Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Evaporator Temperature
Interested in hearing from others on their Heat Pump evaporator temperature just prior to a defrost. A few other bits of data might be useful. My details are:
Evaporator -23C. OAT -4C. Defrost cycle every 46 minutes. Southern England.
2024 build bungalow, Southern England, 179 m2, 12w/m2
Underfloor heating, fully open
Vaillant aroTHERM plus 3.5kW
50 litre volumiser
3.6KW solar panels
Tesla 13.5kw Powerwall 3
For an air-source heat pump the minimum evaporating temperature depends on the compressor design and the manufacturer’s operating envelope.
Typical minimum evaporator (saturation) temperature for R32 heat pumps
–25 °C to –30 °C which is common for modern domestic R32 ASHPs.
Note, some manufacturers restrict operation to –20 °C for efficiency and reliability reasons (reduced thermal stress).
High-performance “cold-climate” units may reach –35 °C, but these are less common in the UK/EU market.
Why the limit exists
At very low evaporating temperatures:
Suction pressure drops very low (R32 saturation pressure at –25 °C ≈ 1.7 bar abs).
Mass flow and capacity reduce sharply.
Risk of liquid floodback to the compressor during defrost increases.
Compressor discharge temperature rises significantly.
Most manufacturers provide an operating envelope showing safe combinations of suction (evaporating) and discharge (condensing) temperatures.
Rule of thumb
If the outdoor air temperature is –10 °C, the evaporator surface will usually sit around –15 to –20 °C (because it must be colder than the air to absorb heat).
This matches what owners see during winter: coils often frost at –5 to –15 °C saturation.
Hitachi Yutaki units predict defrost requirements by a combination of:
1. Outdoor coil temperature sensor
2. Ambient outdoor temperature sensor
3. Refrigerant pressure sensor
4. Runtime / algorithmic prediction
Defrost begins when both the coil temp and calculated saturation temperature indicate that the coil is at or below freezing and the system sees an expected reduction in heat-extraction efficiency.
This means the unit will sometimes enter defrost before you see thick ice, because it's detecting the early film of frost that you can’t see.
Posted by: @iaackFor an air-source heat pump the minimum evaporating temperature depends on the compressor design and the manufacturer’s operating envelope.
Typical minimum evaporator (saturation) temperature for R32 heat pumps
–25 °C to –30 °C which is common for modern domestic R32 ASHPs.
Note, some manufacturers restrict operation to –20 °C for efficiency and reliability reasons (reduced thermal stress).
High-performance “cold-climate” units may reach –35 °C, but these are less common in the UK/EU market.
Why the limit exists
At very low evaporating temperatures:
Suction pressure drops very low (R32 saturation pressure at –25 °C ≈ 1.7 bar abs).
Mass flow and capacity reduce sharply.
Risk of liquid floodback to the compressor during defrost increases.
Compressor discharge temperature rises significantly.
Most manufacturers provide an operating envelope showing safe combinations of suction (evaporating) and discharge (condensing) temperatures.
Rule of thumb
If the outdoor air temperature is –10 °C, the evaporator surface will usually sit around –15 to –20 °C (because it must be colder than the air to absorb heat).
This matches what owners see during winter: coils often frost at –5 to –15 °C saturation.
Hitachi Yutaki units predict defrost requirements by a combination of:
1. Outdoor coil temperature sensor
2. Ambient outdoor temperature sensor
3. Refrigerant pressure sensor
4. Runtime / algorithmic prediction
Defrost begins when both the coil temp and calculated saturation temperature indicate that the coil is at or below freezing and the system sees an expected reduction in heat-extraction efficiency.
This means the unit will sometimes enter defrost before you see thick ice, because it's detecting the early film of frost that you can’t see.
Thank you for the reply. I think you are saying that what I am seeing is normal (Evaporator -23C. OAT -4C. Defrost cycle every 46 minutes).
2024 build bungalow, Southern England, 179 m2, 12w/m2
Underfloor heating, fully open
Vaillant aroTHERM plus 3.5kW
50 litre volumiser
3.6KW solar panels
Tesla 13.5kw Powerwall 3
@trebor12345 Yes, expect defrost cycles to initiate at evaporator temperatures between -20 and -35 degC depending on refrigerant gas, plant design and application.
The cycle time is dependent more on environmental conditions, heat extraction rates (how hard the compressor is working) and forced airflow rates to the evaporator.
If you imagine a heat pump where the airflow to the evaporator is restricted in some way (caused by poor clearances between surrounding walls, evaporator fan not attaining the correct speed due to incorrect factory setup or maybe the early failure of the evaporator fan bearings) then the defrost cycle would still occur at the expected temperatures but the period between cycles would definitely decrease.
Referring now to your other post on this forum, the ice buildup on your unit does, in my experience, seem a little heavier than I would expect. Hopefully others will contradict me!
- 27 Forums
- 2,772 Topics
- 65.3 K Posts
- 2,071 Online
- 7,174 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
The positive reviews keep coming in for Britain's Heat ...
By Mars , 8 hours ago
-
RE: Next steps on my ASHP journey: Radiators and Pipework
I have one of these fitted which also allows you to reg...
By Old_Scientist , 12 hours ago
-
RE: Recommendations in Ely (Cambs) area for Full setup checks on Nibe HP setup for House.
If they can't don't give up. Heat pumps are, in reali...
By JamesPa , 1 day ago
-
RE: Starting Our Heat Pump Journey: 1962 build 3 bed detached house
@ian-s I wouldn't be too concerned about the design ...
By Rob of York , 1 day ago
-
RE: Missing flow temperature in Heat Geek proposal
Yes that's what would happen by turning down the lsv to...
By JamesPa , 2 days ago
-
RE: Grant R290 DHW Cycle Interuption
It looks like some sort of short pre-run. The question...
By JamesPa , 2 days ago
-
RE: Cascade System or larger single unit
@renewables345 I would say if it a new build it’s no mo...
By Aventus Eco , 2 days ago
-
RE: Why are ASHP installs so expensive?
Posted by: @batpred There´s another aspect that coul...
By Rob of York , 2 days ago
-
RE: Say hello and introduce yourself
@gz00, welcome to the forums. There’s a huge amount of ...
By Mars , 2 days ago
-
RE: Home energy storage & battery register
1 fox ess lv5200 batteries, plus 2 more waiting to be i...
By Jimcub , 2 days ago
-
RE: Heat Pump deployment statistics: June 2026
@l8again Unfortunately the government is, I suspect,...
By JamesPa , 2 days ago
-
My feed of random industrial auctions turned up this au...
By Prunus , 2 days ago
-
We’ve just passed 20 million forum views! 🎉
It's official. The Renewable Heating Hub forums have of...
By Mars , 4 days ago
-
RE: Who's your electricity provider and what's your tariff?
@batpred When the raw material input has increased in c...
By Papahuhu , 5 days ago
Members Online
No online members at the moment