That's right the Seplos BMS manages the pack and communicates with the Inverter.
The JK active balancer I think you are referring to is completely independent and only balances the individual cells, nothing more, so that is very unlikely to be your issue.
I have 3 of these upright Seplos packs from Fogstar, which I've upgraded the firmware (and downgraded) from 1.2-1.3-1.4 and have had no issues at all, also running on a Solis S6 inverter (AC Coupled).
The JK active balancer works very well to keep the cells all aligned.
I haven't upgraded to the 1.5 firmware yet as I'm happy with where all my 3 packs are.
It is a matter of luck. 2ith Fogstar "instructions", too much variation can be expected...
But let's see what fogstar say. It may be a while...
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Issues still under investigation by Solis...
Fogstar do not market their batteries as precision kit. And they may have a point when they say "it was just a blip in comms".
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
SITREP #5 (I think)
Milestone completed today, got my solar array working and attached to my Sunsynk Inverter.
6.4kW - running on X2 MPPT strings.
Question - is there any setting on the sunsynk that I need to consider? no export required (yet) but how does it decide to charge the fogstar battery, prioritise Load and/or charge from grid overnight?
Posted by: @batpredThey shared the graph below. It shows that the battery is momentarily reporting a soc, voltage, etc of 0 and then it all changes back to normal. This is not normal behaviour...
May I pick up this comment from last week?
As I understand it, you have a Jikong Active Balancer and a Seplos BMS connected to the same set of 16 LiFePO₄ cells.
There's nothing wrong with that strategy...
... provided both units have the connections they require.
For the benefit of others, this is what a JK Active Balancer looks like:
It has only low-current balancing wires connected to each of the battery terminals.
That's 17 connections for a 16-cell (16S) battery.
The Active Balancer can handle up to 22 or 24 cells, depending on the model.
I've cut short the extra unused wires in the photo above.
A JK BMS is similar, but would also have the (large) wires which connect to the battery negative terminal.
JK use two blue wires in parallel to make that 0v connection.
The +ve connection to the battery doesn't go to the BMS unit, but straight to the inverter(s), via whatever protection devices you've decided to have.
Since @batpred has a Seplos BMS unit, I would expect it to be positioned on this 0v connection route to the battery negative terminal.
A photo would be useful to clarify that.
So how does that Seplos BMS 'know' the overall battery voltage?
It should have one thin (red) wire connected to the +ve battery terminal.
Ie it's not going to do any balancing between cells, but still needs a voltage to power itself!
That is also the wire which tells the BMS what voltage the battery is currently at,
which it passes on to the (Solis) inverter using the CANbus or RS485 data connection.
Do you have that one red wire present @batpred ?
And where is it connected to on the Seplos BMS?
Save energy... recycle electrons!
The wires are all as per Fogstar "instructions" with some common sense where the instructions skip some steps.
All the boards including the seplos bms, came with the kit order. Fogstar never provided me with anything beyond it. I upgraded the seplos bms firmware to the latest, so the inverter could use the pylontech protocol for bms communication.
Regarding this problem Solis identified, I downloaded the BMS logs. But unfortunately this snapshot info is hourly, so it does not help pinpoint the issue. I would not be surprised if Fogstar emphasises the lack of 0 reads on the BMS logs .. 😌
Solis s6 lists 20 or 30 battery brands in their menu but Fogstar does not figure. They are also not liaising with Solis regarding this, so I am doing my best to keep the diagnosis effort going. And avoid any claims that it is not a supported battery..
As for the jk board, it is accessible via Bluetooth. Do you know if firmware upgrades are available for it? I could open the battery pack but I was so happy when I could close it, so I am trying to hold onto those happy moments. 🙂
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
We're at cross purposes.
You're telling us about Instructions and firmware upgrades...
... whilst I'm writing about little red wires 🤨
Without knowing what you've connected where, I don't think anyone here will be able to say why the inverter is reporting 0v on the battery.
Save energy... recycle electrons!
I have 3 of these units and extensive knowledge of building them (and liaising with Fogstar), particularly around the JK Active balancer.
I wouldn't waste your time trying to help Batpred (I have tried).
Batpred seems to be more interested in how badly Fogstar have treated them.
I don't get it because JK to solis is one of the most common configs for these.
Fogstar are great.
Posted by: @ggwSITREP #5 (I think)
Milestone completed today, got my solar array working and attached to my Sunsynk Inverter.
6.4kW - running on X2 MPPT strings.
Question - is there any setting on the sunsynk that I need to consider? no export required (yet) but how does it decide to charge the fogstar battery, prioritise Load and/or charge from grid overnight?
The settings for this are accessible via either the app or the website, and are found the Equipment tab, then the 3 dots and 'Settings', which will show up the System Mode option. On there you can switch export on and off, prioritise the load and set timers (screenshots show how mine are set). There are 6 slots available, that have to start and end at midnight, but it's only the ones that are ticked in the boxes near the top that trigger grid charging to whatever % level you set.
The minimum level you set is also relevant as the system will revert to grid operation if you hit one of these numbers, which is mine are set to 15 when I don't want it to be grid charging. If this was set to 50 in any period, the batteries would only discharge to that level before switching to grid power.
Hope this helps with your configuration.
130m2 4 bed detached house in West Yorkshire
10kW Mitsubishi Ecodan R290 Heat Pump - Installed June 2025
6.3kWp PV, 5kW Sunsynk Inverter, 3 x 5.3kWh Sunsynk Batteries
MyEnergi Zappi Charger for 1 EV (Ioniq5) and 1 PHEV (Outlander)
User of Havenwise (Full control Jun-Dec 2025, DHW only from early Dec)
Subscriber to MelPump App data via CN105 Dongle Kit
Thank you, seems to have gotten it running.
Question - what generation did anyone get today in the UK?
I got 0.5Kwh on a 6.38kw South facing ground mount. Seems so bad it's faulty 🤣 - but it was a very overcast day.
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 258 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Setback savings - fact or fiction?
@cathoderay The input power is largely determined by...
By RobS , 12 minutes ago
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
@editor, this is now an example of greenwashing in the ...
By Majordennisbloodnok , 23 minutes ago
-
RE: Electricity price predictions
@transparent Im impressed by all your work on this. ...
By JamesPa , 2 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Just to wrap this up here for future readers: The S...
By Batpred , 2 hours ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Welcome to the forums.I assume that you're getting the ...
By Sheriff Fatman , 2 hours ago
-
RE: What determines the SOC of a battery?
I agree. Fogstar confirmed that the Seplos BMS does ...
By Batpred , 3 hours ago
-
RE: Say hello and introduce yourself
@editor @kev1964-irl This discussion might be best had ...
By GC61 , 4 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@benson — as @tasos suggests, plotting multiple variabl...
By cathodeRay , 6 hours ago
-
@painter26 — as @jamespa says, it's for filling and re-...
By cathodeRay , 8 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 18 hours ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 20 hours ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 23 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 24 hours ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 24 hours ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 1 day ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 1 day ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 1 day ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 2 days ago
-
RE: DIY solar upgrade - Considering adding more panels
I know this is a bit old, but it made me wonder what co...
By Batpred , 2 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@majordennisbloodnok Daikin, take note! (In fact, I hav...
By Toodles , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
@mk4 — good work! First, I agree, no evidence of cycl...
By cathodeRay , 2 days ago