Trying to choose between 2 towel rads - which one should I go for?
trying to choose between 2 towel rads. one is smaller has 25mm pipes 4.07L of water content and apparently chucks out 670W @50c. the next one is more expensive is taller but has 22mm pipes holds 6.2L of water and apparently outputs 493W @50c. why the descrepancy in output? surely a larger overall rad with more water content outputs more heat? i will be running it on a system designed for 40c at -3.1c outside so will likely see a lower than design temp in the room but its the biggest rad i can fit.
https://www.heatandplumb.com/acatalog/reina-eos-curved-heated-towel-rail?variation=20406
Possibly 25mm Vs 22 mm pipes. Output depends on surface area principally, but also on form factor. A rad that is twice as tall as another will emit less than twice as much.
Plus measurement margin of course
Output typically varies proportionally to DT^1.3 where DT is the temp diff between the average radiator temp and the room temp. If the 50C you quote is actually DT, output will be 25%. If the 50 you quote is the input flow temp then output will be 55%. Both assuming room temp of 20 and flow-return dt of 5
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @adamktrying to choose between 2 towel rads. one is smaller has 25mm pipes 4.07L of water content and apparently chucks out 670W @50c. the next one is more expensive is taller but has 22mm pipes holds 6.2L of water and apparently outputs 493W @50c. why the descrepancy in output? surely a larger overall rad with more water content outputs more heat? i will be running it on a system designed for 40c at -3.1c outside so will likely see a lower than design temp in the room but its the biggest rad i can fit.
https://www.heatandplumb.com/acatalog/reina-eos-curved-heated-towel-rail?variation=20406
Possibly 25mm Vs 22 mm pipes. Output depends on surface area principally, but also on form factor. A rad that is twice as tall as another will emit less than twice as much.
Plus measurement margin of course
Output typically varies proportionally to DT^1.3 where DT is the temp diff between the average radiator temp and the room temp. If the 50C you quote is actually DT, output will be 25%. If the 50 you quote is the input flow temp then output will be 55%. Both assuming room temp of 20 and flow-return dt of 5
both are delta T50 apparently, one is recalculated from a higher flow temp to be more realistic it says on the site.
Posted by: @adamkboth are delta T50 apparently, one is recalculated from a higher flow temp to be more realistic it says on the site.
In that case output at 40C will be 25% of quoted value, ie not a lot.
Towel rails appear to be like this, options if not enough are
- add an electric element
- fit a standard radiator and a rail over (they exist)
- ignore the problem and allow heat from other rooms to make up the difference (the one I chose)
- fit a standard radiator in addition to the towel rail
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @adamkboth are delta T50 apparently, one is recalculated from a higher flow temp to be more realistic it says on the site.
In that case output at 40C will be 25% of quoted value, ie not a lot.
Towel rails appear to be like this, options if not enough are
- add an electric element
- fit a standard radiator and a rail over (they exist)
- ignore the problem and allow heat from other rooms to make up the difference (the one I chose)
- fit a standard radiator in addition to the towel rail
im thinking of going for the taller one and letting the heat from the plant room plus the flow/return 28mm and the primary 28mm's that are in the ceiling all do there bit, as ive had a rad in a bathroom before and they tend to rust quickly. also the room is insulated on all sides including the floor and ceiling.
- 26 Forums
- 2,396 Topics
- 54.3 K Posts
- 303 Online
- 6,077 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Help me keep the faith with my air source heat pump installation
@adamk I'm observing my own system at low temperatures ...
By dr_dongle , 14 minutes ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
Earthing is definitely a subject which is best approach...
By Transparent , 15 minutes ago
-
RE: Running from backup generaor in powercut?
Right on topic, Storm Goretti has done its thing and we...
By Mars , 1 hour ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
I doubt that matters, ToU tariffs are for the benefit o...
By JamesPa , 17 hours ago
-
RE: Free Ecoheat Heat Pump Install
@deltona Yes older houses are problematic like that, bu...
By bontwoody , 20 hours ago
-
RE: Radiator sizing sanity check
As I mentioned early on the cost of supplying and fitti...
By JamesPa , 22 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
I hadn't spotted that there were two pumps in the UFH (...
By JamesPa , 24 hours ago
-
RE: Setback savings - fact or fiction?
Never assume it makes an ass of u and me! You need the...
By JamesPa , 1 day ago
-
RE: New Mitsubishi Ecodan 11.2kW installation - L9 errors and maybe more
Before I answer your specific questions just one more t...
By JamesPa , 1 day ago
-
RE: Electricity price predictions
Great point, one of the key ones in my chat with Octopu...
By Batpred , 1 day ago
-
RE: New Fogstar 15.5kWh upright solution
Let me point out that there are many Chinese suppliers ...
By Transparent , 2 days ago
-
RE: Weather compensation- why you should use it
@majordennisbloodnok — The Two Ronnies Mastermind sketc...
By cathodeRay , 2 days ago
-
Just realised that this image of the cylinder cupboard ...
By Sheriff Fatman , 2 days ago
-
RE: Rodents! A word of warning for heat pump owners
Two thoughts: 1: Let's ask @david-s if Primary Pro in...
By Transparent , 2 days ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
In the diagram below, I describe my understanding of th...
By Batpred , 2 days ago
-
I need to have a look out for it. I know IBM feeds some...
By Batpred , 2 days ago
-
-
RE: Daikin Atherma ASHP Cycling 6 Times an Hour?
Thanks for your reply. Yes that's a good idea to try a...
By John Marshall , 2 days ago
-
RE: Hot water heating in parallel with space heating
An external heat exchanger would need a pump which woul...
By bontwoody , 2 days ago
-
RE: Gen 6 Samsung ASHP losing 20C of DHW in 60 min directly after generation
@ecobaker Thanks for this. I've had it in both slots. ...
By andbeck , 3 days ago