Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
I'll leave it tonight and post the graph tomorrow to see it anything starts to make sense !
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody "but after a minute the 3 way valved closed."
I might be wrong but could it be a 3 port, 2 way valve with mid-position?
Operation by the following voltages
My question would be is it a new valve or the original, has it been plumbed correctly, has the wiring to it been disconnected and reconnected correctly?
Was the new tank fully recommissioned and signed off accordingly as per Mixenergy installation manual? It kind of sounds like to me it hasn't been😗 Is that a fair assessment?
@iaack Hi, thanks for the input.
So the situation is that I had a direct mixergy cylinder fitted 3 years ago but plumbed my heat pump ready so that I could add the Mixergy heat exchanger at a later date. The original cylinder failed and the replacement I was sent is an indirect cylinder.
Getting the plate heat exchanger isnt really financially viable at the moment so I thought I would try partially heating it from the coil.
The plumber who installed the new cylinder wasnt very confident with the wiring around my PV diverter so I said I would commision it as he was nice enough to plumb the coil into my system for me.
I dont think I have a mid port valve (I hope!) as I made that mistake in my last house and knew the issue Picture of my valve is below.
This mornings DHW run shows the same pattern. The flow rate is shown in red.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
I may have found the problem. There is a valve on the return side to stop the water when it was originally plumbed in with nowhere to connect to. It was closed! I've opened it and will try again tonight 😁
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Fingers crossed @bontwoody
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
@old_scientist Well it does seem pretty evident that it wouldnt work with it closed 🙂 but its odd OEM was showing flow, so lets see!
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@old_scientist Yip Yip! it worked.
So the DT was small, probably because the stratification pump is off and the coil isnt big, but it got to a 40% charge on its own before it was stopped and the immersion kicked in. COP was pretty dire though averaging about 1.4. Ill try it in eco mode now which should be slower and give the water more time to conduct the heat away.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoodySo the DT was small, probably because the stratification pump is off and the coil isnt big, but it got to a 40% charge on its own before it was stopped and the immersion kicked in. COP was pretty dire though averaging about 1.4. Ill try it in eco mode now which should be slower and give the water more time to conduct the heat away.
If you can turn on the destrat pump COP should improve because the water in contact with the coil will be colder. You will also heat more of the tank likely to a higher temp.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa absolutely. But I think I might have to get the Mixergy Control unit to achieve that. Ill keep my eyes open on ebay. In the mean time I will also drop the desired tank temperature and maybe heat in short batches with a longish gap.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody so pleased it's finally working.
Posted by: @bontwoody@old_scientist Well it does seem pretty evident that it wouldnt work with it closed 🙂 but its odd OEM was showing flow, so lets see!
Yes, this is what threw me when I read your post yesterday - how were you recording flow for 1min with a closed valve, and if there were no flow, why did the controller not immediately raise an E911 error code. Anyway, kinda irrelevant now it's working.
I hope you are able to improve the COP a little. I use Quiet Mode to limit the output when heating my DHW, which hopefully makes it a little more efficient (lower and slower). My LWT normally sits around 8C above the DHW tank temp during the DHW heating cycle. Without Quiet mode enabled, it's a little higher.
Don't forget to turn Quiet Mode OFF when going back to space heating as it does strange things in space heating, as noted by Glyn Hudson here
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
@old_scientist yes. No E911 error. Very odd. Thanks for the link, very interesting.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
So this was last nights DHW run using economic mode.
Im a bit unsure as to what the actual COP was as it states 3.00 for the whole window, but the instanteous values are much lower. Either way its better than last night.
Ive knocked the target temperature back 5C and scheduled two 30 minute runs with a break for tonight. 🙂
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
-
Mixergy HP Cylinder and Solar Diverter
3 years ago
Currently viewing this topic 2 guests.
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 990 Online
- 6,994 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
An article on funding for heat pumps in case anyone is ...
By Jeff , 2 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks @editor , @indevolt-uk Subject to any comments ...
By JamesPa , 10 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 10 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 14 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 14 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 15 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 16 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 18 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 18 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 1 day ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 1 day ago
-
RE: The Grid Says Yes.. Until It Doesn’t: Why Britain's Net Zero Push is Stalling at the Plug Socket
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 4 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 4 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago
-
That’s the solar up and running, I don’t think it’s the...
By David999 , 4 days ago
-
RE: Seeking ideas / information / commiseration - Pure Drive
I agree with @colinc that you can reuse some of it. A s...
By Batpred , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Im trying me best to ignore orangeman, I figur...
By Papahuhu , 5 days ago