@davidnolan22 - Screenshot of energy input/output attached.
System was commissioned on 8th April.
Note: value for 16th is significantly higher since for some unknown reason MELCloud didn't bother to give a value for the 15th and just included it in the values for the 16th. This is the same in both MELCloud and MELpumped.com (which I suppose just uses the same data).
Your point on lack of cycling is exactly what I was thinking too. Of course it would be better if I could get more heat transferred out of the system through those larger rads and after a visit from the installer (flush/balancing)/a bit of my own tinkering this summer hopefully I will get the troublesome few rads sorted but it's not like it's causing cycling at the moment so I can't believe it's the main factor negatively affecting efficiency.
Mitsubishi Ecodan 8.5kW installed April 2025 + hopefully soon getting 3.6kWp solar PV
@CBrenewable @ashp-bobba seems to be on the case so I will step out for now to avoid possible confusion, name check me if you want me to step back in/it is not solved.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@cbrenewable Can you look on the side of the pump body, should be an arrow showing direction? please have a look at both pumps if you can, TBH even if they are both the correct way if one passes through the other when only needing DHW or heating or 2 are pumping together you are likely looking at one of the main issues.
All you needed and nearly all off these system ever need is a simple Y plan circuit with one pump capable of the power needed for the index circuit and your suppler should always be qualified and know what to do to work these things out as its very basic maths and basic heating eng stuff.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@ashp-bobba Thanks. I've checked the arrows and confirm both point in the correct direction.
I note your concern over whether both are needed. Assuming for a minute that they are both needed, in what scenario would you expect both to be on and working?
I've run the DHW and Heating just now to see which come on and when. My findings:
DHW: Only Flow pump active (I didn't notice the mode). No lights on return pump so assuming it's not active.
Heating: Both pumps active. Flow pump operating in Mode II and Return pump operating in Mode III.
I found a copy of the itemised delivery list from one of the the installer's suppliers and have identified the pumps as: https://theufhgroup.co.uk/products/bastion-a-rated-circulation-pump-6-metre-head-inc-cable-zl-3002-25-6
I also found this data sheet that gives some info on modes but I'm not totally sure how to interpret it: https://theufhgroup.co.uk/cdn/shop/files/ZL-3002.pdf?v=184044485459458873
I had a look at the data sheet but wasn't really able to understand why one pump is in II and another is in III mode. Someone else who knows more than I may have more luck.
Mitsubishi Ecodan 8.5kW installed April 2025 + hopefully soon getting 3.6kWp solar PV
@cbrenewable Lets get to the modes and setting a bit later, sorry to ask but I need to make sure I understand the circuit that has been made. can you confirm the attached arrows on your picture is how the circuits are configured to flow and confirm the below?
DHW: Only Flow pump active (I didn't notice the mode). No lights on return pump so assuming it's not active. (pump you describe is pump 1 on the annotation and pump 2 does not run?)
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
To add red circuit is DHW and blue is heating
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Mitsubishi Ecodan 8.5kW installed April 2025 + hopefully soon getting 3.6kWp solar PV
So if I understand it correct while in DHW mode, the main ASHP pump (1) has to go through the DHW circuit in the cylinder and then pull through the non operating heating return pump (this is not correct and will cause a lot of restriction on that line), I have attached an annotation showing the change the pipe at the bottom in red so the water does not need to go through that pump that is off if your contractor feels they need to keep the second pump.
I have also attached another annotation as an option showing the pump No2 to be removed and then the circuit would resemble something of an S Plan, if the 1 circulation pump is not enough to overcome 6m head for the index circuit you can get more powerful pumps.
ASHP are super sensitive to hydronic balancing to have a return boost pump like this you would need balancing valves and I hate to say in this case if there is no possible way to reach the desired pressure use a Buffer and separate the circuits. To me what you have is a system with a buffer set up and someone just removed the buffer part but now you have uncontrolled flow and pumps in the way of each other set at different rates.
Best system simple Y plan 1 pump index circuit head calculated, balanced circuits and let the Mitsubishi control everything.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Posted by: @ashp-bobbaTo me what you have is a system with a buffer set up and someone just removed the buffer part but now you have uncontrolled flow and pumps in the way of each other set at different rates.
... presumably because the customer (very sensibly) said that they didn't want a buffer!
Why do heat pump installers persist in making things complicated?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa Hi James, I don't know but I have 2 more in my area to look at next week after Easter. There seems to be this issue sometimes.
CB, I think perhaps ask them kindly what they think about designing to run on one pump, perhaps get their perspective, I do think you have a mixed bag of smaller issues perhaps causing this lower efficiency. I think the pump conflicts, balancing of the DT on the rads and the bypass are likely causing some of this. Please remember we are diagnosing from pictures on a forum so this is advice for a way to approach the issue. We engineers carry several very expensive commissioning tools that help us test and commission these systems to standards you are looking for.
I hope my advice at least points you in the right direction.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
-
Mitsubishi Ecodan 11kw Defrosting Issue.
1 month ago
-
Have Consumers Been Lied to About the Efficiency of Heat Pumps Made in China?
3 months ago
-
Ecodan consuming 100kwh per day in new build!!!
3 months ago
-
Help with understanding my Mitsubishi Ecodan air source heat pump
6 months ago
-
Ecodan 11.2kw Wireless thermostat drop outs
6 months ago
- 26 Forums
- 2,228 Topics
- 49.5 K Posts
- 241 Online
- 5,890 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Twin 10kw Grant Aerona Volumiser Tanks using lots of power
The Grant Aerona3 external volumisers are insulated uni...
By Grantmethestrength , 15 minutes ago
-
RE: How good is the app support for your heat pump?
The Bluetooth signal does not reach due to the distance...
By Batpred , 23 minutes ago
-
Samung 16kw 5 months in - Happy with heat and DHW but some questions
Where to start? In brief we are happy with the system...
By DowallyDrifter , 2 hours ago
-
Question about Heating Pump Operation mode – Ecodan FTC6 v20.06
I have a Mitsubishi Ecodan EHST20D-YM9D with PUHZ-SWM80...
By Johj45 , 2 hours ago
-
RE: Electricity price predictions
Currently we are a net importer of electricity, and one...
By Jeff , 2 hours ago
-
RE: Replacing knackered oil boiler with ASHP - Perthshire
@jamespa just confirming that after 5months with the 16...
By DowallyDrifter , 3 hours ago
-
RE: Struggling to get above 3.3 on heating
The first chart in your post above shows average 0.25kW...
By JamesPa , 3 hours ago
-
RE: How to increase DHW water temperature on Samsung Gen 6 Control Panel
Im just in the process of connecting up my mixergy cyli...
By bontwoody , 10 hours ago
-
Unless anyone can tell me differently, there appears to...
By DowallyDrifter , 12 hours ago
-
RE: Should Our Water Circulation Pump Be Configured to Run All The Time?
I run my Vaillant on either expanded mode (either end o...
By JamesPa , 15 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
on a facebook thread someone has comented to the effect...
By AdamK , 24 hours ago
-
-
RE: Samsung Heat Pump – Can't Activate TW2 Pipe Sensor (for Delta T Control)
Wanted to add an update. As I am running HomeAssistan...
By bubuontheweb , 1 day ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
You are correct you dont need the second pump if there ...
By JamesPa , 1 day ago
-
RE: New Fogstar 15.5kWh upright solution
From my experience with inverters from different Far Ea...
By Transparent , 1 day ago
-
@bontwoody Thank goodness you are ‘back on-line’ so to ...
By Toodles , 1 day ago
-
RE: Automation options to maximuse efficiency & ToU tariffs
@majordennisbloodnok Seems reasonable. It would be m...
By Batpred , 1 day ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
@hcas OK Thanks. Will do.
By bontwoody , 1 day ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
@transparent Thank you for a very comprehensive, tim...
By Batpred , 1 day ago
-
RE: Isolating the system for a planned power cut
@transparent 😊 I may have lost you there.. I ...
By Batpred , 1 day ago