Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Advice on ASHP choice needed
Posted by: @derek-mIt should also be noted that the actual heat loss of bedrooms can be lower than the calculated value, due to heat rising and solar gain through the roof.
Excellent observation @derek-m, modern well insulated homes with low infiltration/exfiltration AC/h values tend to suffer from overheating upstairs. This is due to simple physics with warm air being less dense and rising in the heating season. Modern lifestyle factors compound this, such as increasing preference for open plan living and larger hallways, stairs and landings, or atriums, where warm air can easily rise.
Non-scientific estimations by myself seem to show the upstairs of uniformly heated two storey dwellings can be 2degC warmer than downstairs. We can usually turn down heat output upstairs, but what if there's a heating capacity shortfall downstairs, or the downstairs emitters have not been sized to compensate for heat energy migration to other spaces? This isn't considered in any room by room heat loss sizing calculation software that I'm aware of. They all assume closed rooms/zones.
Maybe we should flip our home layouts upside for better thermal comfort, with living spaces upstairs and sleeping rooms downstairs?! 😉
I can’t help but feel a simple solution could be to design houses once again with stairs that are hidden behind a door so the whole of th upstairs can be easily isolated. Failing that, of course, the really low-tech solution of keeping all upstairs doors closed so only the landing overheats.
I’m well aware there are many homes where my generalisations wouldn’t work, of course.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
@majordennisbloodnok Aha Bloodnock! I have a sneaky plan, Eccles, put the upstairs in the basement!😉 Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Posted by: @toodles@majordennisbloodnok Aha Bloodnock! I have a sneaky plan, Eccles, put the upstairs in the basement!😉 Toodles.
Our last house it was, coolest and most stable temperature summer and winter room in the house, very quiet also. The upstairs was left for guests, way to warm in the summer.
@johnmo I suppose that gave them a ‘warm welcome’ 😉
There’s something to be said for ‘living’ upstairs in the heated environment and retiring to the lower level to sleep. Anyone carried out an analysis of energy consumption with such an arrangement? Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Posted by: @AnonymousPosted by: @majordennisbloodnokcould be to design houses once again
Without an upstairs?
He, he.
You got me rereading what I posted. Fortunately, I did say “once again with…” so there was a qualifying part to the sentence.
Houses certainly often used to hide stairs behind doors, probably so the occupants could heat rooms separately rather than the whole house at a time. I can’t see a good reason for not moving back to that compartmental design.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
Posted by: @majordennisbloodnokHouses certainly often used to hide stairs behind doors, probably so the occupants could heat rooms separately rather than the whole house at a time. I can’t see a good reason for not moving back to that compartmental design.
Houses used to have almost no insulation, so compartmentalising made a big difference. For well insulated houses the difference is smaller, because the thermal conductivity between rooms is much greater than the thermal conductivity between the inside and the outside.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Agreed, @jamespa, and understood. However, since an issue related to open plan design has been mentioned I would suggest there is still a place for designing in the option to compartmentalise even if that choice is rarely used and the doors are left open. In fairness there may well be fire safety benefits as well, so I stand by my earlier statement; I can’t see a good argument for avoiding that sort of design.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
Posted by: @majordennisbloodnokAgreed, @jamespa, and understood. However, since an issue related to open plan design has been mentioned I would suggest there is still a place for designing in the option to compartmentalise even if that choice is rarely used and the doors are left open. In fairness there may well be fire safety benefits as well, so I stand by my earlier statement; I can’t see a good argument for avoiding that sort of design.
Fair enough and I agree that a closed staircase would reduce hot air rising, although I suspect that convection downstairs together with transmission through an uninsulated ceiling/floor would still convey a lot of heat to the upstairs. Nevertheless it will doubtless have an effect (and you could insulate the floor/ceiling void). Also, as you say, if its fire resistant will also aid with fire compartmentalisation. So from a purely technical function perspective I wouldn't dispute that there is no good reason to avoid this design style.
Of course houses are for living in as well, and many people prefer fairly (or almost completely) open plan. That said, fashion has probably made this more popular than its due and fashions have a habit of reversing!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
You do realise that by having more doors, it means that there are more doors that your wife can slam in your face. 😋
Posted by: @derek-mYou do realise that by having more doors, it means that there are more doors that your wife can slam in your face. 😋
😁
After more than a quarter of a century married, she’s more than inventive enough already if the situation calls (and I have deserved it on occasion). Another door or two would only serve to reduce the volume; silver linings and all that…
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 272 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Hush mode now released. I've not tried it yet. Should b...
By swwils , 58 minutes ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 1 hour ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 14 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 15 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 15 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 18 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 1 day ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 1 day ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago