Bosch CS5800i 5kW - Experience So Far
@ectoplasmosis Buderus is a subsidiary of the Bosch Group, so I assume the different badges are just meant to capitalise on brand recognition in different markets. It does seem to be a proper 'in house' developed unit.
In other news, I've made big strides in improving our heating efficiency. I did this by adding an offset to the heating curve to bring it lower, then adding a minimum flow temperature of 28C. In order to stop the flat overheating at temperatures where the flow should be lower than 28C, I then added a fairly large room influence factor. This should be okay as the flat is well insulated and it takes a long time for temperatures to change significantly. Also, in the event that we do decide to leave all the windows and doors open, there's a maximum flow temperature of 40C configured.
This means that the heating will generally cycle on for a good few hours until the room influence grows enough (at around 1K over the target) that the unit turns off. It seems like if the target flow temperature (before the minimum flow limit is applied) is below 25 it just sets it to 0 and turns off until the room temperature falls enough that the room influence stops blocking the heating.
It remains to be seen how well this works across different parts of the performance curve, but for now we're comfortably around a COP of 4.5 while the outdoor temperature has been around 5.5C.
Sadly, it also seems the flow rate reported by the heat pump via the EMS isn't especially accurate. It looks like it could be off by as much as 25% when doing hot water, so I think any more detailed analysis will require a proper heat- or flow-meter.
-
My Octopus Cosy 6 Heat Pump Journey: From Quote to Completion
2 months ago
-
Yes, the "zoning with ASHP" topic again...
8 months ago
-
Installations in Flats
1 year ago
-
My British Gas – Heat Force ASHP Installation: A Frustrating Experience
1 year ago
-
Low shower pressure after ASHP retrofit
1 year ago
- 26 Forums
- 2,364 Topics
- 53.6 K Posts
- 517 Online
- 6,029 Members
Join Us!
Worth Watching
Latest Posts
-
-
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@kevh it's worth remembering that many lsvs only actual...
By JamesPa , 18 hours ago
-
RE: Setback savings - fact or fiction?
Exactly. We only need to compare conditions, to decide ...
By cathodeRay , 24 hours ago
-
RE: Balancing financial efficiency and comfort using the Octopus Cosy tariff
I found because I have very low heat loss I can set bac...
By RadWhisperer , 1 day ago
-
RE: Need Help Optimising My Rushed ECO4 Install: 12kW Bosch Heat Pump
Welcome @mickamills We too have an oversized 12kW Sa...
By Old_Scientist , 1 day ago
-
RE: My Powerwall 3 Consumes 3-4 kWh/Day in Self-Consumption: Is This Normal?
@caron I can confirm that the power usage of the PW3 is...
By Old_Scientist , 1 day ago
-
RE: Speedcomfort radiator fans
Thats true, but having tried (and succeeded) in constru...
By JamesPa , 2 days ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
@bash brilliant, thanks for the feedback
By energy9165 , 2 days ago
-
RE: Heat Pump Heats the House… But It’s Not Cosy. Emitter Changes or System Tweak?
@alastair There I was, feeling grumpy, he said “Cheer u...
By Toodles , 2 days ago
-
RE: Grant Aerona: Is there a setting to keep the 2-port valve open during pump blockade
Depends on OAT. Mine cycles at OAT>10 and of course...
By JamesPa , 2 days ago
-
RE: New Fogstar 15.5kWh upright solution
@transparent My conclusion is as you have noted, tha...
By Bash , 2 days ago
-
RE: Mitsubishi Ecodan R290 10kW performance
And to you too. Wishing you a very enjoyable festive s...
By Sheriff Fatman , 2 days ago
-
RE: External pipework insulation
They do? But that isn't apparent from the photos we'r...
By Transparent , 2 days ago
-
RE: Say hello and introduce yourself
@velcro welcome to the forums. Please feel free start a...
By Mars , 3 days ago
-
Daikin EDLA11D3V3 DHW Settings
I have a newly installed EDLA11D3V3 which I'm still get...
By Velcro , 3 days ago
-
RE: Midea ASHP – how to set weather compensation
@curlykatie did you get sorted with this?
By MickaMills , 3 days ago
-
RE: MyVaillant Connect Regular Disconnect
Thanks. Yes, if the time is consistently 11pm every nig...
By buckwem , 4 days ago