Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
UFH downstairs and radiators upstairs balancing question
Can I pick you brain about mine
260m2 house.
2 x UFH manifold, one 150m2 manifold in new extension, one 50m2 in old ground floor. 110m2 rad run for bedrooms above.
Ive a LLH, 2 primary circuit pumps, one pump off the header for rads, one shunt pump to the manifolds and one pump on each manifold.
Its now running all open with only one stat, no UFH stat control. The design has not been great and its been a struggle, this is my second winter. The UFH can heat those areas at very low flow temps, rarely above 30 degrees unless its close to zero or below outside.
The temp gap to rooms above can get quite wide, sometimes a bit too wide.
Say my flow/return is 30/25, the DT of the rads is only 1, and the UFH slightly over 5. I’ve spoken to my installer about getting more DT off the rads. The advice has been in increase the speed of water through the UFH, turn all pumps to max. My UFH is a mix mainly 12mm low profile pipes and some 16mm traditional. Putting the pumps to max does nothing unless I also open the flows the UFH loops, but if I do that, parts of the house that only need 20% of the heat loss can consume much of the flow of the primary and get even warmer. Am I best to start to restrict flows into the house that get too much heat. My installer warmed me not to do this the water would be flowing to slowly in that part and the return would be too cold
Any before you ask, no they have not balanced it for me, they have offered to come back at some point.
@davidnolan22 Hi, ok first of all it very hard to truly balance duel UFH circuits and rads when they have a shunt, Splan valve and a manifold pumps, usually we would want an open loop system to have one pump controlled by the ASHP supplying the whole balanced system. one pump inline with another is a different challenge. Also its unlikely unless your radiator is a K3 and very large it will heat a medium sized room of say 4x4m2 at 30/25.
Brands Like Ecodan and many others have duel zone control and can modulate the flow slightly to different circuits but you would need to run the system hotter and unfortunately blend back down at the UFH manifolds to control the flow temperature which then can also cause a higher return on the flow and short cycle the ASHP.
You may find that if the UFH loops are over designed for a flow rate of 40℃ and the rads are under designed for a flow rate of 30℃, so if you choose 30 the rads are short and if you choose 40 the UFH is over.
Some tricks that may work.
If you have multiple loops on the UFH example: lets say you have 4 loops in the dining area spread out like loops 123and 4 in order left to right you could close down loops 2 and 4 or 1 and 3, this would half the power of the UFH but keep it kind of spread out, if it is slightly over designed, this would then let you run the system at 40/35 and add more power to the rads.
Just make a note by taking pictures or videos of where settings are before adjusting anything so you can always put it back where it was.
Any heating system has little chance of working correctly if it is not balanced.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Posted by: @ashp-bobba@davidnolan22 Hi, ok first of all it very hard to truly balance duel UFH circuits and rads when they have a shunt, Splan valve and a manifold pumps, usually we would want an open loop system to have one pump controlled by the ASHP supplying the whole balanced system.
Isn't this a great example of KISS!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Hi, thanks for reply.
I've started to play, its still very warm outside so need it to get cooler, but I've closed 2 loops out of 9 where we are most overpowered with the UFH, This did increase the flow temp to the rads by a degree (I was getting a small amount of blending at the LLH, the rads is the lower out from the header so got blended by a degree). the rads are now seeing the primary flow temp. So I assume i've just nudged the secondary flow (hard to measure) to slightly below the primary flow (31 l/min)
@davidnolan22 If I understand you correctly, you are saying that the output to the radiators is being fed from the lower port on the LLH.
Normal practice is that the top port opposite the flow from the heat pump would feed the heating circuit. The lower ports are for the return from the end of the heating pipework into the LLH and the port on the opposite side feeds back to the heat pump (return). This means that the flow from the heat pump enters one side at the top of the LLH and the flow out to the radiators is on the opposite side, also at the top; the return enters the LLH on the same side as the port that flows to the radiators but at the bottom, and the fourth port at the bottom is the return to the heat pump. This is the normal route to reduce distortion (mixing) to the minimum; at this point it is advantageous to minimise any difference in temperature across the ports by controlling the pump’s flow rate to further reduce didtortion. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
sorry, my bad. Its a 6 port LLH. of the 2 higher ones, the rad circuit is the lower of those 2.
Posted by: @davidnolan22
sorry, my bad. Its a 6 port LLH. of the 2 higher ones, the rad circuit is the lower of those 2.
I wonder what the logic of this was, that will be the cooler of the two whereas I would have thought you want the rad circuit on the warmer.
Never mind it shouldn't matter that much, how is the balancing going, are you getting closer? From what I recall your problem is that its too cool upstairs where you have radiators, and too warm downstairs, where you have UFH. More flow through the radiators and less flow through the UFH should sort this unless the radiators are too far undersized in the first place; has adjusting the relative flows made any difference?
Posted by: @davidnolan22Say my flow/return is 30/25, the DT of the rads is only 1, and the UFH slightly over 5. I’ve spoken to my installer about getting more DT off the rads.
Dont! The adjustment you need to make will reduce the DT through the rads and will increase the DT through the UFH. Thats the mechanism by which the UFH emits less (because the average temperature is reduced) and the rads emit more (because their average temperature is increased), which is what you are trying to achieve. DT is much misunderstood!
Just to be clear the way the balancing works is this:
The loss from an emitter (to the room) is determined by the average temperature of the emitter.
If you increase the flow through an emitter then the average emitter temperature will increase because the DT across the emitter decreases as a result of the increased flow. This will increase the loss from the emitter to the room (which will cause the DT to increase a bit, so if you are calculating it you need to iterate, but the real world does this for you).
Conversely
If you decrease the flow through an emitter then the average emitter temperature will decrease because the DT across the emitter increases as a result of the reduced flow. This will decrease the loss from the emitter to the room.
Thus, given what you have told us, Im expecting your system to be in balance (for temperature) when the DT across the radiators is relatively low and the DT across the UFH relatively high.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Hi, thanks for getting back to me.
this week will be more interesting as its getting colder here is Sheffield.
Can you explain the DT comment a bit more. If the temp is coming in at say 28 degrees to the rads and leaving at 28, then the energy transfer must be zero. So if the DT is 1, then is it not that only a bit of heat is transferred to the room at any given flow rate. The rads are sized a bit small for the flow temp the UFH needs, so I need a little more temp. I've closed 2-3 of the UFH heating loops as suggested but its not cold enough really to see it its helped.
I'll keep you updated
Posted by: @davidnolan22Can you explain the DT comment a bit more. If the temp is coming in at say 28 degrees to the rads and leaving at 28, then the energy transfer must be zero.
Yes thats true, but that cant happen unless the room temperature is 28C!
Its best in most circumstances to think of DT as a consequence of other things, not something you control. The emissions from a radiator are determined by its average surface temperature in relation to the room temperature. The first of these is principally determined by the flow temperature. So a radiator of a given area with an average surface temperature of 28C and a room temperature of 20C will emit a certain amount of heat. This, together with the flow rate will determine the DT. There is a bit of circularity here because a higher DT means a lower average surface temperature for any given flow temperature, so to do the calculation you have to iterate a few times (nature of course does the iteration for you). Thats why a lower DT (which, if all else stays the same, can be achieved by increasing the flow rate) will actually result in a higher emission from the radiator in any given set of circumstances.
To complicate matters further some heat pumps have a DT control loop. This secondary control loop modulates the water pump to target a specific system level DT. However the DT variations as described above will still occur at the level of the individual emitters, so balancing for room temperature is still effective.
Posted by: @davidnolan22The rads are sized a bit small for the flow temp the UFH needs, so I need a little more temp. I've closed 2-3 of the UFH heating loops as suggested but its not cold enough really to see it its helped.
Yes. So you can:
- reduce the DT across the rads by increasing the flow rate through them. This increases their average surface temperature for any given FT. The effect is limited though - if you start with a DT of 5 then the best you can get (at flow rate = infinity) is a DT of 0, 2.5C higher average temp
- increase the DT across the UFH by reducing the flow rate through it. This reduces the average surface temperature for any given FT. The effect is essentially unlimited, with zero flow rate (ie closing loops), the average surface temp falls to the room/slab temp so there are no heat is emitted
- increase the radiator area
- reduce the UFH area (which you are doing by closing loops)
One thing to be careful with if you close loops completely is that it reduces the system volume - ie the volume of water in the active sysem. This will reduce the 'on' period when the heat pump is cycling, which reduces efficiency. Its probably better to turn them all down very low than switch some off completely, but of course that depends on practicality. In extremis if you reduce the system volume too far you can get into a problem with defrost, where there isn't enough hot water in the system to melt the ice that forms on the compressor. This can cause a death spiral. Heat pump manufacturers specify a minimum system volume for this purpose (in reality you want a larger system volume so that cycling is more efficient).
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 27 Forums
- 2,541 Topics
- 59.2 K Posts
- 309 Online
- 6,822 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Indeed we don’t! Much though I wish to be loy...
By Toodles , 52 minutes ago
-
RE: Who's your electricity provider and what's your tariff?
@chandykris Thanks, that’s a fair point and I agree th...
By Eliuccio , 2 hours ago
-
As a full price electricity user (nae smart meter signa...
By Abernyte , 6 hours ago
-
Aerotherm 12+12kw cascade huge power utilisation
Looking for a little bit of advice. new inst...
By Hamish_mckay , 7 hours ago
-
Daikin high temperature heat pump
Hello, I have a DAIKIN ERSQ 016AAV1 16KW. I have a BRC2...
By gajolos , 7 hours ago
-
RE: Setback savings - fact or fiction?
I changed the pump power to the actual value to see if ...
By RobS , 9 hours ago
-
RE: Samsung Gen 7 16kW Integrated unit Modbus monitoring
@majordennisbloodnok Thanks I hope it helps someone. St...
By antonical , 21 hours ago
-
RE: NIBE Heat Pump Warranty: What's an Adequate Engineer Attendance Time?
Totally agree. However the manufacturers know that fe...
By JamesPa , 22 hours ago
-
-
RE: The law of unintended consequences....
Oh Thank you Major, I was just beginning to wonder wher...
By Toodles , 1 day ago
-
RE: Forum updates, announcements & issues
I know that the notifications are being delivered now w...
By Mars , 1 day ago
-
RE: Advice needed after a successful "leftfield" experiment.....
@pauli I have sent a direct message with the financial ...
By ChandyKris , 1 day ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
Does it disappear when the heat pump is off? What abou...
By JamesPa , 1 day ago
-
RE: Fitting heat pump plumbing and pipes in advance?
Great tips, thanks. The PEX/Al/PEX option sounds much m...
By Jonatan , 1 day ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Those control valves on the UFH manifold could be an is...
By Travellingwave , 1 day ago
-
RE: Daikin Altherma 3 LT compressor longevity question
Up to a point yes. However every heat pump (and every ...
By JamesPa , 2 days ago
-
RE: New Build ASHP Defects - Looking for Advice, Support & Shared Experiences
Is that a single pair only? If so it may be part if th...
By JamesPa , 2 days ago
-
@batpred, you’re quite right; it does work well. I don’...
By Majordennisbloodnok , 2 days ago
-
RE: Ecodan Cylinder Possible Weeping Around Thermostat Port
Update: Mitsubishi sent an engineer around. It was li...
By Gruff2001 , 2 days ago
-
RE: A Smarter Smart Controller from Homely?
@benson Agreed. I believe the COP gains with homely, i...
By Papahuhu , 2 days ago
-
How to Find All Your Posts and Topics on the Forum – A Quick Guide
If you’ve ever posted something on the forum and then s...
By Mars , 2 days ago
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
Sorry to hear that but I'm not surprised TBH. Stratifi...
By JamesPa , 2 days ago
-
RE: Say hello and introduce yourself
@pt151 welcome to the forums, and looking forward to he...
By Mars , 3 days ago
-
Samsung Gen 7 16kW Integrated unit Modbus monitoring
Looking for some assistance to get modbus monitoring wo...
By antonical , 3 days ago