Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Please find attached the results for the 24 hour period from 21:00 on 12th Dec. 2023 to 21:00 on 13th Dec. 2023.
The first table uses LWT's averaged from the whole of the minute data during any 1 hour period, the second table averages the LWT only when the compressor was producing thermal energy. It would be interesting to know which method may give the more aligned result.
The time shown is at the end of each 1 hour period.
The OAT value used has been averaged over each 1 hour period from the raw data, no adjustment has been made for deviation from the true ambient temperature.
If anyone has any questions then please ask.
@derek-m - thanks. I've got various other things to be getting on with today, but later on I will plot the two predictions against the observed values and post the result.
The period in this spreadsheet is as you note in the tables a no setback period. Are you also able to do a prediction covering one or more of the setback periods (16/17 Dec onward) (a) with a 6 hour 2100 to 0300 setback and (b) without a setback?
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderay@derek-m - thanks. I've got various other things to be getting on with today, but later on I will plot the two predictions against the observed values and post the result.
The period in this spreadsheet is as you note in the tables a no setback period. Are you also able to do a prediction covering one or more of the setback periods (16/17 Dec onward) (a) with a 6 hour 2100 to 0300 setback and (b) without a setback?
Yes. No Problem.
Here are charts of @derek-m's model predictions vs my observed (based on amps x volts) values for energy in (PI in @derek-m's spreadsheet), first scatter plots and then bar charts. They are hourly energy in values over a 24 hour period, 2100 12 Dec to 2100 13 Dec 2023, no setback and a moderate relatively stable OAT (range 7.1 - 8.9). The text box on the left hand side of the scatter plot gives the 24 hour totals, 'Midea' is the value based on the Midea total (cumulative) values (current value - value one hour ago). I have checked for errors typos etc but E&OE as ever, I am only human.
Edit: bar charts temporarily removed because there was an error, correct version will be posted shortly
Edit: corrected bar charts now added
Midea 14kW (for now...) ASHP heating both building and DHW
Please find attached the previous results with those from 13th to 16th Dec. added.
Please also note that as yet the spreadsheet makes no correction for DHW heating, since, as yet, I am undecided as to how much DHW heating may contribute to overall building heating.
@derek-m - sorry, I did make an error in one of the bar charts (second lower chart had same data as first), I have now corrected that. I have also done the same thing, this time using my combined OAT vs energy in regression line equation (the basis I used to calculate predicted values in my earlier observed vs predicted charts):
I will shortly post all the charts in one image, to make direct comparison easier.
Midea 14kW (for now...) ASHP heating both building and DHW
Here are all the charts in one image, to (I hope - you need a large monitor) make direct comparison easier:
This is a comparison, albeit only for one rather unexceptional but not atypical day, of predictions based on observed data (using my regression line) and a model worked up from scratch. I think the comparison is interesting: despite having the worst R squared value, my regression line equation makes the best 24 hour value prediction. If we take the 'true' value to be 35.32 kWh (with the Midea 36 being a rounding error), then my regression over-estimates by 2.6 kWh, while your closest model prediction under-estimates by 3.05 kWh. @jamespa will no doubt correct me, but what I think is going on here is a sort of regression to the mean: the hourly values are a bit out, but over a 24 hour period the 'outness' cancels itself out, if that makes sense. I'm also if I admit it a bit suspicious of the third R squared value...it looks a bit low to me. All thoughts and comments welcome. Please bear in mind the goal is to be able to predict accurately what the 24 hour energy in would have been, had a setback not been applied, which can then be compared to the actual use with a setback applied.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @derek-mPlease find attached the previous results with those from 13th to 16th Dec. added.
Please also note that as yet the spreadsheet makes no correction for DHW heating, since, as yet, I am undecided as to how much DHW heating may contribute to overall building heating.
Thanks, I will do what I can as soon as I can. The really interesting 24 periods will be the setback periods, but the non-setback ones are also very useful.
Midea 14kW (for now...) ASHP heating both building and DHW
Please find attached the results file with the remaining data added up to the 18th December, which is all the data provided.
Could you now post the un-redacted raw data so that meaningful comparison can be made.
Posted by: @derek-mCould you now post the un-redacted raw data so that meaningful comparison can be made.
Will do, but juggling many things at the moment for all the usual reasons, so may be a delay. But will do as soon as I can.
PS what is unmeaningful about the charts I have already posted?
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayPosted by: @derek-mCould you now post the un-redacted raw data so that meaningful comparison can be made.
Will do, but juggling many things at the moment for all the usual reasons, so may be a delay. But will do as soon as I can.
PS what is unmeaningful about the charts I have already posted?
Nothing.
I am used to looking at the big picture, identifying probable problem areas, and then looking in detail at these areas.
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 760 Online
- 6,994 Members
Join Us!
Worth Watching
Latest Posts
-
Brown Oily Residue Blocking Air Vent and Weeping Relief Valve... Anyone Seen This?
My installation is 4 years old. After about 18 months a...
By seoras , 2 hours ago
-
RE: Renewables & Heat Pumps in the News
An article on funding for heat pumps in case anyone is ...
By Jeff , 3 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks @editor , @indevolt-uk Subject to any comments ...
By JamesPa , 11 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 11 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 15 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 15 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 16 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 17 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 19 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 19 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 1 day ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 1 day ago
-
RE: The Grid Says Yes.. Until It Doesn’t: Why Britain's Net Zero Push is Stalling at the Plug Socket
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 4 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 4 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago
-
That’s the solar up and running, I don’t think it’s the...
By David999 , 4 days ago
-
RE: Seeking ideas / information / commiseration - Pure Drive
I agree with @colinc that you can reuse some of it. A s...
By Batpred , 4 days ago