Posted by: @craig1980
- @derek-m I didn't set them back to 21 straight away and left them for a day. At night it was longer between but by the next day it was back to the same.Â
Had the indoor temperature changed? A further test would be to watch closely the operation of the wireless receivers for the thermostats when the system performs its short off - on cycle.
Also check that all the plug and socket connections on the circuit board are making good contact.
Â
Posted by: @craig1980@derek-m no change in the indoor temperature. The lights on the receivers do not change when it cycles on and off.
Did you close the airing cupboard door overnight? The reason I ask is that sometimes equipment, and circuit boards, can suffer intermittent faults due to thermal expansion.
What water law settings are applied at the moment?
Â
@derek-m the airing cupboard door is always shut. It doesn't get that warm in there.Â
Pics of the screen set up of water law.Â
Not sure if the set up with "floor" is correct. Whether it should be FCU instead?
Also running -2 on the home screen which I'm led to believe is a short cut to adjusting a water law setting. Assuming the 31?Â
Â
Posted by: @derek-mYes, I've seen all the different diagrams in the manuals, but it doesn't tell one which is correct. Also I don't see the point in having two pumps to do the job that one pump should be able to do.
I’d go with the one from the Jule installation manual, as it’s a Jule cylinder/heatpump package. Now that we’ve seen some more photo’s you can clearly see that the hydraulics match what is shown I their manual exactly.
Â
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Posted by: @derek-mHi Hugh,
Do you know if the Samsung controller will still use WC when operating with the indoor temperature located within the controller?
I have a lot of time for Glyn Hudson over on YouTube who has just DIYd his 5kW Samsung install and has documented it with a decent video. From the comments I’ve been having with his, he says that the Samsung will still use WC when the wired controller is used as for measuring room temperature. I’ve asked him if the controller will also support load compensation and reduce the flow temperature when the room is approaching the target temp. Inversely, increasing the flow temp to recover quickly from a nighttime or away/holiday mode setback temperature.
He uses a single pump (with PWM control) on his setup but his primary pipe work is short.
Â
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Let me have a read through the manual and decipher what some of the descriptions mean. I'll get back to you tomorrow.
Glyn has his 5kW Samsung wired/plumbed up with full monitoring, the data can be viewed at:
https://emoncms.org/samsung5kw
Single grundfos PWM pump, a heatpump cylinder with a 1m2 coil (the same cylinder I’ve got - they were cheap on eBay back in the summer), and radiators throughout.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
- 22 Forums
- 2,096 Topics
- 46.1 K Posts
- 62 Online
- 3,383 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Mitsubishi cycling while on chilled water output
@downfield Ah, sorry I didn't realise you had fan assis...
By ASHP-BOBBA , 5 minutes ago
-
RE: Commencing on an ASHP Installation Process
I'm fairness to Havenwise the logic of dhw heating is t...
By JamesPa , 8 minutes ago
-
@jamespa Thanks for the advice - very helpful. I had al...
By abam48 , 10 hours ago
-
RE: Weather compensated secondary circuits with Biomass
Hi @andycoo we do an LK 110 standalone weather compensa...
By Sune , 10 hours ago
-
RE: Adding battery storage to SolarEdge PV system
@chandykris No need to apologise at all! I forgot to ad...
By Toodles , 1 day ago
-
RE: Say hello and introduce yourself
Yes please do Suggesting a loss in the region...
By JamesPa , 1 day ago
-
RE: Surface mount or bury primaries for heat pump installation?
Can we have some links to those you're considering plea...
By Transparent , 1 day ago
-
As I have reported elsewhere we turned on the cooling o...
By downfield , 2 days ago
-
@hughf, I think we’ll organise an RHH session at Instal...
By Mars , 3 days ago
-
@el3b Hi, sorry to hear that, it is advisable to instal...
By ASHP-BOBBA , 3 days ago
-
RE: Difficult positioning of air source heat pump
@rikiarn Out of intrigue, the thread reads as though Ai...
By Sheriff Fatman , 3 days ago
-
RE: Mitsubishi Ecodan Fails to Heat Water despite temperature drop
@m1kegibson If you are able to access the service me...
By HarriUp , 3 days ago
-
RE: When will heat pumps and install prices come down?
... which of course is impossible because the world mov...
By JamesPa , 3 days ago
-
RE: Battery storage to run Heat Pump.
I would be surprised if the battery chemistry is going ...
By Transparent , 4 days ago