Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
help sizing rads based on room by room heat loss
Posted by: @jamespaPosted by: @adamk@jamespa thanks for the info but I think I must have something wrong. The heat loss for the whole house is about 7.5kw. The room is only 3.756m x 3.686m. Current rad is a P+ 1450mm 380mm.
Have you got the loss calculations, if so perhaps you could post?
My house loss is also about 7kW and I had one room well over 1kW, went for a Mitsubishi fancoil for that, very nice piece of kit
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa heat loss list on first post.
it’s the one that says nearly 2kw, I’ve just split it into 2 rooms as we’re going to put a sliding wall between the dining and living room, plus one rad is in one area and another in the other.
Posted by: @adamk@jamespa heat loss list on first post.
it’s the one that says nearly 2kw, I’ve just split it into 2 rooms as we’re going to put a sliding wall between the dining and living room, plus one rad is in one area and another in the other.
The living/lounge and kitchen in your list aren't dissimilar to mine and were, for me, by far the most difficult rooms to find radiators for. I ended up with four rads in total covering a kitchen/living room and a separate long living room. The balance between two halves of each room wasn't perfect, but it hasn't mattered in practice. One of the four rads was a mitsubishi fancoil and another was the existing rad with a bunch of computer fans added (not sure how much difference that has actually made)..
I avoided type 33 as I had already fitted one in the bedroom (the other difficult room) and the wife hates it. Personally I quite like it as it looks 'serious - but I would advise to look at an example of a type 33 before settling on one, they are quite noticeably deeper.
Having got a fancoil I wish we had got a couple more. They are nice and neat, quite small, not particularly noisy and with three of them I might have been able to do some meaningful cooling in summer. Jaga Strada are also popular fan radiators and those who have them seem to rate them highly..
I was designing for 45C where the oversize factor (ie the factor by which you have to divide the DT50 output to get the output at the chosen FT) is 2.8. At 40C its 3.9 which makes quite a difference. In practice Im running at 42 so half way in between, presumably because the loss was a bit overestimated.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @adamk@jamespa so if i have a 1988w rad at 40c @-3.1 it will only be 509w?
If its 1988W at DT 50, which is how most radiators are specified (but note not all, one brand is specified at DT70!) then yes that's right. At FT40 and RT 20 your average DT is 17.5. So your rad output is 1988*(17.5/50)^1.3 = 509W.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 27 Forums
- 2,783 Topics
- 65.6 K Posts
- 1,371 Online
- 7,187 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: How should the Boiler Upgrade Scheme be reformed?
It's the reverse, the hybrids need less space. The back...
By Temperature_Gradient , 6 minutes ago
-
RE: Replacing Storage Heaters with a Heat Pump in a Stone Cottage
This tool lets you input the makeup of your wall, ceili...
By bobflux , 2 hours ago
-
Over the years, due to the non barrier PEX underfloor h...
By bobflux , 12 hours ago
-
RE: Getting closer to a finished Haier system
All the 45° elbows required for getting the primaries i...
By Singlespeed , 14 hours ago
-
RE: Tesla Powerwall (2) Calibration Cycles
@papahuhu Likewise, the main ‘extra’ relates to TOU tar...
By Toodles , 19 hours ago
-
RE: DIY Heat Pump Installations: Navigating Legal and Regulatory Hurdles
Thanks for the reference @jamespa I can't see any te...
By Transparent , 2 days ago
-
RE: battery storage without solar
Indeed, current on the grid input = current used for ch...
By bobflux , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
@papahuhu @papahuhu A lot of tears and sweat went into ...
By Andris , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
We have the same problem, 12 mature trees clip the morn...
By Papahuhu , 3 days ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
I had a battery and inverter installed a while ago, my ...
By Batpred , 3 days ago
-
RE: Is This Initial Free Quote From Octopus Trusted Partner Reasonable?
@ltron2 The EPC on our house is A-92, however that i...
By Rob of York , 3 days ago
-
RE: Heat pump branding. Clever, contemporary… or a bit too much?
The layout is confusing - much better like this: We b...
By downfield , 4 days ago
-
RE: Is it just me, or does tradesperson timekeeping and communication drive you absolutely mad?
My experience, backed up by opinions from various frien...
By Majordennisbloodnok , 4 days ago
-
RE: Analysis of the economics of switching to an A2W ASHP compared to other heat sources
I had a meeting today with a company based out of Swede...
By Mars , 5 days ago
-
RE: Review your electricity provider
We were with Octopus in our old house and it was fault...
By ian33a , 5 days ago