I've just watched the outside temp on the display for the whole 8 min run. It starts at 6.6 degrees then by around 4 mins it's dropped to 6.3 degrees then in the last minute or so it climbs back to 6.6 where it cuts out for 20 seconds but starts again when still on 6.6.Â
I'm looking for something changing, during the 20 second period, from the heat pump switching off, to it restarting.
Correct me if I am wrong, that your heat pump runs for 8 minutes or so, switches off for 20 seconds, then runs for a further 8 minutes or so, etc. etc.
A further thing that I find quite surprising is how low are the temperatures of your radiators, your home must be very well insulated.
The next test to try would be to change the controller mode from WC to a fixed LWT of say 35C, and see what effect this has on how your heat pump operates, and what changes occur to the radiator temperatures and room temperatures.
Yes, that's correct. 8 mins on, 20 seconds off then 8 on ad infinitum. There is no change in the outside temp during the 20 seconds.Â
I'm not sure if it's that great on insulation. Cavity wall beads, loft insulation, large double glazed windows but heating sits at 18-18.5 all day. Heat pump is on 24-7.Â
Posted by: @craig1980Yes, that's correct. 8 mins on, 20 seconds off then 8 on ad infinitum. There is no change in the outside temp during the 20 seconds.Â
I'm not sure if it's that great on insulation. Cavity wall beads, loft insulation, large double glazed windows but heating sits at 18-18.5 all day. Heat pump is on 24-7.Â
The temperatures measured on your radiators would indicate that there is very little heat energy being transferred into your home.
Â
Try pulling up the 'Indoor Zone Status Information' as shown on page 18 in the manual shown below.
Thanks,
Now try monitoring the 'Master Indoor Zone Information', particularly as the 20 second off period ends and the heat pump restarts.
- 26 Forums
- 2,114 Topics
- 46.4 K Posts
- 62 Online
- 3,410 Members
Join Us!
Latest Posts
-
RE: No-code, plug-and-play monitoring for your heat pump
The issue with the Grant is that you have to wire direc...
By Grantmethestrength , 1 hour ago
-
RE: Is this just haze or something more?
I am not a scientist nor a meteorologist and I know the...
By Toodles , 1 hour ago
-
RE: Benefits of an extra horizontal loop for GSHP
It will improve performance, but by how much depends on...
By Brendon Uys , 6 hours ago
-
RE: The good, the bad and the not that great – my heat pump installation
Said I would pop back with a update. Only Mr Jesus h...
By Burtis , 20 hours ago
-
RE: Buffers, hot water and cooling
Thats presumably heat pump DT, what about radiator DT a...
By JamesPa , 21 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@chandykris Exactly the same here. We now have 13.5kWh ...
By Old_Scientist , 1 day ago
-
Compressor and Evaporator Stratification
I have had a few issues with my Hitachi spilt heatpump ...
By trebor12345 , 1 day ago
-
RE: Wood burner with ASHP - direct air?
This depends on the size of your wood burner and size/t...
By Lucia , 2 days ago
-
RE: Difficult positioning of air source heat pump
@rikiarn It's a not a buffer it's a volumiser which is ...
By Lucia , 2 days ago
-
RE: Is your heat pump insured?
To make things clear, lots of insurance companies cover...
By Lucia , 2 days ago
-
RE: Boxt Heat Pump Installation Experience
@adrian any updates since installation? How is it perfo...
By Ashfp , 2 days ago
-
RE: Say hello and introduce yourself
Hi @seatonian - Yes, I know Seaton, and I have the Nat...
By Transparent , 3 days ago
-
@seatonian got your email. Will connect you with a reco...
By Mars , 4 days ago
-
@downfield and @toddles, this isn’t in the settings cur...
By Mars , 6 days ago
-
RE: Homely launched for Grant Aerona ASHP control
I haven't bought the Aerona Smart Controller (£700!) bu...
By Prunus , 6 days ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
For the record, Grant supply ethylene glycol for their ...
By Prunus , 6 days ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer amazing. Well done!
By Mars , 6 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Ebac 5kw - Monobloc R32. Developed and made in UK - Mit...
By marcinwloch69@gmail.com , 1 week ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Just another thought - it might be worth thinking about...
By JamesPa , 1 week ago
-
RE: BUS Grant: removal of all other fossil fuel heat sources
@rikiarn - just have a think as to how much it will cos...
By Transparent , 1 week ago