ASHP Cycling On/Off...
 
Notifications
Clear all

ASHP Cycling On/Off - Is it an issue?

81 Posts
13 Users
90 Reactions
21.9 K Views
(@saenergy)
Trusted Member Member
126 kWhs
Expert
Joined: 3 years ago
Posts: 17
 

@editor Ah yes, my bad, should of tagged @hydros

 

 

Internationally recognised award winning installer of heat pumps and stuff


   
👍
2
ReplyQuote
(@hydros)
Estimable Member Member
333 kWhs
Joined: 3 years ago
Posts: 59
Topic starter  

@saenergy 

The auto bypass is located just after the 3 port valve, before any of the radiators. A quick google search suggests it should be located further in to the central heating circuit. I think it has been put here for ease of access rather than any other reason. I'm not sure why it's even needed, I have a towel rail in the bathroom which is one of the further radiators from the heat pump, and I now have all the TRV's fully open, so I would have thought that would be a sufficient circuit to not require an auto bypass valve. I have left it alone so far. Picture of the valve below. 

image

   
👍
2
ReplyQuote
(@hydros)
Estimable Member Member
333 kWhs
Joined: 3 years ago
Posts: 59
Topic starter  

@derek-m & @kev-m

Thanks for looking over the report. I was going around in circles a bit with the report too but didn't know if it was me and my limited technical understanding of the subject.

From personal experience of the last two weeks I'm sticking with the method of running with weather compensation, slow and steady, the house is much more comfortable. I'd like to try Leaving Water Temperature Modulation if I can convince the installer to move the controller. I'd just like to reduce the cycling further if possible. 

 


   
👍
2
ReplyQuote



(@derek-m)
Illustrious Member Member
15283 kWhs
Veteran Expert
Joined: 4 years ago
Posts: 4429
 

Hi @kev-m 

A quick question I am hoping you can answer.

Because of the mild weather we are suffering at the moment, I assume that your heat pump is cycling?

How frequent is the cycling and for how long does your heat pump run?


   
ReplyQuote
(@saenergy)
Trusted Member Member
126 kWhs
Expert
Joined: 3 years ago
Posts: 17
 

@hydros Thats going to cause problems for sure.  I would remove it completely.  Easy enough to do, just get a couple of 22mm compression end caps and remove it.  So long as you leave the Towel rad(s) open it will be fine.

Also, check the diverter valve has been setup correctly.  Those valves have a number of options and its easy to get it wrong, if its not setup as a diverter it can act as a mid pos which I have seen a few times.

Just had annother quick look at the diagram, you have a volumiser and a BUH.  I don't wire the BUH to run ever.  It should be a last resort and frankly an inline 3kW heater is going to do very little.  What it can do though is get stuck on or cycle if the ASHP control isn't quite right.  This can cause issues, mostly with run cost but also it can mess with the lower modulation point of the ASHP as you have a fixed input on a modulating system.  If you can disable it via an isolator I would do that too.

This post was modified 3 years ago by SAEnergy

Internationally recognised award winning installer of heat pumps and stuff


   
👍
4
ReplyQuote
(@kev-m)
Famed Member Member
5606 kWhs
Joined: 4 years ago
Posts: 1276
 
Posted by: @derek-m

Hi @kev-m 

A quick question I am hoping you can answer.

Because of the mild weather we are suffering at the moment, I assume that your heat pump is cycling?

How frequent is the cycling and for how long does your heat pump run?

Hi Derek,

Yes it does cycle.  I'm currently not using weather compensation so yesterday looked like this. You can see the flow drop as the thermostats stop the ASHP.

Ambient 13C, Thermostats 45C Flow.  15kWh

Close up

Flow 45C Cycling

When I was using weather compensation, a mild day looked like this.  The peak in the middle is HW.

Ambient 9.4C, Weather Compensation, 17.2kWh

Close up

Weather Comp cycling close up

So it looks like 3 times per hour or so.

 


   
👍
2
ReplyQuote
(@derek-m)
Illustrious Member Member
15283 kWhs
Veteran Expert
Joined: 4 years ago
Posts: 4429
 

Hi @kev-m 

Thanks for that Kev. It would appear that you are already doing something that I was going to suggest.

Running the system on thermostat control, rather than weather compensation, when the weather is milder. In that way the amount of cycling should be reduced and I suspect it will also reduce energy consumption.

Looking forward to seeing your results when you have completed your tests.


   
👍
2
ReplyQuote
(@jonathans)
Eminent Member Member
10 kWhs
Joined: 3 years ago
Posts: 12
 
Posted by: @derek-m

When operating on weather compensation, the thermostat should be set above the desired temperature, so that it does not switch off your heat pump prematurely.

@derek-m, I have a question about this statement. I think I understand your later explanation of how premature shutoff happens (link) but I don't understand why this situation is any different with weather compensation versus without. Why is this not an issue all the time? Also, how much higher should a thermostat be set to compensate for this?


   
ReplyQuote
(@derek-m)
Illustrious Member Member
15283 kWhs
Veteran Expert
Joined: 4 years ago
Posts: 4429
 
Posted by: @jonathans
Posted by: @derek-m

When operating on weather compensation, the thermostat should be set above the desired temperature, so that it does not switch off your heat pump prematurely.

@derek-m, I have a question about this statement. I think I understand your later explanation of how premature shutoff happens (link) but I don't understand why this situation is any different with weather compensation versus without. Why is this not an issue all the time? Also, how much higher should a thermostat be set to compensate for this?

Hi Jonathans,

In weather compensation mode, the ASHP controller is stopping and starting the heat pump, rather than the thermostat. Dependent upon the outside air temperature, the ASHP controller will calculate the required water flow temperature that meets the present heat demand, and in this way the heat pump operates more efficiently.

When controlling the indoor air temperature using thermostats, the water flow temperature has to be at a higher value, to compensate for the periods when the heat pump is switched off and hence not supplying any heat energy. This higher value could be a few degrees or +20C, the thermostat will still switch the heat pump off when the set temperature has been reached.

If you try to operate your system with both the controller and the thermostats trying to control the temperature, then it probably will not perform very well.

The choice is therefore, to control your system on weather compensation, and set the thermostats 1C or 2C above the desired temperature, so that they don't normally interfere with the controller. This would probably be the best mode of operation when the outdoor air temperature is below +7C.

At the moment I am researching a possible alternative method of control, for milder weather conditions, to try to reduce compressor cycling. This method would involve using the weather compensation offset, to increase the water flow temperature by 1C or 2C, but then set the thermostats to control the indoor temperature at the desired level. Provided that the water flow temperature is sufficient to meet the heat demand, the desired indoor air temperature will be achieved and the thermostats will switch the heat pump on and off. This should reduce compressor cycling but still provide good overall efficiency.

I believe that Kev is already carrying out tests along these lines, so we should welcome any results he may have available.

 


   
ReplyQuote



(@jonathans)
Eminent Member Member
10 kWhs
Joined: 3 years ago
Posts: 12
 

@derek-m

Thanks very much -- I think I understand this now, as well as the source of my confusion. My Vaillant 12kW operates only w/the Vaillant Sensocomfort controller, ie, it has no other independent thermostat. So if I grasp your explanation, this means that even under weather compensation, I would use that controller as usual. That is, I would set a set-back temperature and then any other higher-heat demand periods (this is what I mean by 'as usual' -- putting in exactly the desired temperature rather than something slightly higher), initiate the function that adjusts the flow temp based on the current room temp, and then just let the ASHP run itself & adjust flow temps as it sees fit.

Have I correctly grasped the difference between the ASHP controller and the thermostat in your explanation?


   
ReplyQuote
(@derek-m)
Illustrious Member Member
15283 kWhs
Veteran Expert
Joined: 4 years ago
Posts: 4429
 

@jonathans 

I am getting ready to go out this evening, so will have a detailed look tomorrow and get back to you.


   
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
26255 kWhs
Veteran
Joined: 4 years ago
Posts: 2979
 

@derek-m, have a super evening. Best wishes to you and the Mrs. for 2022, and thank you for all your research, work and effort in helping homeowners with their heat pumps. Massively appreciated.

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Subscribe and follow our Homeowners’ Q&A heat pump podcast


   
👍
2
ReplyQuote
Page 5 / 7



Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security