Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Evaporator Temperature
Interested in hearing from others on their Heat Pump evaporator temperature just prior to a defrost. A few other bits of data might be useful. My details are:
Evaporator -23C. OAT -4C. Defrost cycle every 46 minutes. Southern England.
2024 build bungalow, Southern England, 179 m2, 14w/m2
Underfloor heating, fully open
Vaillant aroTHERM plus 3.5kW
50 litre volumiser
3.6KW solar panels
Tesla 13.5kw Powerwall
For an air-source heat pump the minimum evaporating temperature depends on the compressor design and the manufacturer’s operating envelope.
Typical minimum evaporator (saturation) temperature for R32 heat pumps
–25 °C to –30 °C which is common for modern domestic R32 ASHPs.
Note, some manufacturers restrict operation to –20 °C for efficiency and reliability reasons (reduced thermal stress).
High-performance “cold-climate” units may reach –35 °C, but these are less common in the UK/EU market.
Why the limit exists
At very low evaporating temperatures:
Suction pressure drops very low (R32 saturation pressure at –25 °C ≈ 1.7 bar abs).
Mass flow and capacity reduce sharply.
Risk of liquid floodback to the compressor during defrost increases.
Compressor discharge temperature rises significantly.
Most manufacturers provide an operating envelope showing safe combinations of suction (evaporating) and discharge (condensing) temperatures.
Rule of thumb
If the outdoor air temperature is –10 °C, the evaporator surface will usually sit around –15 to –20 °C (because it must be colder than the air to absorb heat).
This matches what owners see during winter: coils often frost at –5 to –15 °C saturation.
Hitachi Yutaki units predict defrost requirements by a combination of:
1. Outdoor coil temperature sensor
2. Ambient outdoor temperature sensor
3. Refrigerant pressure sensor
4. Runtime / algorithmic prediction
Defrost begins when both the coil temp and calculated saturation temperature indicate that the coil is at or below freezing and the system sees an expected reduction in heat-extraction efficiency.
This means the unit will sometimes enter defrost before you see thick ice, because it's detecting the early film of frost that you can’t see.
Posted by: @iaackFor an air-source heat pump the minimum evaporating temperature depends on the compressor design and the manufacturer’s operating envelope.
Typical minimum evaporator (saturation) temperature for R32 heat pumps
–25 °C to –30 °C which is common for modern domestic R32 ASHPs.
Note, some manufacturers restrict operation to –20 °C for efficiency and reliability reasons (reduced thermal stress).
High-performance “cold-climate” units may reach –35 °C, but these are less common in the UK/EU market.
Why the limit exists
At very low evaporating temperatures:
Suction pressure drops very low (R32 saturation pressure at –25 °C ≈ 1.7 bar abs).
Mass flow and capacity reduce sharply.
Risk of liquid floodback to the compressor during defrost increases.
Compressor discharge temperature rises significantly.
Most manufacturers provide an operating envelope showing safe combinations of suction (evaporating) and discharge (condensing) temperatures.
Rule of thumb
If the outdoor air temperature is –10 °C, the evaporator surface will usually sit around –15 to –20 °C (because it must be colder than the air to absorb heat).
This matches what owners see during winter: coils often frost at –5 to –15 °C saturation.
Hitachi Yutaki units predict defrost requirements by a combination of:
1. Outdoor coil temperature sensor
2. Ambient outdoor temperature sensor
3. Refrigerant pressure sensor
4. Runtime / algorithmic prediction
Defrost begins when both the coil temp and calculated saturation temperature indicate that the coil is at or below freezing and the system sees an expected reduction in heat-extraction efficiency.
This means the unit will sometimes enter defrost before you see thick ice, because it's detecting the early film of frost that you can’t see.
Thank you for the reply. I think you are saying that what I am seeing is normal (Evaporator -23C. OAT -4C. Defrost cycle every 46 minutes).
2024 build bungalow, Southern England, 179 m2, 14w/m2
Underfloor heating, fully open
Vaillant aroTHERM plus 3.5kW
50 litre volumiser
3.6KW solar panels
Tesla 13.5kw Powerwall
@trebor12345 Yes, expect defrost cycles to initiate at evaporator temperatures between -20 and -35 degC depending on refrigerant gas, plant design and application.
The cycle time is dependent more on environmental conditions, heat extraction rates (how hard the compressor is working) and forced airflow rates to the evaporator.
If you imagine a heat pump where the airflow to the evaporator is restricted in some way (caused by poor clearances between surrounding walls, evaporator fan not attaining the correct speed due to incorrect factory setup or maybe the early failure of the evaporator fan bearings) then the defrost cycle would still occur at the expected temperatures but the period between cycles would definitely decrease.
Referring now to your other post on this forum, the ice buildup on your unit does, in my experience, seem a little heavier than I would expect. Hopefully others will contradict me!
- 27 Forums
- 2,750 Topics
- 64.7 K Posts
- 1,746 Online
- 7,158 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
Hi, sorry that I have been absent for a while. I'd like...
By baroquebank , 32 minutes ago
-
RE: To re-pipe or not to re-pipe? Moving from oil boiler to air source heat pump.
@penval, really useful update. After all the discussion...
By Mars , 4 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@papahuhu I prefer to look at it simplistically. We d...
By Old_Scientist , 1 day ago
-
RE: How Accurate Is My DIY Heat Loss Calculation?
D'oh - of course. I shouldn't post before my brain is f...
By Old_Scientist , 1 day ago
-
RE: Questions about A2A for heating as well as cooling
@rob-of-york I would concur with the underfloor insulat...
By Toodles , 1 day ago
-
RE: New Vaillant Arotherm controls link to existing thermostats ; wired vs wireless
Nothing attached! I have rads but UFH makes the case ...
By JamesPa , 1 day ago
-
RE: Cooling with air to water heat pumps
Passive cooling should always be the first call. Keep ...
By JamesPa , 1 day ago
-
RE: Do I add Air Con or MVHR to existing A2W ASHP?
@rob-of-york Thank you, I’m thinking along these same l...
By Toodles , 2 days ago
-
@Mars Good questions! The downstairs unit did the maj...
By Rob of York , 2 days ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@dave, I think @jamespa has probably identified the mos...
By Mars , 3 days ago
-
RE: Plug and play solar. Thoughts?
My thought is simple. Bring it on and bring on plug in...
By JamesPa , 3 days ago
-
RE: Heat Geek mini store vs pump size
Yes I agree, that’s why Heat Geek have most likely sele...
By Tomtheheatingengineer , 4 days ago
-
@tomtheheatingengineer, thank you, and welcome to the f...
By Mars , 4 days ago
-
RE: Is the "divide by 2900" rule still valid?
Really flow rate is a pipework limitation not a water p...
By JamesPa , 5 days ago