Ecodan ASHP - How to optimise my set up?
Again, thank you for another thorough post, @derek-m - will revert once I've digested / understood and prepared a cohesive, relevant response!
Mitsubishi ecodan PUZ-WM60VAA (6kW) with FTC6; third-party cylinder + pumps; LLH
That would seem logical, however do you know if the FTC (via pump speed setting) can control third party pumps, or only their own? I know the Grundfos is capable of (what I think is called) PWM but will have to double-check if the right connections exist to/on it.I believe that the FTC controller can only vary the water pump speed if the actual water pump is capable of having its speed varied. An easy way to check is change the speed setting from 1 to 5 and listen for a change in pump speed.Posted by: @derek-m
Could I therefore deduce that if I have a smaller delta T, then reducing the flow should increase that?If the flow rate is say 10 lpm and the DT is 5C, then a certain quantity of thermal energy will be transported. If the flow rate is now increased to 20 lpm then to transport the same quantity of thermal energy the DT must reduce to 2.5C.
...or on the Grundfos if the speed works in isolation. OK, thanks.If you can vary the water pump speed between 1 and 5 by means of the FTC, then it may be possible to identify the setting that produces a DT of approximately 5C when the heating demand is at a maximum.
Noted with interest. It does sound obvious when you say it that way! Will test per zone and see how mine performs. Thanks.With regard to the required flow rate through UFH as against radiators, I suspect it will depend upon the heating capacity of the UFH and radiators. If you pass 3kW of thermal energy into both radiators and UFH, and both are capable of emitting 3kW of thermal energy, then the required flow rate and subsequent DT should be approximately the same.
Mitsubishi ecodan PUZ-WM60VAA (6kW) with FTC6; third-party cylinder + pumps; LLH
Yes, reducing the flow rate should cause the DT to increase. What actually happens in practice is that say the overall flow rate is 10 lpm, and is supplying 10 radiators of equal size and each have a balanced flow of 1 lpm. If the volume of water in each radiator is 7 litres, then it will take approximately 7 minutes for the content of each radiator to be replaced with a fresh supply.
During its transition through each radiator thermal energy will be absorbed from the water by the radiator body, which in turn will emit this thermal energy to heat the air in each room. If the water is entering the radiators at 40C, during the 7 minutes transition it will start to cool as it loses thermal energy, so may exit the radiator at 35C.
If the flow rate is increased, the water passes through each radiator in a shorter period of time, so has less time to cool. Reducing the flow rate gives the water longer to cool, so the return water will be cooler, producing a larger DT.
The same quantity of thermal energy will be being transferred from the heat pump to the heat emitters, just the quantity of water being used is varying.
Coming late into this. I like the flow explanation re heat emitters. Presumably it's similar at the ashp heat exchanger ie. at lower flow rates the water in the ashp heat exchanger will have more time to be heated and reach a higher temperature. My experience is that lower flow rates cause more cycling - as higher temperatures are reached? Also do higher temperatures reduce the cop?
Posted by: @slideruleComing late into this. I like the flow explanation re heat emitters. Presumably it's similar at the ashp heat exchanger ie. at lower flow rates the water in the ashp heat exchanger will have more time to be heated and reach a higher temperature. My experience is that lower flow rates cause more cycling - as higher temperatures are reached? Also do higher temperatures reduce the cop?
The process is slightly different at the heat pump end.
The LWT is set by the controller, either a fixed value or one using WC. If the heat pump is heating the water to a set LWT of 40C and the return water from the heat emitters is 35C, the system should be balanced with a DT of 5C.
If the quantity of thermal energy being emitted by the heat emitters now reduces, the RWT will start to increase. This in turn will cause the LWT to start to increase, since the heat pump was operating to increase the water temperature by 5C.
The heat pump controller will sense this increase in LWT and will slow the compressor to try to balance thermal energy supply to thermal energy demand. This should work fine until the compressor slows to its minimum operating speed, at which point both the LWT and RWT will start to increase and the compressor will eventually be stopped on the high water temperature limit. The heat pump will now cycle.
If the system is operating in a balanced condition as described above, but the flow rate is now doubled, the heat emitters will still be emitting approximately the same quantity of thermal energy, but the RWT will start to increase. The heat pump compressor should remain operating at approximately the same speed, since it still needs to supply the same quantity of thermal energy, but because it is heating double the quantity of water, it only needs to raise the temperature by 2.5C. So the LWT should remain at 40C, but the RWT should increase to 37.5C.
Some heat pumps systems have the ability to vary the water pump speed in an attempt to maintain the DT at 5C.
To try to control the quantity of thermal energy being emitted by the heat emitters, the heat pump controller, operating in WC mode, could lower the LWT, and as described above would also cause the compressor to slow, thereby improving the overall efficiency.
As you can appreciate, there are actually several control systems all working in co-ordination to try to keep the heat pump operating in a reliable and efficient manner. This is why the system needs to be correctly installed and optimised.
Posted by: @derek-mSome heat pumps systems have the ability to vary the water pump speed in an attempt to maintain the DT at 5C.
Mine does this. The ASHP is basically never switched off it's either heating or cooling.
Circulation pump is set to run at all times, the heat pump controller changes it's speed dependant on what going on.
When compressor is off the pump runs at min speed around 0.6m³/h. On compressor start the circulation pump increases speed to about 0.92m³/h. Once target temp is reached for discharge flow and dT starts to decrease flow rate is increased to maintain to help maintain dT, gets to 1.03m³/h. Basically dT will continue decreasing until max flow temp is reached and compressor switches off.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
Hi everyone. Just got my Ecodan fitted and attempting to find out how to run it to best effect. Slowly picking stuff up on here. It would appear my installer set the system up as you would a gas CH system, ie quick blast in the morning and again in the evening. I’ve tried to level things off a bit and am playing around with WC curve, but it’s a bit tricky at the moment as it’s so mild. One thing I noticed was on my MEL cloud app it would appear my return temp is higher than my flow. I assume this is impossible and the installer has simply mixed up the thermistors. Will this affect the system performance or is it just for display purposes? Thanks
It will affect system performance as those are the main temperatures the controller will use to switch the outside unit on and off – definitely a case of getting the installer out to rectify the issue.
Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV
Posted by: @morrisnotoffOne thing I noticed was on my MEL cloud app it would appear my return temp is higher than my flow. I assume this is impossible and the installer has simply mixed up the thermistors.
As @harriup says this needs to be fixed.
Its worth noting that, later in the season, when defrost occurs, there will be short periods when return is higher than flow (because the heat pump is essentially operating in reverse). But you shouldn't be defrosting at present!
Thanks for the replies. I’ve got the installer out to remedy on Wednesday. Cheers
-
Mitsubishi EcoDan ASHP Settings not saving.
2 days ago
-
Mitsubishi Ecodan 11kw Defrosting Issue.
1 week ago
-
Is my Ecodan well installed and setup?
1 month ago
-
Ecodan DHW Settings missing
9 months ago
-
Ecodan - optimal external installation?
10 months ago
Currently viewing this topic 1 guest.
- 21 Forums
- 1,747 Topics
- 37.4 K Posts
- 60 Online
- 2,036 Members
Join Us!
Latest Posts
-
RE: The UK’s Heating Nightmare: Why Many Systems Fail Homeowners
"within a few years" is a pretty long timeframe within ...
By Transparent , 8 minutes ago
-
RE: Samsung E911 intermittent issue
@netdonkey The model number for your Samsung indicates ...
By ASHP-BOBBA , 55 minutes ago
-
RE: The good, the bad and the not that great – my heat pump installation
@dunlorn Good shout that buddy will give it a go at ...
By Burtis , 14 hours ago
-
RE: Heat Pump Books For Beginners – Bodge Buster & From Zero To Heat Pump Hero
@odd_lion I still have two copies of Bodge Buster left ...
By Mars , 22 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
@bromide Thanks for the advice, doing it once but prope...
By ChandyKris , 23 hours ago
-
RE: Agile: average import cost vs other tariffs?
@toodles 13.5kWh here, but no ASHP. 27kWh would be ampl...
By IanMK13 , 1 day ago
-
RE: What is a considered a decent weather curve?
Thanks Gary, I'll do that with the Drayton balancing ke...
By Crimson , 1 day ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
I've created a separate thread to discuss WC settings a...
By Crimson , 1 day ago
-
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
Thanks I will try that and look at results
By A E Deans , 1 day ago
-
RE: New Samsung 12KW Heat Pump Help
No such luck yet - installers are saying their quoted 3...
By dinhp , 2 days ago
-
RE: Excessive performance/system issues with GSHP
@johnr Thanks - the Buffer tank is in the integral gara...
By didjerama_uk , 2 days ago
-
RE: Do thick walls make for warm houses?
@robl Thanks, thats interesting 🙂
By bontwoody , 2 days ago
-
RE: Mitsubishi EcoDan ASHP Settings not saving.
@fez96 Who’d of thought.? 👍
By Westkent , 2 days ago
-
RE: In the Bleak Midwinter... Midea heat pump performance, poor COP and windchill in action
A similar pattern happened again last night and into th...
By cathodeRay , 3 days ago
-
RE: Samsung HP secondary pump wiring
Thanks for the reply. I have asked a couple of days ago...
By Chris-in-Kemnay , 4 days ago
-
RE: Who's your electricity provider and what's your tariff?
Hi All We have 2 ASHPs, Solar/Battery system and soon...
By AlanB , 4 days ago
-
@westkent OK , Interesting , Im surprised that Airsourc...
By Alfapat , 4 days ago
-
RE: Post Buffer Tank DUCA Circulating Pump Settings
@potatoman I raised this with Secon, and here's what th...
By Mars , 4 days ago
-
RE: Smart meter installation – seamless or a potential nightmare?
@transparent, now hosted on our site as attached.
By Mars , 4 days ago
Latest Topics
-
Samsung E911 intermittent issue
By NetDonkey 15 hours ago
-
Samsung HP secondary pump wiring
By Chris-in-Kemnay 4 days ago
-
Post Buffer Tank DUCA Circulating Pump Settings
By Potatoman 5 days ago
-
Baffled by heat pump size/ choice!
By zuluwarrior 7 days ago
-
Vaillant ASHP Weather Compensation with Octopus Cosy
By tom58l 1 week ago
-
By R0y124 1 week ago
-
Mitsubishi Ecodan 11kw Defrosting Issue.
By ThunderMink 1 week ago