Ecodan circulation pump
Hi @sunandair , so if I’ve understood correctly, you believe the pump running 24/7 is ok/normal? I’m happy with that, but my only concern is why this would be the case when the outside temperature is ok, say +5, or in summer at +25? The bit I don’t get is why I need to circulate water then as the ashp will be off as room stats won’t call for heating?
it just feels odd that the circulation pump runs 24/7, although I guess the electrical consumption isn’t going to be that high?
on a separate note, please can you help me with setting up the energy consumption and produced data. It show blank at the moment per the photos I posted and I can’t work out how to get that working?
thanks in advance. Adam.
@adamba I don't believe the pump running 24/7 is either normal or desirable but I have not a clue how to stop it when there's no call for heat (CH) or DHW heating.
Someone will need to tell you how to set up consumption and production data I'm afraid. Mine was set up by the installer.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Hi @morgan , I find it a bit strange as this wasn’t the case for my old heat pump that broke beyond repair (apparently, although I think they just wanted to sell me one of their new range).
I’m not sure if we’ve just not installed correctly. Maybe the circulation pump needs to have the same ‘run’ signal as provided to the external ashp?
This would make sense to me as I would think something needs to tell the circulation pump to run (as the ashp needs to be told to run). If it’s not a wiring connection in the Mitsubishi control panel then maybe there is another setting on the keypad?
I’m past my knowledge level though!
Posted by: @adambaHi @sunandair , so if I’ve understood correctly, you believe the pump running 24/7 is ok/normal? I’m happy with that, but my only concern is why this would be the case when the outside temperature is ok, say +5, or in summer at +25? The bit I don’t get is why I need to circulate water then as the ashp will be off as room stats won’t call for heating?
it just feels odd that the circulation pump runs 24/7, although I guess the electrical consumption isn’t going to be that high?
on a separate note, please can you help me with setting up the energy consumption and produced data. It show blank at the moment per the photos I posted and I can’t work out how to get that working?
thanks in advance. Adam.
The wiring diagram I studied recently, shows the main and any auxiliary water pumps wired to the main Mitsubishi control panel. Is that the case with your system?
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Hi @derek-m , yes the circulation pump is wired to the Mitsubishi control panel, but I can’t remember which terminal. I will post a photo later of the control panel connections. If you and other could see if it’s the same as yours/normal it will be really helpful. I’ll post a couple with some commentary.
One other quick question, people keep referencing “pumps”. I only have one circulation pump - am I missing something…maybe you’re systems are all bigger?
Thanks.
Posted by: @adambaHi @derek-m , yes the circulation pump is wired to the Mitsubishi control panel, but I can’t remember which terminal. I will post a photo later of the control panel connections. If you and other could see if it’s the same as yours/normal it will be really helpful. I’ll post a couple with some commentary.
One other quick question, people keep referencing “pumps”. I only have one circulation pump - am I missing something…maybe you’re systems are all bigger?
Thanks.
You are one of the lucky ones to only have the one water pump, which would indicate that you don't have the unnecessary complexity that has been built into other systems. Having just one water pump will not only slightly reduce electricity consumption, it will also mean that you don't have a buffer tank, low loss header or plate heat exchanger installed, any of which can seriously effect overall efficiency.
Obviously, your water pump should operate whenever your heat pump is supplying the central heating or DHW, but may also run - on for a period of time after the heat pump has stopped. There are also settings to periodically run the water pump for a short period of time, even when the heat pump is stopped, to ensure that the water temperature sensors are measuring the average temperature. I will have to look at the manual, but I believe that the water pump can also be set to run continuously.
Posted by: @adambaHi @derek-m , yes the circulation pump is wired to the Mitsubishi control panel, but I can’t remember which terminal. I will post a photo later of the control panel connections. If you and other could see if it’s the same as yours/normal it will be really helpful. I’ll post a couple with some commentary.
One other quick question, people keep referencing “pumps”. I only have one circulation pump - am I missing something…maybe you’re systems are all bigger?
Thanks.
The main water pump should be wired to OUT1 on terminal block TBO.1 connections 1 & 2 as shown on page B-46 of the attached manual. I would suggest that you also check the water pump economy setting as shown on page B-70 and the freeze stat setting as mentioned on page B-72.
Posted by: @adambaHi @derek-m , yes the circulation pump is wired to the Mitsubishi control panel, but I can’t remember which terminal. I will post a photo later of the control panel connections. If you and other could see if it’s the same as yours/normal it will be really helpful. I’ll post a couple with some commentary.
One other quick question, people keep referencing “pumps”. I only have one circulation pump - am I missing something…maybe you’re systems are all bigger?
Thanks.
You obviously have failed your observancy test, since you failed to notice that I had not attached the referenced manual.
Posted by: @adambaHi @sunandair , so if I’ve understood correctly, you believe the pump running 24/7 is ok/normal?
No, that’s a slightly different slant on what I said. My point was that when you’ve resolved any problems you may have with your system you may find the most energy efficient way to operate your under floor heating is at low temperature with a continuous flow.
Posted by: @sunandairthe most energy efficient way to operate your under floor heating is at low temperature with a continuous flow
I agree that without evidence suggesting otherwise, this is probably the way to go. But this could be a moot point ...
... and likely depends on other factors If you are on economy 7 and have good thermal mass in your UFH you should get 7 hours electricity at 16p and 17 hours at 47p. The CoP needs to be 3 times better during the 17 hours (on average) to justify running it through the 17 hours as well.
Things to consider though
- the heat pump is working much harder at night and running a number of defrost cycles (right now - that should stop at some point in spring)
- there is the cost of wear and tear (which is probably higher at night - due to low outside temp and the higher flow temperatures)
- a yoyo of temperatures (maybe not good for the floor - expand/contract a lot)
- upstairs UFH does not have the same thermal mass as downstairs (can be fixed by zoning)
- option of using solar in the day, if you have it, or battery may offset the costs allowing you to be on a cheaper all day tarrif
I am still trying to work out the best option, since there are some [potential] "costs" that are not that easy to quantify.
-
Ecodan unable to hit legionella target temp - what's the consensus?
3 days ago
-
Mitsubishi Ecodan 11kw Defrosting Issue.
1 week ago
-
Ecodan consuming 100kwh per day in new build!!!
5 months ago
-
Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
8 months ago
-
Ecodan 11.2kw Wireless thermostat drop outs
8 months ago
- 26 Forums
- 2,356 Topics
- 53.4 K Posts
- 418 Online
- 6,017 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@kevh with the Cosy 6 I know it definitely goes to arou...
By HarrisonC , 8 hours ago
-
RE: Setback savings - fact or fiction?
@cathoderay yes I am familiar with SQL. Interesting num...
By RobS , 9 hours ago
-
Parsnip, Bacon & Coconut Milk Soup
First let me say, I am only a cook because I am human a...
By Toodles , 9 hours ago
-
RE: Controlling Daikin Altherma via P1P2 and Home Assistant
@weoleyric Oh Dear, I don’t think I am going to be of m...
By Toodles , 9 hours ago
-
RE: Electricity price predictions
Ben Watts posted on LinkedIn that he had updated this w...
By Judith , 15 hours ago
-
RE: The good, the bad and the not that great – my heat pump installation
Small update, Emailed and Spoke to Midea UK and they ...
By Burtis , 15 hours ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
@bash Octopus does charge for the admin. The process al...
By Batpred , 15 hours ago
-
RE: External pipework insulation
@transparent HI all The products you mention are ver...
By David Smith , 15 hours ago
-
RE: New Fogstar 15.5kWh upright solution
Issues still under investigation by Solis... Fogstar ...
By Batpred , 15 hours ago
-
RE: Who's your electricity provider and what's your tariff?
I agree, the consumer is not being properly represented...
By Batpred , 15 hours ago
-
RE: Advice on internal circulation pump noise
Thanks @mikefl - I'll maybe have a look at the lock-shi...
By jtg , 1 day ago
-
RE: Heat Pump Heats the House… But It’s Not Cosy. Emitter Changes or System Tweak?
@toodles interesting suggestion, thanks. I will try to...
By GrahamF , 1 day ago
-
RE: Mitsubishi Ecodan Auto Adaption trial to stop cycling.
The interval you talk of, i think, will be 60min for an...
By F1p , 2 days ago
-
Agree with @majordennisbloodnok on the setbacks. We hav...
By ChandyKris , 2 days ago
-
RE: Speedcomfort radiator fans
@deltona the way the links were added broke the page. A...
By Mars , 2 days ago
-
RE: Refrigerant R32, is it now banned in the EU from 1st Jan 2027 for monobloc ASHPs?
This has been delayed from what I believe to be this ye...
By dgclimatecontrol , 3 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
this is why I provided current flow temperatures in the...
By ksim , 3 days ago
-
RE: Why Millions of UK Homes Struggle With Heat Pumps
There's many homes that would be quite a disruption for...
By dgclimatecontrol , 3 days ago
-
RE: Ecodan unable to hit legionella target temp - what's the consensus?
@rhh2348 ...maybe this option is what you want? Alter...
By benson , 3 days ago