I know you are getting lots of god advice but our situation was similar and we found one other thing….(we put in ASHP on Jan 6th this year having run out of LPG 3 days earlier - into a freezing house! - it took a lot of energy to warm up the house)
but one of our issues was a sticky UFH actuator. Even though the actuator was open, water was not flowing through that circuit so that part of the house was cold. You say your house had been largely unoccupied before you moved in? Your UFH valves could be stuck closed?
if this is happening then the Ecodan (to protect itself from damage) will not force fluid if it can’t push and the heat it generates gets diverted back to the heat pump (ie outside).
it’s worth checking your UFH flow pipes - they should be warm. If not they are likely seized. To unseize you usually just need to rotate the valve anti-clockwise ( with a radiator key under the actuator head) a little and you should hear an inrush of water..
(No don’t overdo the rotation! You don’t want the water coming out of the manifold!)
im just a newbie myself and you may not have this problem - but it is worth a check I think?
Gonna challenge a few things here...here’s their take on what’s going on.Posted by: @editor
I'm not sure those correlate. The system can be set to use 'flow temp' mode (Mitsubishi speak for fixed flow temperature) and it could be set to somewhere between 45 and 55C but likely if the installer did set that, it seems most tend to use 50.Your system includes a low-loss header and third-party thermostats, which are likely set to a fixed flow temperature of 45–55°C.
It's not, however, as if you look at the main remote controller screen you'll see the triangle indicating compensation curve is in use:
That's actually the temperature of the water in the cylinder. As mentioned in the OPs earlier post ( https://renewableheatinghub.co.uk/forums/postid/42714), the flow temp has been at 29 and return at 27 (via comp curve).The installer noted that your flow temperature is currently set to 47°C
Worth checking what the unit thinks it's using - from the front screen:
press the bottom right button (called the 'option' button), you'll see
press the energy monitor button (the magnifying glass bottom right)
have a look at / share the Consumed and Delivered figures?
To follow on from the above post, you may wish to check all your UFH loops are open sufficiently - assuming the valve controls are in good condition, make a list of them then record how many 'half turns' it takes to close each one (so you can put it back again if necessary), then close each one in turn and open back up to 1L/m flow (or two full turns if there are no guages) and leave for 4 - 12 hours. For rooms that get too hot, turn down half a turn per 12/24 hours until it's comfortable then tweak up/down to get perfect temp for the room (you may have to adjust other rooms' valves to compensate). There are more advanced ways of balancing UFH but this should give you a 'quick' indication if that was the issue / get you 80% there.
Lots of ideas above about what could be causing your issues. Nobody, including me, can be definitive because we don't have your system in front of us.
Can I suggest you now do a bit of 'elimination' to see which ones to pursue further and which can be rejected based on observations on the actual system?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@anca1808 a few thoughts re your high kWh usage:
1 are there any unlabelled breakers in your consumer unit that could be using power?
2 in fact, are all the breakers labelled with the circuits they protect?
3 do you have a steep driveway fitted with underground deicing cables? I have these and they draw c4kW when activated. I switch mine manually but some are fitted with a thermostat that switches them when icy conditions are likely and this may be faulty.
Mitsubishi Zubadan 14kW with Mixergy 210l DHW in 220m2 barn property. 24 solar panels = 9kWp with GivEnergy 5.0kW Hybrid inverter and 19kWh GivE batteries. Jaga Strada fan-assisted rads throughout. Landvac vacuum glazing/triple glazed windows.
@anca1808 I'd certainly backup the suggestion from @rhh2348 to check the consumption as measured by the unit - I know it is the main culprit in your high usage figures but it is worth checking to make sure there is not another less obvious draw.
Flow temps in the low thirties are not going produce radiators that feel warm to the touch - they'll be below body temperature after all - and 19.5° suggests the rooms upstairs are being heated, adequately, even if not to your desired level.
It is good that you have a Mitsi engineer booked. I suspect that the fact you say there has been a three year gap between installation of the pump and occupation of the house could be a significant factor - it is a mechanical device filled with water, both of which will suffer/cause degradation if they sit unused. I hope that your system included anti-freeze as that has an anti-corrosion additive.
Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV
Hi all,
Just a small update between crying babies and daily struggles of moving...My partner was away until tonight so once he is back we will start troubleshooting as per above advices.
To answer some of the questions. This is an empty house. We have no electric car, no big consumers, not even a washing machine as this has not arrived. We only had time to move essentials last weekend.We did use kettle, oven and microwave. Hence why I was so panicked that with a virtually empty house, 100Kwh was enormous and unexplainable. So whatever was showing on our house smart meter, I assumed it was the heat pump.
The pipes from outside all the way to the house are now insulated.
I also changed the DHW to heat up 3 times a day for 1 h when I have a very good tarrif on Octapus Cosy.
The garage is not warm to say the hear is kept in there .
Plumber who did insulation friday said the immersion is not on all the time and that is not the culprit. I really did not check that myself if it is on or nor
@JamesPa I will try the pump off pump on and measure things this week.
@Gary. Yes I have read the manual and settings look alright ( as far as my uneducated eyefor heat pumps) . The pump was running at 5 like you notices so I dialled down to 2 and now with the code 540 it shows 13l/min, which i guess it s satisfactory. And yes I wull order that wifi thing off amazon once i have my interner set up end of week. I can get on melcloud then and share more data.
@JohnR. I am no expert and I know the numbers are not making anysense. Yes, I bled all radiators, but like many explained, the radiators will not get hot with the heat pump. There is an issue of hetting heating upstairs for some reason
For the last 2 days my consume went down to 47kwh per day for whole house, which I am mildly happier about ( I assume the house has now wormed up and this is the real consume, maybe insulation helped a bit) . But still the upstairs does not heat up pass 20 degrees with all Trv open and stat put high.
It is still not right in my opinion as consume is still too high and for the upstairs not to get to my wanted temperature , so the developer got in touch with mitsubishi and a specialist will come ( don t have date yet) . I will ask him to service it and check all system. I ll ask to show me as well if all ufh are open how much etc. I do not want to do it by myself as it is a bit too much if something goes wrong and i flood the house.
@rhh2348 Yes, I checked the consumed and delivered. It was turned on on 13th of february as on 14th we completed the purchase. since then until today 23rd it has consumed 791 and delivered 1700. In january it was turned on a few days ( don t know how many) to check if it is working in preparation for our move feb/march. in those few days it consumed 728 as per the log.
@downdlfield. No cables that I know of. I will go around to see if everything is labelled.
Like I said, I am a bit out of my depth with all of this. We will start troubleshooting from tomorrow until mitsubishi comes out and hopefully reduce our consume so i do not take a second mortgage for my energy bill .. .
I will let you know how it goes and what the specilist says when he comes.
Thank you all for the help, support and advices!!
Posted by: @anca1808It was turned on on 13th of february as on 14th we completed the purchase. since then until today 23rd it has consumed 791 and delivered 1700. In january it was turned on a few days ( don t know how many) to check if it is working in preparation for our move feb/march. in those few days it consumed 728 as per the log.
That consumption data is consistent with the high smart meter readings but is way too high for an efficient heat pump system. Similarly, 791kWh consumed to deliver 1,700kWh of heat indicates very poor performance and something is preventing the heat pump from runing efficiently. For comparison, since 1st January my Vaillant heat pump claims to have consumed nearly 850kWh of electricity but has delivered just over 4,500kWh of heat. By good luck or judgement I seem to have got an efficient system.
I suspect that your system hasn't enjoyed sitting idle for 3 years since commissioning.
@anca1808 Just to give you some comfort and set expectations, my Vaillant heat pump is working out 13% cheaper than gas on a like for like basis, over the period November 2024-date (which is the worst period for heat pumps!). I haven't done anything clever, just operated it open loop on pure WC with the WC adjusted down to the lowest it will go consistent with the house being warm. I do have a ToU electricity tarrif, without this it would be about on a par with gas.
Please feel free to post back after Mitsubishi have visited and ask any further questions, you should not be experiencing such high consumption.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
It sounds like you are getting to grips with it well. I just want to check, are the pressure gauges in the system showing a sensible sort of pressure? Did it drop after you bled the radiators?
Also I just wonder if the unit itself has lost some of the the refrigerant gas it is supposed to have, but i imagine that is more the job for the engineer to check.
Hi all,
There is really no update .
I have tried loads of the advice given, nothing made a real difference.
The developers plumber has come around and insulated everything. One mitsubishi engineer came and said nothing is wrong, but some pipes are heating up the garage floor and there might be some heat loss there. He was not very helpful to be honest.
Currently weather has improved, but consume is still around 20kwh/day. My upstairs never gets warmer than 19/20 although I set it at 22. So I have the same issues. As a note I did a calculation and my radiators are undersized by a smidge, so I asked that to be checked.
I kicked off yesterday at the developer because there is an issue just no one seems to find out what is what and I wanted a specialist in design of systems to be paid to come around, but he just asked for yet another mitsibishi dude to make an appearance.
I have contacted a heat geek from my area and awaiting for him to come round in a couple of weeks. He is the only one that said there are faults with the system design just by looking at pictures.
I will update the page once I have more answers....
A
Sorry to hear this is not yet fixed but please do keep posting as those here can help. At present its actually very cold at night despite the warm days so some ongoing consumption is to be expected.
Regarding upstairs the output is dependent on size and flow temperature. If you were to increase the flow temperature the upstairs rads would warm up more, but at the expense of efficiency. It may be a balancing problem, ie something throttling the flow to the rads and diverting it all through the UFH, if you have the ability to measure the temperatures either side of the rads and compare this with the flow temperatures you could ferret this out. Of course the developers should do all this for you!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
-
Mitsubishi Ecodan 11kw Defrosting Issue.
1 week ago
-
Have Consumers Been Lied to About the Efficiency of Heat Pumps Made in China?
1 month ago
-
Help with understanding my Mitsubishi Ecodan air source heat pump
5 months ago
-
Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
5 months ago
-
Ecodan 11.2kw Wireless thermostat drop outs
5 months ago
Currently viewing this topic 1 guest.
- 26 Forums
- 2,171 Topics
- 47.8 K Posts
- 34 Online
- 5,744 Members
Podcast Picks
Latest Posts
-
WC curve best discovered by experiment anyway as any lo...
By JamesPa , 2 hours ago
-
RE: Big Changes Coming to Our Heat Pump System
@editor your engineer's attitude is truly horrifying. ...
By GrahamF , 19 hours ago
-
RE: How to choose Towel Rails for an ASHP
@rob-nezard yes absolutely. Here is the link and a pho...
By GrahamF , 21 hours ago
-
@mixergy Thanks for the update, I would appreciate some...
By bontwoody , 23 hours ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
Unfortunately I'm not that well connected 😂 ...
By Scalextrix , 1 day ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
It is interesting to see what our new Grant Aerona 290 ...
By GrahamF , 1 day ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I've never physically seen it, but I seem to recall som...
By cathodeRay , 1 day ago
-
@jamespa Ours is a Daikin EDLA03 8 kW and the Delta T =...
By Toodles , 1 day ago
-
RE: Midea ASHP – how to set weather compensation
I noticed that too and thought the same thing, but then...
By cathodeRay , 2 days ago
-
RE: Ya can’t win! It is S*d’s Law!
@old_scientist If IOF is still running next late spring...
By Toodles , 2 days ago
-
RE: Electricity price predictions
Those of you on Agile will do well tomorrow; there are ...
By Toodles , 2 days ago
-
RE: Who’s Caved and Switched the Heating On Already?
We've been running our Ecodan system, installed in June...
By Sheriff Fatman , 2 days ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 3 days ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 3 days ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 3 days ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 3 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 5 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 5 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 6 days ago