Trying to choose between 2 towel rads - which one should I go for?
trying to choose between 2 towel rads. one is smaller has 25mm pipes 4.07L of water content and apparently chucks out 670W @50c. the next one is more expensive is taller but has 22mm pipes holds 6.2L of water and apparently outputs 493W @50c. why the descrepancy in output? surely a larger overall rad with more water content outputs more heat? i will be running it on a system designed for 40c at -3.1c outside so will likely see a lower than design temp in the room but its the biggest rad i can fit.
https://www.heatandplumb.com/acatalog/reina-eos-curved-heated-towel-rail?variation=20406
Possibly 25mm Vs 22 mm pipes. Output depends on surface area principally, but also on form factor. A rad that is twice as tall as another will emit less than twice as much.
Plus measurement margin of course
Output typically varies proportionally to DT^1.3 where DT is the temp diff between the average radiator temp and the room temp. If the 50C you quote is actually DT, output will be 25%. If the 50 you quote is the input flow temp then output will be 55%. Both assuming room temp of 20 and flow-return dt of 5
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @adamktrying to choose between 2 towel rads. one is smaller has 25mm pipes 4.07L of water content and apparently chucks out 670W @50c. the next one is more expensive is taller but has 22mm pipes holds 6.2L of water and apparently outputs 493W @50c. why the descrepancy in output? surely a larger overall rad with more water content outputs more heat? i will be running it on a system designed for 40c at -3.1c outside so will likely see a lower than design temp in the room but its the biggest rad i can fit.
https://www.heatandplumb.com/acatalog/reina-eos-curved-heated-towel-rail?variation=20406
Possibly 25mm Vs 22 mm pipes. Output depends on surface area principally, but also on form factor. A rad that is twice as tall as another will emit less than twice as much.
Plus measurement margin of course
Output typically varies proportionally to DT^1.3 where DT is the temp diff between the average radiator temp and the room temp. If the 50C you quote is actually DT, output will be 25%. If the 50 you quote is the input flow temp then output will be 55%. Both assuming room temp of 20 and flow-return dt of 5
both are delta T50 apparently, one is recalculated from a higher flow temp to be more realistic it says on the site.
Posted by: @adamkboth are delta T50 apparently, one is recalculated from a higher flow temp to be more realistic it says on the site.
In that case output at 40C will be 25% of quoted value, ie not a lot.
Towel rails appear to be like this, options if not enough are
- add an electric element
- fit a standard radiator and a rail over (they exist)
- ignore the problem and allow heat from other rooms to make up the difference (the one I chose)
- fit a standard radiator in addition to the towel rail
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @adamkboth are delta T50 apparently, one is recalculated from a higher flow temp to be more realistic it says on the site.
In that case output at 40C will be 25% of quoted value, ie not a lot.
Towel rails appear to be like this, options if not enough are
- add an electric element
- fit a standard radiator and a rail over (they exist)
- ignore the problem and allow heat from other rooms to make up the difference (the one I chose)
- fit a standard radiator in addition to the towel rail
im thinking of going for the taller one and letting the heat from the plant room plus the flow/return 28mm and the primary 28mm's that are in the ceiling all do there bit, as ive had a rad in a bathroom before and they tend to rust quickly. also the room is insulated on all sides including the floor and ceiling.
- 22 Forums
- 2,088 Topics
- 45.8 K Posts
- 50 Online
- 3,374 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: My misgivings about installing ASHP and solar panels via the ECO4 scheme...
For the sake of balance, I will share that our ECO4 exp...
By Old_Scientist , 2 hours ago
-
RE: Commencing on an ASHP Installation Process
@sheriff-fatman just keep an eye on them... definitely ...
By Mars , 4 hours ago
-
RE: How not to install a heat pump
You are right. Thinking on this has evolved over the p...
By JamesPa , 17 hours ago
-
RE: Vaillant AroTherm Plus 7kW
Thanks for the comprehensive write-up, I am considering...
By Scalextrix , 18 hours ago
-
@ashp-bobba ‘Wattson, how many grammes of Co2 are you r...
By Toodles , 19 hours ago
-
RE: DHW SET UP with Samsung gen 5
Thats good news indeed, you are very likely almost ther...
By JamesPa , 20 hours ago
-
RE: Renewables & Heat Pumps in the News
Ain't consumerism wonderful! Just because EVs could b...
By Majordennisbloodnok , 21 hours ago
-
RE: Plate heat exchanger considerations
As far as I can tell my vented system would have a peak...
By Scalextrix , 22 hours ago
-
RE: Air Changes per Hour - ACH and the MCS requirement
There have been a few discussions dotted around (e.g. I...
By Declan90 , 1 day ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Having made some enquiries locally I have found a compa...
By Morgan , 1 day ago
-
RE: I don't need any heating in the summer. How do I turn my Samsung heat pump off?
Thats great Someone else is struggling with this in a...
By JamesPa , 1 day ago
-
@bart Best of luck moving forward, I look forward to he...
By ASHP-BOBBA , 2 days ago
-
RE: Ecodan EMP2 kit - is it any good?
Please note: heat meter accuracy at 95+% is as long as ...
By ASHP-BOBBA , 3 days ago
-
RE: Flow Rate & Low Loss Headers
Houses with reasonably low loss aren't going to require...
By JamesPa , 3 days ago
-
RE: Help me keep the faith with my air source heat pump installation
If it's running on WC then at night it's quite likely t...
By JamesPa , 3 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@majordennisbloodnok That’s OK as long as the ‘Terminol...
By Toodles , 4 days ago