@old_scientist and @allyfish , thank you both for this. We currently have a 23yr old Oil boiler, installed in a then new-build. I have no doubt that some of the sludge festering in the pipe and emitter system is of the same vintage.
I am fairly confident we have 22mm F&R from the boiler going up and around the first floor, with 10mm u-bore teeing off to all the rads on both floors. the ratio of 10mm to 22mm copper is unknown and will only be bottomed-out by inspection with a Mk I Eyeball, viz. by lifting the first-floor boards; which no doubt are chipboard, just for added interest to the task.
We are moving into retirement mode, hence will be spending more daytime at home; and given the Oil boiler has passed its prime it will likely need a "tech refresh" in the nearer future too. This why we are considering ASHP for our energy needs; likely looking at PV solar/battery too. Insulation is 'ok', building heat loss is 9.6kW. Windows were replaced 2017 and the loft will be treated to another 150mm duvet.
One plumbing option is to re-pipe the first-floor copper with fit-for-purpose sizes and spec-up rads for a high-flow, lower-temp air-source system. The intent is to route into the ground floor concrete to lay pipe throughout for UFH. Admittedly it'll be a huge disruption, albeit only a few weeks; but we are fortunate to have a contingency for temporary accommodation, namely a caravan.
Mad ? ... borderline ... but more a case of investing in our future energy needs, with lower running costs while delivering increased comfort as our needs change over time. We're not really looking for ROI, per se, although it won't be long into the future where oil-fired heating will reduce a property's marketability and sale price: just my pov.
Posted by: @colincMad ? ... borderline ... but more a case of investing in our future energy needs, with lower running costs while delivering increased comfort as our needs change over time.
I had similar thoughts with my heat pump and, to a lesser extent EV (I have had solar panels from 2011).
Having made the leap I have absolutely no regrets with either. Both are a far superior experience with lower running costs and a reduced dependence on foreign despots. Of course they complement the solar as well so Im now pretty well insulated from energy price fluctuations. My original motivation was largely environmental but actually there are very immediate personal benefits.
I don't have batteries yet, because I cant quite make the business case work and I cant see a robust environmental case. There will come a time when it will, I'm sure, at which point I will do that also.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa Likewise in many respects; we don’t have an EV or even a push along scooter (poor sight, keep death off the roads!), however, we do have a battery. ‘Twas expensive and thought of slightly as a luxury; with continuously rising energy prices and the availability of TOU tariffs, that luxury is now more of a bonus!
We have solar panels and we have very good insulation; all these investments provide a warm feeling too. We have a heat pump and are all-electric and thus don’t have a gas meter or pay more than the one standing charge. We reclaimed our investment from the bank as we had paid on a credit card for a Wind Turbine project that went down the pan and we are still awaiting our first payments (possibly next summer) on our solar farm project investment. Regards, Toodles,
Toodles, heats his home with cold draughts and cooks food with magnets.
Well, you must have been an "early adopter" for solar panels; what I describe as "bleeding edge" as opposed to the 'leading edge", and will have gained considerable experience over that time as this industry has developed.
I would agree there are many positive aspects for the environment for solar panels, athough my buy-in is somewhat limited to the way that lobbyists (corporate, environment & academia), MSM, and political factions 'across the house' are 'weaponising' the whole environmental debate to suit their own agenda and objectives. Basically, the 'room' needs some adults present who are not hell-bent on pursuing their confirmation-bias; sadly a human trait that bears no fruit.
Regarding batteries and the environment I take your point, and have seen first-hand the way rare-earth extraction continues to blot and poison the landscape in The Congo and DRC: the West is as much a culprit and catalyst as China. Maybe the development of exploiting sodium, perhaps replacing lithium, might change this; albeit it's a different 'beast' in terms of its capability profile currently.
In my experience a Business Case can be skewed to suit the aim; one only has to look at HMG's decades of fairly regular incompetence since WWII for examples.
I doubt much will change on my watch, so meantine I will be investing in PV & Battery as the "better evil"; and as you suggest, achieving a small level of energy independence.
The practicalities of investing in Wind and Solar is something I no little about; and although it does sound interesting, rightly or wrongly I am not very motivated that way. There seems to be multi-billion £/$ investment pouring into large scale battery storage currently, which is really the only way to make sense of the billions already invested in wind and solar energy. It's a shame that tidal and wave energy has not gained much traction in R&D investment.
The cynic in me suggests that because it's fairly low-tech there's not enough of a "big bucks" incentive for corporate entities to exploit. That said, at their source: sun, wind, and sea energy capture are all fairly basic technically. The operating environment and the energy storage is more of a challenge.
However, we seem to have the gumption to put wind turbines and solar panels in almost any environment, so why not corall the tides and waves on an industrial scale too ?
Last time I looked at a map we are pretty much surrounded by water; depending of course on one's view of nation boundaries, but I live in hope.
Posted by: @colincThe practicalities of investing in Wind and Solar is something I no little about; and although it does sound interesting, rightly or wrongly I am not very motivated that way. There seems to be multi-billion £/$ investment pouring into large scale battery storage currently, which is really the only way to make sense of the billions already invested in wind and solar energy. It's a shame that tidal and wave energy has not gained much traction in R&D investment.
The cynic in me suggests that because it's fairly low-tech there's not enough of a "big bucks" incentive for corporate entities to exploit. That said, at their source: sun, wind, and sea energy capture are all fairly basic technically. The operating environment and the energy storage is more of a challenge.
However, we seem to have the gumption to put wind turbines and solar panels in almost any environment, so why not corall the tides and waves on an industrial scale too ?
Last time I looked at a map we are pretty much surrounded by water; depending of course on one's view of nation boundaries, but I live in hope.
and we have some of the strongest tidal flows anywhere on the globe.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
@jamespa most I've ever seen is 5 and often 4, surely any more than two and you need to ask 'why?'
Posted by: @dgclimatecontrol@jamespa most I've ever seen is 5 and often 4, surely any more than two and you need to ask 'why?'
I assume you are referring to this post https://renewableheatinghub.co.uk/forums/postid/50045/ and yes indeed you do have to ask why!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa Yes that post.
@colinc good luck with your project!
UFH is the absolute best from both comfort and ASHP efficiency. We have it in the extension and wish we had elsewhere in the house. But we chickened out on initial house refurb since we have solid concrete floors and they would have all had to come up for the 6inch of polystyrene insulation to go in. The mess would have been horrible and even though we were still in rented we didn’t even get quotes for it.
Sadly our surveyor said, ‘you don’t need to dig the floor up all UFH systems add insulation’ (2mm of it!). A quick calculation by us stopped that approach, using electrical ufh to heat the rest of the street via the garden, no thanks. That was 15years ago but the surveyor world hasn’t moved on much, just before the energy crisis a neighbour doing a refit had electric ufh fitted in his lounge in his solid floor house and found it never even got the room tepid whilst nearly bankrupting him.
You are doing the right thing by planning for a water based system. You get the benefit of the COP on electricity usage.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP 4.7) open system operating on WC
Dear Mars,
Thanks for writing this postI'm trying to get my head around this, my installer put in a 16kw pump with 28mm pipework and not only is heating inadequate but got flow sensor switch warnings and it seems cylinder is damaged too. Trying to get NICEIC to investigate is like getting water out of stone... the above seems below industry standard but I cannot find a source, wonder if you have any tips?
Thanks in advance, A
Alex, on the face of it, a 16 kW heat pump on 28 mm primary pipework should immediately raise questions. At a typical heat pump design, 16 kW requires roughly 0.76 litres per second of flow, which is about 45-50 litres per minute. At sensible velocities (around 1 m/s), 28 mm copper is generally comfortable up to roughly 12 kW. Push it to 16 kW and you are either running excessive velocities, creating high pressure drop or simply not achieving the required flow. None of those outcomes are acceptable in a properly designed system. I would imagine that flow switch warnings are consistent with that. If the pump cannot physically achieve the minimum required flow rate because the pipework is too restrictive, you will see intermittent or persistent flow errors. In terms of “industry standard”, there is no single public rule that says “thou shalt use 35 mm at 16 kW”, but the principles are set out in the CIBSE Domestic Heating Design Guide and manufacturer technical manuals. The correct approach is to calculate required flow rate from output and delta T, then size pipework to keep velocity and pressure drop within acceptable limits. If your installer cannot produce those calculations, that in itself is revealing. Having said that, I'm still to see an installer provide this level of information which means most don't do the maths. If you are pursuing NICEIC, be aware they are primarily an electrical certification body. They are not hydraulic design specialists. I think it's NAPIT you're after. I would suggest you formally request the following in writing from the installer in you do pursue a case.
- The design heat loss calculation
- The design flow temperature and delta T used
- The calculated required system flow rate
- The pipe sizing and velocity calculations for the primary circuit
- The commissioning sheets showing achieved flow rate and pump settings
If they cannot demonstrate that 28 mm was sufficient for 16 kW at their stated delta T, you have a technical basis for challenge. Keep everything documented. Do not rely on phone conversations. Feel free to post findings here.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
- 27 Forums
- 2,520 Topics
- 58.6 K Posts
- 464 Online
- 6,800 Members
Join Us!
Worth Watching
Latest Posts
-
Issue with a Grant Air Source Heat Pump & Tado Smart Thermostat
Hi all I'm having some trouble with a Grant ASHP and ...
By Renewables345 , 30 minutes ago
-
RE: Underfloor Heating Installation Issues with Heat Pump
We suffered a water leak last year in two rooms and had...
By MartinHook_UK , 41 minutes ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Now seems a good time to summarise the costs and effici...
By benson , 50 minutes ago
-
RE: Heat Pump vs New Gas Boiler for Inherited House - Worth the Extra Cost?
*** I now see @jamespa has already posted but will stil...
By cathodeRay , 2 hours ago
-
RE: Tell us about your Solar (PV) setup
@mk4 Charge to 100%, discharge down to 10%.
By bobflux , 2 hours ago
-
RE: Daikin Altherma 3 LT compressor longevity question
This mess is intriguing: I wonder if this represent...
By bobflux , 3 hours ago
-
RE: Connecting Growatt SPH5000 over wired ethernet rather than wireless
The simplest wired option is usually the Growatt Ethern...
By Jonatan , 8 hours ago
-
RE: Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
ASHPs do have a minimum compressor speed. The minimum h...
By bobflux , 14 hours ago
-
RE: Electricity price predictions
@jamespa And it seems some of the nasty public cloud...
By Batpred , 15 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
Technology is rapidly advancing. BBC News reported th...
By Transparent , 18 hours ago
-
What matters for flow and pressure drop is internal dia...
By bobflux , 19 hours ago
-
RE: Do Fridges and Freezers have COP ratings?
@editor Thank you all for your replies and submitted in...
By Toodles , 21 hours ago
-
I know and yes. The secondary deltaT wont necessaril...
By JamesPa , 1 day ago
-
RE: Designing heating system with air to water heat pump in France, near Lyon
Just love the way you put it! 🤣
By Batpred , 2 days ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thank you for sharing. So it seems that your Schneid...
By Batpred , 2 days ago
-
RE: Forum updates, announcements & issues
@upnorthandpersonal thanks for the thoughtful, consider...
By Mars , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@mk4 All 21 panels have their own Enphase IQ7a microinv...
By Toodles , 2 days ago
-
RE: Setback savings - fact or fiction?
Great, so you have proven that MELCloud is consistently...
By RobS , 3 days ago
-
RE: Mitsu PUHZ120Y 'Outdoor Temp 'error?
Thanks David & James It almos...
By DavidAlgarve , 3 days ago
-
RE: Surge protection devices SPDs
@trebor12345 - your original Topic about the right type...
By Transparent , 3 days ago
-
RE: Help needed with Samsung AE120RXYDEG
@tomf I’ve been sent this from a service engineer at Sa...
By Mars , 3 days ago
-
RE: Buying large amp bidirectional RCD and RCBO
Yes... I went through this particular headache and ende...
By bobflux , 4 days ago
-
O-oh! Let's take this as an opportunity to 'pass the ...
By Transparent , 4 days ago