops very low (R32 saturation pressure at –25 °C ≈ 1.7 bar abs).
Mass flow and capacity reduce sharply.
Risk of liquid floodback to the compressor during defrost increases.
Compressor discharge temperature rises significantly.
Most manufacturers provide an operating envelope showing safe combinations of suction (evaporating) and discharge (condensing) temperatures.
Rule of thumb
If the outdoor air temperature is –10 °C, the evaporator surface will usually sit around –15 to –20 °C (because it must be colder than the air to absorb heat).
This matches what owners see during winter: coils often frost at –5 to –15 °C saturation.
Hitachi Yutaki units predict defrost requirements by a combination of:
1. Outdoor coil temperature sensor
2. Ambient outdoor temperature sensor
3. Refrigerant pressure sensor
4. Runtime / algorithmic prediction
Defrost begins when both the coil temp and calculated saturation temperature indicate that the coil is at or below freezing and the system sees an expected reduction in heat-extraction efficiency.
This means the unit will sometimes enter defrost before you see thick ice, because it's detecting the early film of frost that you can’t see.
Posted by: @iaackFor an air-source heat pump the minimum evaporating temperature depends on the compressor design and the manufacturer’s operating envelope.
Typical minimum evaporator (saturation) temperature for R32 heat pumps
–25 °C to –30 °C which is common for modern domestic R32 ASHPs.
Note, some manufacturers restrict operation to –20 °C for efficiency and reliability reasons (reduced thermal stress).
High-performance “cold-climate” units may reach –35 °C, but these are less common in the UK/EU market.
Why the limit exists
At very low evaporating temperatures:
Suction pressure drops very low (R32 saturation pressure at –25 °C ≈ 1.7 bar abs).
Mass flow and capacity reduce sharply.
Risk of liquid floodback to the compressor during defrost increases.
Compressor discharge temperature rises significantly.
Most manufacturers provide an operating envelope showing safe combinations of suction (evaporating) and discharge (condensing) temperatures.
Rule of thumb
If the outdoor air temperature is –10 °C, the evaporator surface will usually sit around –15 to –20 °C (because it must be colder than the air to absorb heat).
This matches what owners see during winter: coils often frost at –5 to –15 °C saturation.
Hitachi Yutaki units predict defrost requirements by a combination of:
1. Outdoor coil temperature sensor
2. Ambient outdoor temperature sensor
3. Refrigerant pressure sensor
4. Runtime / algorithmic prediction
Defrost begins when both the coil temp and calculated saturation temperature indicate that the coil is at or below freezing and the system sees an expected reduction in heat-extraction efficiency.
This means the unit will sometimes enter defrost before you see thick ice, because it's detecting the early film of frost that you can’t see.
Thank you for the reply. I think you are saying that what I am seeing is normal (Evaporator -23C. OAT -4C. Defrost cycle every 46 minutes).
Hitachi Yutaki SCombi Heat Pump
(Indoor Unit ) RWD-3.0RW1E-220S-K
(Outdoor Unit) RAS-3WHVRP1
2024 build bungalow, Southern england, 179 m2, 14w/m2
Underfloor heating all fully open
7KW heat pump
50 litre buffer tank (4 port)
3.6KW solar panels
@trebor12345 Yes, expect defrost cycles to initiate at evaporator temperatures between -20 and -35 degC depending on refrigerant gas, plant design and application.
The cycle time is dependent more on environmental conditions, heat extraction rates (how hard the compressor is working) and forced airflow rates to the evaporator.
If you imagine a heat pump where the airflow to the evaporator is restricted in some way (caused by poor clearances between surrounding walls, evaporator fan not attaining the correct speed due to incorrect factory setup or maybe the early failure of the evaporator fan bearings) then the defrost cycle would still occur at the expected temperatures but the period between cycles would definitely decrease.
Referring now to your other post on this forum, the ice buildup on your unit does, in my experience, seem a little heavier than I would expect. Hopefully others will contradict me!
- 26 Forums
- 2,607 Topics
- 60.8 K Posts
- 490 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
@editor, I hear that too. I can confirm that out of ...
By ASHP-BOBBA , 2 hours ago
-
End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
As many of you know, our Global Energy Systems heat pum...
By Mars , 2 hours ago
-
@derbygraham fully agree with James, and it’d be good t...
By Mars , 3 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Finally got around to installing and setting up the Sol...
By Mars , 3 hours ago
-
Unfortunately its a function of the physics. Max heat ...
By JamesPa , 4 hours ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 4 hours ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 5 hours ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 7 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 8 hours ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 10 hours ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 12 hours ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 16 hours ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 1 day ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 1 day ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Many thanks for your, and the subsequent, answers tk qu...
By KevH , 2 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 2 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 2 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 3 days ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 4 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@optimistic-optimiser I have has a Daikin for a few yea...
By madsid , 4 days ago
-
RE: UK DIY Battery: SEPLOS 48V 200Ah x2 + Sunsynk 8K – Safe Installation for Garage Conversion
The rule of thumb is to ensure that you can isolate any...
By Transparent , 4 days ago