I've just watched the outside temp on the display for the whole 8 min run. It starts at 6.6 degrees then by around 4 mins it's dropped to 6.3 degrees then in the last minute or so it climbs back to 6.6 where it cuts out for 20 seconds but starts again when still on 6.6.Â
I'm looking for something changing, during the 20 second period, from the heat pump switching off, to it restarting.
Correct me if I am wrong, that your heat pump runs for 8 minutes or so, switches off for 20 seconds, then runs for a further 8 minutes or so, etc. etc.
A further thing that I find quite surprising is how low are the temperatures of your radiators, your home must be very well insulated.
The next test to try would be to change the controller mode from WC to a fixed LWT of say 35C, and see what effect this has on how your heat pump operates, and what changes occur to the radiator temperatures and room temperatures.
Yes, that's correct. 8 mins on, 20 seconds off then 8 on ad infinitum. There is no change in the outside temp during the 20 seconds.Â
I'm not sure if it's that great on insulation. Cavity wall beads, loft insulation, large double glazed windows but heating sits at 18-18.5 all day. Heat pump is on 24-7.Â
Posted by: @craig1980Yes, that's correct. 8 mins on, 20 seconds off then 8 on ad infinitum. There is no change in the outside temp during the 20 seconds.Â
I'm not sure if it's that great on insulation. Cavity wall beads, loft insulation, large double glazed windows but heating sits at 18-18.5 all day. Heat pump is on 24-7.Â
The temperatures measured on your radiators would indicate that there is very little heat energy being transferred into your home.
Â
Try pulling up the 'Indoor Zone Status Information' as shown on page 18 in the manual shown below.
Thanks,
Now try monitoring the 'Master Indoor Zone Information', particularly as the 20 second off period ends and the heat pump restarts.
- 26 Forums
- 2,199 Topics
- 48.4 K Posts
- 66 Online
- 5,854 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Why Air Release Valves and Deaerators are Non-Negotiable
Top tip to fit an isolation valve! All good points. I...
By Old_Scientist , 7 minutes ago
-
RE: Heat Pump Installers: Competence, Illusion and the Hard Truth Homeowners Must Face
@editor I hope you have at least a partially working he...
By GrahamF , 43 minutes ago
-
@drei are taking measurements from the heat pump, or do...
By GrahamF , 4 hours ago
-
RE: Heat pump and wifi kit connection.
Wi-Fi kit covers any Samsung device that has a modem in...
By Alfapat , 11 hours ago
-
RE: How to Understand Wiring Up a Heat Pump
I’m watched @pirate-rich rewire our wiring centre last ...
By Mars , 12 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@agentgeorge err… Pass! I dunno what caused that! I’ll ...
By Toodles , 13 hours ago
-
RE: Sizing - Save me from my headache
If you get an R290 pump you should be able to heat the ...
By JamesPa , 13 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa can you take a pic of the primaries inside the...
By AdamK , 13 hours ago
-
RE: Large heat pump options for church building
@aventus-eco Thanks Sean, will drop you a line.
By Josephiah , 13 hours ago
-
RE: Moving FIT array onto a Tesla Powerwall 3 possible?
@toodles that’s good news for @adamk
By Judith , 14 hours ago
-
RE: Samsung Gen 6 - Schedules not working
@technogeek That sounds very logical :-). I will give i...
By bontwoody , 18 hours ago
-
RE: Who's your electricity provider and what's your tariff?
Considering Octopus states all their electricity is gre...
By AgentGeorge , 18 hours ago
-
RE: Heat Pump + Tado Setup: Smarter Control for Secondary Pumps?
@pirate-rich thanks for the reply. If I were to explo...
By Lloydi , 18 hours ago
-
RE: Seal the Deal: Don't Let Your Heat Pump Leak Energy
@transparent I think the committee might get into some ...
By Toodles , 19 hours ago
-
Samsung ASHP Support in Midlands area?
Hi all, Per title.... can anyone recommend a ASHP ser...
By Andehh , 20 hours ago
-
May I present the maths I referred to earlier when disc...
By Transparent , 22 hours ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
How many times and dates have epc sap rules been change...
By Tim441 , 23 hours ago
-
RE: Rodents! A word of warning for heat pump owners
I think similar care should be taken against vermin ing...
By Transparent , 24 hours ago