Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Effect of buffer tank or volumiser on heat pump system
Can someone please either confirm or put me right on the following:
My understanding is that a buffer tank will introduce mixing of flow and return water in a system and causes its overall efficiency to reduce as a higher flow temeperature is needed.
Do volumisers have the same effect? as an installer is telling my brother in law that it wont effect the efficiency and is there as a safe guard for the defrost cycle.
I also thought that if you add up the volume of the radiators and pipes you could then say whether a volumiser was needed or not.
Thanks in advance.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
10kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
You are basically correct in what you state.
A buffer tank may cause lower efficiency due to mixing unless the water flowrate both in and out is kept balanced.
A volumiser vessel, as the name suggests, just adds volume to the system. If you look in the heat pump manual it should state the minimum required volume for the system. If the heat emitters and pipework do not provide sufficient volume then a volume vessel would be required.
I suppose it also depends where the volumiser is located, since it will lose some thermal energy, which could add to the overall energy loss if located outside the buildings thermal envelope.
There will also be added cost.
@derek-m Thanks Derek. Apart from the cost issue, would you say it was better not to have a internal volumiser if there were sufficient volume of circulating water in the radiators or is cost the only downsize?
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
10kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoody@derek-m Thanks Derek. Apart from the cost issue, would you say it was better not to have a internal volumiser if there were sufficient volume of circulating water in the radiators or is cost the only downsize?
I don't know if anyone has actually performed any tests to see if having extra water volume within the system, could improve the defrost cycle. I suppose a further possible downside would be if the system contains anti-freeze, since more anti-freeze would also increase costs.
As far as I am aware, LLH's perform like a very thin buffer tank. How many water pumps are installed in your system?
Unless the flow rate of each water pump is matched, then there could be mixing occurring within the LLH.
Probably the easiest way to optimise the system operation, would be to try to ensure that the primary water pump (the one at the heat pump side), is always supplying slightly more water flow than the secondary water pump.
@bontwoody I went with an inline volumiser. All you say is correct, it cannot detract anything from efficiency, whereas a buffer or LLH always does - you can only seek to minimise that inefficiency with 1ary/2ary side flow rate balancing but you'll never get to zero loss.
I believe tests have been done that show that the effect defrost with a volumiser can be a bit better because there is that higher volume of hot water circulating. I have the volumiser on the flow side of the CH circuit, between the HP and the rads, inside the house in the airing cupboard. my reasoning for this is that it stores water at the LWT when the HP shuts down, meaning that at the next startup there's 50L of water already in the circuit at the last LWT, which I think smooths startup a little bit. and any heat loss is into the house.
the main reason to have one though is if your system volume is too low . I was just over the min but decided to add one to be sure (and I wasn't sure about which TRV's I'd keep at the time either), no real downside other than buying it / fitting it / finding room for it .
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
I found this by Graham Hendra which is interesting around the siting of a volumiser.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
10kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody yes thats one of the ones I read when making my decisions.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Apologies for re-introducing this topic. I was persuaded by contributers on this forum, that I should remove the second CH pump and change the function of the buffer tank to use it as a volumiser.
I have forgotten how it was suggested that I should use the four connections on the tank in this configuration.
Existing connections are LHS: Top - From ASHP; Bottom - Return to ASHP RHS Top- To CH: Bottom - Return from CH
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 12kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
- 27 Forums
- 2,820 Topics
- 66.9 K Posts
- 3,130 Online
- 7,232 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
-
RE: Why don't people choose heat pumps?
By the same measure we should be insisting that all gas...
By Batpred , 2 hours ago
-
RE: How quickly would you want/expect heat recovery to take from setback?
True but .. because the room is colder dt rad to room i...
By JamesPa , 2 hours ago
-
Got two or three heat pump quotes that don’t agree? Post them here.
One of the biggest sources of confusion I see on Renewa...
By Mars , 2 hours ago
-
RE: Load Shift and Lifestyle Shift Complete - our journey has ended, for now
I do not disagree with the concept of wanting to live a...
By Batpred , 2 hours ago
-
RE: Buffer tank on a 2 x 14kw Ecodan system
@singlespeed I am going to put a temperature sensor on ...
By fosterl2 , 4 hours ago
-
RE: Grant Aerona - Weather Compensation and Schedules
@taffonthetaff Yes, I have now gotten to the bottom of ...
By bontwoody , 5 hours ago
-
RE: Grant R290 DHW Cycle Interuption
Occasionally our Grant R290 activates all three circuit...
By TaffontheTaff , 5 hours ago
-
RE: Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
@davec 47kwh for 3 days is very low, compared to what I...
By johnd , 7 hours ago
-
RE: Our 10 year old Grant heat pump failed
As I understand it it was working then stopped. More l...
By JamesPa , 11 hours ago
-
@pipcart, Wattson is back... please go to the homepage ...
By Mars , 11 hours ago
-
Do heat pump defrost cycles impair heat pump efficiency (COP values)?
The short answer is no, as far as I can see from data f...
By cathodeRay , 11 hours ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That is a good approach and an excellent result. For co...
By Judith , 1 day ago