Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
I'll leave it tonight and post the graph tomorrow to see it anything starts to make sense !
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody "but after a minute the 3 way valved closed."
I might be wrong but could it be a 3 port, 2 way valve with mid-position?
Operation by the following voltages
My question would be is it a new valve or the original, has it been plumbed correctly, has the wiring to it been disconnected and reconnected correctly?
Was the new tank fully recommissioned and signed off accordingly as per Mixenergy installation manual? It kind of sounds like to me it hasn't been😗 Is that a fair assessment?
@iaack Hi, thanks for the input.
So the situation is that I had a direct mixergy cylinder fitted 3 years ago but plumbed my heat pump ready so that I could add the Mixergy heat exchanger at a later date. The original cylinder failed and the replacement I was sent is an indirect cylinder.
Getting the plate heat exchanger isnt really financially viable at the moment so I thought I would try partially heating it from the coil.
The plumber who installed the new cylinder wasnt very confident with the wiring around my PV diverter so I said I would commision it as he was nice enough to plumb the coil into my system for me.
I dont think I have a mid port valve (I hope!) as I made that mistake in my last house and knew the issue Picture of my valve is below.
This mornings DHW run shows the same pattern. The flow rate is shown in red.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
I may have found the problem. There is a valve on the return side to stop the water when it was originally plumbed in with nowhere to connect to. It was closed! I've opened it and will try again tonight 😁
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Fingers crossed @bontwoody
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
@old_scientist Well it does seem pretty evident that it wouldnt work with it closed 🙂 but its odd OEM was showing flow, so lets see!
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@old_scientist Yip Yip! it worked.
So the DT was small, probably because the stratification pump is off and the coil isnt big, but it got to a 40% charge on its own before it was stopped and the immersion kicked in. COP was pretty dire though averaging about 1.4. Ill try it in eco mode now which should be slower and give the water more time to conduct the heat away.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoodySo the DT was small, probably because the stratification pump is off and the coil isnt big, but it got to a 40% charge on its own before it was stopped and the immersion kicked in. COP was pretty dire though averaging about 1.4. Ill try it in eco mode now which should be slower and give the water more time to conduct the heat away.
If you can turn on the destrat pump COP should improve because the water in contact with the coil will be colder. You will also heat more of the tank likely to a higher temp.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa absolutely. But I think I might have to get the Mixergy Control unit to achieve that. Ill keep my eyes open on ebay. In the mean time I will also drop the desired tank temperature and maybe heat in short batches with a longish gap.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody so pleased it's finally working.
Posted by: @bontwoody@old_scientist Well it does seem pretty evident that it wouldnt work with it closed 🙂 but its odd OEM was showing flow, so lets see!
Yes, this is what threw me when I read your post yesterday - how were you recording flow for 1min with a closed valve, and if there were no flow, why did the controller not immediately raise an E911 error code. Anyway, kinda irrelevant now it's working.
I hope you are able to improve the COP a little. I use Quiet Mode to limit the output when heating my DHW, which hopefully makes it a little more efficient (lower and slower). My LWT normally sits around 8C above the DHW tank temp during the DHW heating cycle. Without Quiet mode enabled, it's a little higher.
Don't forget to turn Quiet Mode OFF when going back to space heating as it does strange things in space heating, as noted by Glyn Hudson here
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
@old_scientist yes. No E911 error. Very odd. Thanks for the link, very interesting.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
So this was last nights DHW run using economic mode.
Im a bit unsure as to what the actual COP was as it states 3.00 for the whole window, but the instanteous values are much lower. Either way its better than last night.
Ive knocked the target temperature back 5C and scheduled two 30 minute runs with a break for tonight. 🙂
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 300 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Our Cosy 9 has been in hush mode for three days. So far...
By KevH , 6 minutes ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 4 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 16 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 18 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 18 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 21 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 1 day ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 1 day ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 3 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 3 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago