Bathroom Radiator replacement

5 Posts
3 Users
0 Reactions
456 Views
(@alfapat)
Reputable Member Member
Joined: 2 years ago
Posts: 160
Topic starter  

I need to replace a 600 x 1200 double panel radiator as it leeks a little with a vertical towel and heat radiator . How do I compare an old radiator to this , is it by the amount of BTU'S they emit ?


   
Quote
(@jamespa)
Illustrious Member Moderator
Joined: 2 years ago
Posts: 2312
 

Posted by: @alfapat

I need to replace a 600 x 1200 double panel radiator as it leeks a little with a vertical towel and heat radiator . How do I compare an old radiator to this , is it by the amount of BTU'S they emit ?

Thats the main consideration.   You need to calculate btu or kW at your design flow temperature and compare with the room heat loss.  Towel rails emit very little heat so you are unlikely to match the output of a panel radiator.

 

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@alfapat)
Reputable Member Member
Joined: 2 years ago
Posts: 160
Topic starter  

OK , Thanks James, can the btu's be calculated from the existing Radiator as it was measured to size for that room initially.

By the way I have a plumber / heat engineer the create a volumizer out of buffer and remove excess pumps and sort the pipework , at last!


   
ReplyQuote



(@jamespa)
Illustrious Member Moderator
Joined: 2 years ago
Posts: 2312
 

Posted by: @alfapat

OK , Thanks James, can the btu's be calculated from the existing Radiator as it was measured to size for that room initially.

By the way I have a plumber / heat engineer the create a volumizer out of buffer and remove excess pumps and sort the pipework , at last!

Yes.  Just find any radiator catalogue eg myson or stelrad and look it up.  This will give you W at a DT of 50C between flow temp and room.  To convert to W at whatever your design ft is, use output proportional to DT raised to the power 1.3. 

Alternatively you can just look for another rad with the same output at DT50, but you are unlikely to find a towel rail that does this.

 

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
Joined: 4 years ago
Posts: 3109
 

@rob-nezard can you please offer your professional advice on this subject?

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Subscribe and follow our Homeowners’ Q&A heat pump podcast


   
ReplyQuote
Share:

Join Us!

Trusted Installers

Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.

✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available

👉 Find your installer now!

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security