help sizing rads based on room by room heat loss
Posted by: @jamespaPosted by: @adamk@jamespa thanks for the info but I think I must have something wrong. The heat loss for the whole house is about 7.5kw. The room is only 3.756m x 3.686m. Current rad is a P+ 1450mm 380mm.
Have you got the loss calculations, if so perhaps you could post?
My house loss is also about 7kW and I had one room well over 1kW, went for a Mitsubishi fancoil for that, very nice piece of kit
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa heat loss list on first post.
it’s the one that says nearly 2kw, I’ve just split it into 2 rooms as we’re going to put a sliding wall between the dining and living room, plus one rad is in one area and another in the other.
Posted by: @adamk@jamespa heat loss list on first post.
it’s the one that says nearly 2kw, I’ve just split it into 2 rooms as we’re going to put a sliding wall between the dining and living room, plus one rad is in one area and another in the other.
The living/lounge and kitchen in your list aren't dissimilar to mine and were, for me, by far the most difficult rooms to find radiators for. I ended up with four rads in total covering a kitchen/living room and a separate long living room. The balance between two halves of each room wasn't perfect, but it hasn't mattered in practice. One of the four rads was a mitsubishi fancoil and another was the existing rad with a bunch of computer fans added (not sure how much difference that has actually made)..
I avoided type 33 as I had already fitted one in the bedroom (the other difficult room) and the wife hates it. Personally I quite like it as it looks 'serious - but I would advise to look at an example of a type 33 before settling on one, they are quite noticeably deeper.
Having got a fancoil I wish we had got a couple more. They are nice and neat, quite small, not particularly noisy and with three of them I might have been able to do some meaningful cooling in summer. Jaga Strada are also popular fan radiators and those who have them seem to rate them highly..
I was designing for 45C where the oversize factor (ie the factor by which you have to divide the DT50 output to get the output at the chosen FT) is 2.8. At 40C its 3.9 which makes quite a difference. In practice Im running at 42 so half way in between, presumably because the loss was a bit overestimated.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @adamk@jamespa so if i have a 1988w rad at 40c @-3.1 it will only be 509w?
If its 1988W at DT 50, which is how most radiators are specified (but note not all, one brand is specified at DT70!) then yes that's right. At FT40 and RT 20 your average DT is 17.5. So your rad output is 1988*(17.5/50)^1.3 = 509W.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 22 Forums
- 2,073 Topics
- 45.5 K Posts
- 67 Online
- 3,353 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Solar Power Output – Let’s Compare Generation Figures
Well we finished this month with an all time record! Ev...
By Andris , 10 hours ago
-
RE: 5 Star Service from Havenwise
Oh good! I was wondering when/if you might pick them ...
By Transparent , 12 hours ago
-
RE: Air Changes per Hour - ACH and the MCS requirement
update - my old installer insisted on a heat loss of 11...
By MatWin , 13 hours ago
-
I agree it's not very helpful. Generally, the max heat ...
By Old_Scientist , 15 hours ago
-
RE: Commencing on an ASHP Installation Process
I think therein lies the problem. Ratio of quotes to i...
By JamesPa , 1 day ago
-
RE: Why Your MCS-Certified Installer Might Not Be As Competent As You Think
Hive and most other smart thermostats don't play well w...
By JamesPa , 2 days ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
Thanks for the input. I've been running various experim...
By Grahamh-uk , 2 days ago
-
RE: Radiators downstairs are cooler at the bottom after ASHP install
@melonbuffet Hi, this sounds great is you are getting 5...
By ASHP-BOBBA , 2 days ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
I believe there's another reason that network upgrades ...
By Transparent , 2 days ago
-
RE: What’s the modern take on advised types of insulation?
@jeff I am sorry @jeff if I have misunderstood what you...
By Toodles , 3 days ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@editor Cobbler’s Mantra that!
By Toodles , 3 days ago
-
RE: Renewables & Heat Pumps in the News
Australia Blue, the first wind farm in Western Victoria...
By Morgan , 4 days ago
-
RE: Flow rate discrepancy between ASHP and manifold
That's useful thanks, I hadn't seen that table before. ...
By AshRolls , 4 days ago
-
In principle I agree, @johnmo, but with provisos. The...
By Majordennisbloodnok , 4 days ago
-
RE: Heat pump installation and BUS Grant timings
@jamespa Thats how I understood it too. 🙂
By ASHP-BOBBA , 5 days ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
@sallyl That sounds about right if they are re-filling ...
By Brendon Uys , 5 days ago
-
I wouldn't be so sure about that. Heat pump designers ...
By JamesPa , 5 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@toodles they're a rowdy bunch!
By Mars , 6 days ago
-
RE: Home energy storage & battery register
@jamespa To a certain extent, by exporting to the grid ...
By Toodles , 6 days ago