I've just watched the outside temp on the display for the whole 8 min run. It starts at 6.6 degrees then by around 4 mins it's dropped to 6.3 degrees then in the last minute or so it climbs back to 6.6 where it cuts out for 20 seconds but starts again when still on 6.6.Â
I'm looking for something changing, during the 20 second period, from the heat pump switching off, to it restarting.
Correct me if I am wrong, that your heat pump runs for 8 minutes or so, switches off for 20 seconds, then runs for a further 8 minutes or so, etc. etc.
A further thing that I find quite surprising is how low are the temperatures of your radiators, your home must be very well insulated.
The next test to try would be to change the controller mode from WC to a fixed LWT of say 35C, and see what effect this has on how your heat pump operates, and what changes occur to the radiator temperatures and room temperatures.
Yes, that's correct. 8 mins on, 20 seconds off then 8 on ad infinitum. There is no change in the outside temp during the 20 seconds.Â
I'm not sure if it's that great on insulation. Cavity wall beads, loft insulation, large double glazed windows but heating sits at 18-18.5 all day. Heat pump is on 24-7.Â
Posted by: @craig1980Yes, that's correct. 8 mins on, 20 seconds off then 8 on ad infinitum. There is no change in the outside temp during the 20 seconds.Â
I'm not sure if it's that great on insulation. Cavity wall beads, loft insulation, large double glazed windows but heating sits at 18-18.5 all day. Heat pump is on 24-7.Â
The temperatures measured on your radiators would indicate that there is very little heat energy being transferred into your home.
Â
Try pulling up the 'Indoor Zone Status Information' as shown on page 18 in the manual shown below.
Thanks,
Now try monitoring the 'Master Indoor Zone Information', particularly as the 20 second off period ends and the heat pump restarts.
- 26 Forums
- 2,112 Topics
- 46.4 K Posts
- 23 Online
- 3,405 Members
Join Us!
Latest Posts
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Ebac 5kw - Monobloc R32. Developed and made in UK - Mit...
By marcinwloch69@gmail.com , 55 minutes ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Just another thought - it might be worth thinking about...
By JamesPa , 4 hours ago
-
RE: No-code, plug-and-play monitoring for your heat pump
My installer fitted one of these as his choice for moni...
By Broadsman , 5 hours ago
-
RE: BUS Grant: removal of all other fossil fuel heat sources
@rikiarn - just have a think as to how much it will cos...
By Transparent , 18 hours ago
-
Don't do much digging around.That's best left to the pr...
By Transparent , 19 hours ago
-
Hi all, I was wondering if anyone had an idea of how th...
By Wh0am3ye , 21 hours ago
-
RE: EBAC re-entering the ASHP market in 2023
@toodles confirm i have Ebac 5kw ASAP + homely and it w...
By marcinwloch69@gmail.com , 23 hours ago
-
RE: Compute heat loss from energy used
@jamespa Ebac must be similar to Mitsubishi as they buy...
By marcinwloch69@gmail.com , 23 hours ago
-
@pie_eater I have been thinking of adding cooling to my...
By TechnoGeek , 3 days ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
Agree, but you may have a hard time convincing them, as...
By JamesPa , 4 days ago
-
RE: Seal the Deal: Don't Let Your Heat Pump Leak Energy
Hi - fyi - there's a dead image link in the 'Optimal In...
By seatonian , 5 days ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
@chandykris Horses and beggars…. 😉 Toodles.
By Toodles , 5 days ago
-
RE: Cleaning up after gas meter removed
@agentgeorge Likewise in the loft space; we have 300mm ...
By Toodles , 5 days ago
-
RE: Ecodan consuming 100kwh per day in new build!!!
This particular example is one of the worst I have seen...
By JamesPa , 5 days ago
-
-
RE: Fan running in hot weather ...why?
I wonder if it has some kind of pressure transducer to ...
By ASHP-BOBBA , 6 days ago
-
RE: Cooling with Samsung Gen6 and Flow error
@iaack The system isnt running long enough for any cond...
By EcoBaker , 6 days ago
-
@heacol thanks for confirming we can only hope NAPIT ag...
By Bart , 6 days ago