Fine tuning your AS...
 
Notifications
Clear all

Fine tuning your ASHP performance

195 Posts
15 Users
76 Likes
22.5 K Views
(@kev-m)
Famed Member Moderator
5550 kWhs
Joined: 3 years ago
Posts: 1299
 

@markc 

really good data that supports what a lot of us are trying.  A couple of questions (1) I think you are using weather compensation but still using external thermostats; is that right?  To give my supplier credit, that's how they set up my system and (2) Do you have the total energy delivered over the two periods?  That would be another good comparison. (sorry if I've missed this)

I've also heard the 'people will complain if rads aren't hot' comment.

Kev   

This post was modified 2 years ago by Kev M

   
ReplyQuote
(@derek-m)
Illustrious Member Moderator
13551 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 4144
 

@markc 

Thanks Mark.

Excellent data once again.

I fully agree about a database or something similar, but also the need to educate both customers and installers about how to operate ASHP's in the most efficient manner. You are doing a great job, keep spreading the gospel.

One of the reasons that I created the modelling tool, was so that it would be possible to probably find the approximate settings for the weather compensation curve, without the need for continual trial and error.


   
ReplyQuote
(@adaml)
Trusted Member Member
92 kWhs
Joined: 2 years ago
Posts: 42
 

@derek-m 

 

Hi Derek, can you please let me know a little about the modelling tool? Sorry if a little late to the party.

 


   
ReplyQuote



(@derek-m)
Illustrious Member Moderator
13551 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 4144
 
Posted by: @adaml

@derek-m 

 

Hi Derek, can you please let me know a little about the modelling tool? Sorry if a little late to the party.

 

What would you like to know?


   
ReplyQuote
(@adaml)
Trusted Member Member
92 kWhs
Joined: 2 years ago
Posts: 42
 

@derek-m I suppose how close are we to having a modelling tool that can suggest an optimum weather dependent curve/other optimum settings as @MarkC suggested?

Without taking this OT (and not withstanding my gas/ASHP setup) it is difficult to know what the optimum is and I'm still trying to get my head around the different curves suggested and the impact of adjusting these.

 


   
ReplyQuote
(@derek-m)
Illustrious Member Moderator
13551 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 4144
 

@adaml 

The modelling tool that I produced appears to give reasonably accurate results for Ecodan 14 kW ASHP's, provided that fairly accurate data for heat demand and total heat emitter output capacity is entered. It could be used for other sizes of Ecodan heat pumps and those from other manufacturers, provided that operating data obtained from standard testing procedures can be obtained and entered into the spreadsheets to replace that for the 14 kW Ecodan.

You could still do the modelling for your ASHP, by assuming that the gas boiler is not functioning, so only the heat pump was operating. The modelling tool would calculate the required water flow temperature for ambient air temperatures from 20C down to -15C.


   
ReplyQuote
(@markc)
Reputable Member Member
93 kWhs
Joined: 3 years ago
Posts: 97
Topic starter  
Posted by: @kev-m

@markc 

really good data that supports what a lot of us are trying.  A couple of questions (1) I think you are using weather compensation but still using external thermostats; is that right?  To give my supplier credit, that's how they set up my system and (2) Do you have the total energy delivered over the two periods?  That would be another good comparison. (sorry if I've missed this)

I've also heard the 'people will complain if rads aren't hot' comment.

Kev   

I'm assuming by external you mean external to the ASHP, not outside in the fresh air.

1. I have 4 internal thermostats (Heatmiser and Nest) and they are all set to 25ºC (so effectively now calling for heat all the time). The ASHP uses it's own external (i.e. outside the house) thermistor to read ambient outside air temp and set the flow heat.

2. 8-9/12 produced 218.4kWh, 10-11/12 produced 255.9kWh


   
ReplyQuote
(@kev-m)
Famed Member Moderator
5550 kWhs
Joined: 3 years ago
Posts: 1299
 

@markc 

sorry, by external I meant 3rd party. Same set up as me then.

thanks


   
ReplyQuote
(@markc)
Reputable Member Member
93 kWhs
Joined: 3 years ago
Posts: 97
Topic starter  

I now have a full years metered ASAP energy usage that I can report on.

 

The headline is that energy usage has come in just about bang on what was expected.

And the system is performing very well. We have had no issues with the pump.

 

According to the MCS estimates that were produced, the energy requirements for heating and DHW were 21,571 kWh.

And the estimated energy usage for the ASHP was 6765 kWh.

 

For the year the system has actually used 6441kWh for DHW and heating.

 

Comparing ASHP to LPG which is what I moved from:

2020 I spent £1500 on LPG. This was with the heating set at 18ºC from 22:00 until 17:00 and 22ºC 17:00 until 22:00.

 

At the time of commissioning (the good ol’ days!) I was paying 15p per kWh for electricity. Assuming prices would have remained stable.

£0.15 x 6441 = £966 for a house that is constantly 22ºC.

 

So all things being equal and assuming all energy prices have risen a similar percentage, the move from LPG to ASHP does ‘seem’ to be the right move.

 

That being said:

Even with the RHI deducted the new system cost £3000. The installation was £14K, RHI is paying back £11K.

I had to pay £1000 to have the LPG tank removed.

 

I’ve pulled out a couple of months for comparison.

 

In April the system was running on a set flow temp of 50ºC and the heating was controlled with internal thermostats.

As discussed in other chats/threads this is done so the system matches the usage of a gas boiler type installation so customers are more comfortable with how to control it.

We also had the thermostats set to:

22:00 - 6:00 = 16ºC

06:00 - 18:00 = 18ºC

18:00 - 22:00 = 22ºC

22ºC feels comfortable for us so the house did feel cool and I was attempting to use as little energy as possible. Not a comfortable setting for us.

The heating used 838.4 kWh and delivered 2285 kWh of heating.

April COP was 2.6

Average outside temp was 6.38ºC

 

As we got into October and the energy usage began to rise we started looking into optimising the system on the forum and changed the settings to weather compensation.

 

As part of this move we set the system up to deliver a constant 22ºC internal temperature, 24 hours a day. The thermostats no longer controlled the system as the weather compensation regulates the flow temperature.

 

The heating used 593.1 kWh and delivered 2339 kWh of heating.

November COP was 3.7

Average outside temp was 8.08ºC

 

Granted, April was slightly colder than Nov outside. Both months required a similar amount of heating.

But, when using a set 50ºC flow temp, April used a third MORE electricity to deliver a cooler, less comfortable internal temperature.

 

So with a set up like ours, (UFH downstairs and rads upstairs) my take is that weather compensation and 24/7 heating is the way to go.

annual
april
nov

   
Derek M, Saz, Derek M and 1 people reacted
ReplyQuote



(@kev-m)
Famed Member Moderator
5550 kWhs
Joined: 3 years ago
Posts: 1299
 

@markc 

Good results and looks like you made the right decision. Even allowing for the warmer November you're still using a lot less power.  I did the same sort of experiment and reckoned weather compensation was 15-20% less but I was using 45 deg fixed flow. I also kept the temperature the same all day in both scenarios. 

The other thing you've mentioned that isn't often talked about is comfort.  I prefer a constant temperature rather than ups and downs and weather compensation does this better than thermostats, even when maintaining a constant temperature.  


   
ReplyQuote
Morgan
(@morgan)
Noble Member Member
3941 kWhs
Joined: 3 years ago
Posts: 533
 

@markc 

Nice1.  What temps did you set your weather compensation curve at?

Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.


   
ReplyQuote
(@markc)
Reputable Member Member
93 kWhs
Joined: 3 years ago
Posts: 97
Topic starter  

@morgan It's currently set at 40ºC flow @ -5ºC outside and 20ºC flow @ 20ºC outside.

Although at the moment the overriding offset is at -5.


   