Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Gen 6 Samsung ASHP losing 20C of DHW in 60 min directly after generation
Hi all - I have a Gen6 Samsung ASHP linked to a thermal store. Stratification is (has) supposed to keep the top for DHW. My temperature sensor for DHW is in the top most slot of the thermal store.
Over the past 2 months, I've had DHW generation set to 50C. As you can see in the attached graph, I am losing 10C within 30 min and then another 10C over the hour. It seems to me that my stratification is collapsed, as the temperature is being pulled down very rapidly to my central heating target. And our radiators get much warmer during the DHW generation.
We have an over-engineered system with a pump each on the flow and return (EMBRASS Peerless) and I've reduced these to speed II, with improved central heating performance (I think) but no change to the DHW issue.
Thanks for any insights.
Couple of questions and a thought:
I cant actually work out in the plot which line is the DHW temperature and which the heat pump flow temperature. Can you clarify.
To respond to your stated position:
Has anything else changed in the DHW system?
I presume it (including surrounding pipes) is well insulated/insulation hasnt changed
Is it possible the diverter valve is slightly stuck, leaking some (cooler) water at space heating temperature through to the coil. That could account for it.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa - thanks for the reply.
You've made me look at these traces more carefully. The green trace is what I've been looking at and it's the heat pump heating flow temperature. It can't be the tank temperature as it gets to 50 in 3 min!
The DHW temperature is missing and should be a blue trace labelled as "hot water flow temperature". I think.
This suggests that we may have an issue with the sensor... I'll work on that, and look for any issues with diverters too.
Posted by: @andbeck@jamespa - thanks for the reply.
You've made me look at these traces more carefully. The green trace is what I've been looking at and it's the heat pump heating flow temperature. It can't be the tank temperature as it gets to 50 in 3 min!
The DHW temperature is missing and should be a blue trace labelled as "hot water flow temperature". I think.
This suggests that we may have an issue with the sensor... I'll work on that, and look for any issues with diverters too.
That was what confused me! The heat pump FT is doing what you would expect.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Shouldn’t your temp sensor be in the middle or lowest sensor pocket? Otherwise you’re not actually heating up much volume of water before the DHW temp sensor get to target and turns off, thus not actually much heat stored. My tank a 200L telford has two pockets one at the top and one around half to two thirds down the tank that is the one I use.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
@ecobaker Thanks for this. I've had it in both slots. Currently in the top as in the middle it takes much longer and disrupts the heating more - again, I've been managing a temperature loss problem and probably need to replace the sensor.
I can't seem to figure out whether the sensor is a bog standard PT 1000 for this situation... do you know?
-
Should I make my radiators smaller?
2 years ago
-
ÀSHP heat loss - how close to perfect can we get?
2 years ago
-
Help needed with Grant Aerona ASHP
3 years ago
- 27 Forums
- 2,819 Topics
- 66.8 K Posts
- 1,519 Online
- 7,232 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
@davec 47kwh for 3 days is very low, compared to what I...
By johnd , 5 minutes ago
-
RE: Buffer tank on a 2 x 14kw Ecodan system
The pool heat exchanger looks like one of thes...
By Singlespeed , 10 minutes ago
-
RE: How quickly would you want/expect heat recovery to take from setback?
Actually, good point. Yesterday was sunny for a good c...
By AndrewJ , 17 minutes ago
-
I opted to buy sets of 16 bare LiFePO₄ cells and place ...
By Transparent , 41 minutes ago
-
RE: Why don't people choose heat pumps?
This topic is straying into useful observations about t...
By Transparent , 3 hours ago
-
RE: Load Shift and Lifestyle Shift Complete - our journey has ended, for now
This opening sentence stopped my reading right at the s...
By QdsdHxJX9PFLfi7 , 4 hours ago
-
RE: Our 10 year old Grant heat pump failed
As I understand it it was working then stopped. More l...
By JamesPa , 4 hours ago
-
@pipcart, Wattson is back... please go to the homepage ...
By Mars , 5 hours ago
-
Do heat pump defrost cycles impair heat pump efficiency (COP values)?
The short answer is no, as far as I can see from data f...
By cathodeRay , 5 hours ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That is a good approach and an excellent result. For co...
By Judith , 23 hours ago
-
RE: Say hello and introduce yourself
Good to see you here, @claytonbrowne, and welcome to th...
By Mars , 1 day ago
-
RE: Issues with Samsung heat pump – high running costs and house dropping to 11C overnight
It looks very much like a radiator balancing i...
By hml1827 , 2 days ago
-
I have, @transparent, but chose to pose the question he...
By Majordennisbloodnok , 2 days ago